Ilyas
TRNSYS's sign convection for azimuth is that facing the equator is 0,
facing away from the equator is +/- 180, facing east is -90 and facing
west is +90. In the northern hemisphere this means that facing the
equator is an azimuth of 0. In your diagram it looks as though your
building faces 10° east of north. This means that your N facade will
have an azimuth of -170. Your south facade will have an azimuth of 10.
Your west facade will have an azimuth of 100 and your east facade will
have an azimuth of -80
David