[TRNSYS-users] Active layer/boundary condition - strange results
hotline
hotline at Transsolar.com
Thu Jan 25 03:02:20 PST 2018
Dear Karol and Katarzyna,
If boundary conditions = IDENTICAL, the surface temperatures of the active wall Tsi and Tso will only be identical, if:
* Wall construction is symmetrical
* Convective heat transfer coefficients (front and back) are the same
Best
Christoph Stetter
__________________________________________________________________________________________________
Christoph Stetter M.Eng.
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
http://www.transsolar.com<http://www.transsolar.com/>
Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Stuttgart - München - New York - Paris
Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle
Eingetragen beim Amtsgericht Stuttgart HRB 23347,
Steuernummer: 99073/00911,USt-IdNr.: DE 152272639
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von Karol Bandurski via TRNSYS-users
Gesendet: Montag, 22. Januar 2018 12:44
An: trnsys-users at cae.wisc.edu
Cc: Karol Bandurski <karol.bandurski at put.poznan.pl>
Betreff: [TRNSYS-users] Active layer/boundary condition - strange results
Dear Users and Developers,
We would like to model active layer as component of TABS.
Now our model is one zone with active layer in ceiling. Adiabatic condition/IDENTICAL for all internal partition and set. We have one external wall.
1. We would like to keep neighborhood zones in the same AIR temperature. But when we set boundary condition to IDENTICAL over TABS, then outer surface of this partition has higher temperature then indoor air temperature and active layer water temperature... -Why?
1. The situation is better if we set convective heat transfer coefficient, on outer surface of TABS to 0.001. If we understand, it is mean direct contact between air and surface. So if there are adiabatic/identical condition: outer SURFACE temperature of TABS has the same temperature as AIR inside modelled zone. But our aim is to keep identical inside and outside AIR temperature, not SURFACE temperature... How we can do it?
Kind regards,
Karol
--------------------------------------------------------------------
Karol BANDURSKI M. Sc.
Faculty of Civil and Environemntal Engeneering
Division of Heating, Air Conditioning and Air Protection
Poznan University of Technology
https://www.researchgate.net/profile/Karol_Bandurski
www.put.poznan.pl/~karol.bandurski<http://www.put.poznan.pl/~karol.bandurski>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180125/5ee411d0/attachment-0003.html>
More information about the TRNSYS-users
mailing list