[TRNSYS-users] error type 665 with high heat power of performance data

David BRADLEY d.bradley at tess-inc.com
Tue Oct 17 11:39:33 PDT 2017


Alex,

  Type665 just reads performance data from an external file. There is no 
restriction on the size of the heat pump that can be modeled. If you 
have the data file for the mitsubishi PEADRP125JA entered correctly then 
Type665 will read it. If that model of heat pump has a variable speed 
compressor in it then Type665 is not an appropriate model to use. 
Type665 models an on/off device whose compressor speed is not able to 
modulate and would possibly therefore use more power under low load/duty 
cycle conditions.

kind regards,

  David



On 10/17/2017 04:46, Alex moreno via TRNSYS-users wrote:
> Hi im working with a model with type 665, i want use the performace data
> of comercial heat pump, mitsubishi PEADRP125JA(
> L), if i divide the values of heating power and power of compresor to 2
> the heat pump works well. is posible this type of heat pump not allow
> high values of heat power ?
>
> regards
>
> alex
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com



More information about the TRNSYS-users mailing list