some further clarification on the internal control of shading:
The shading control is applied only if a window has defined a shading factor >0 with internal control.
If you didn’t specify this in your 3D building project for a window surface, the window surface is unshaded no matter what is values are specified by the internal shading control
Thus, it is recommended to
- not use strange values for the shading control for switching of shading
- but set the shading factor for window surfaces to 0 for unshaded.
Marion
-----------------------------------------------------------------------------------------------------------------------------------------------------------
Dipl.-Ing. Marion Hiller
TRANSSOLAR Energietechnik GmbH
Stuttgart - Munich - New York - Paris
t: +49.711.67976.0<tel:%2B49.711.67976.27> f: +49.711.67976.11<tel:%2B49.711.67976.11>
www.transsolar.com/<http://www.transsolar.com/>
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347 / Steuernummer: 99073/00911 / USt-IdNr.: DE 152272639
Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von David BRADLEY via TRNSYS-users
Gesendet: Donnerstag, 4. Januar 2018 21:09
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: David BRADLEY <d.bradley at tess-inc.com>
Betreff: Re: [TRNSYS-users] How to specify no movable shadings when importing 3D building using the wizard
Yossef,
I usually set those values to close if > 10000 and open if less than 10000. The value in question is the incident solar radiation (in kJ/h.m2). Typically the solar radiation will never exceed 5000 kJ/h.m2 so the value of 10000 removes the shades from consideration.
Your method sounds to me as though it will work as well. I am not sure on the source of 120 and 140 but setting the max shade value to 0 will do the job.
kind regards,
David
On 12/30/2017 07:54, Yossef Ibrahimi via TRNSYS-users wrote:
Dear Trnsys community,
I'm using the wizard to import the 3D building project, but it shows me options for shadings, I want to specify that there is no shadings, so I left "close if total..." set to 140, "open if total..." set to 120, and for maximum I put 0 as a value. Is that the correct way to ignore movable shadings?
Thank you
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180108/69652d7e/attachment.html>
More information about the TRNSYS-users
mailing list