[TRNSYS-users] ask for help
David BRADLEY
d.bradley at tess-inc.com
Tue Nov 14 10:16:37 PST 2017
Weihua Lv,
I am not entirely sure that I understand your question. The input mass
flow rate should be the total mass flow rate that is being supplied to
the floor. The active layer algorithm implemented in Type56 is
restricted so that if you divide the total flow rate by the floor area
you must get a value that is above 15 kg/h.m2.
kind regards,
David
On 11/13/2017 07:08, 吕伟华 via TRNSYS-users wrote:
> Dear sir!
> I am trying to use the MultizoneBuilding model to do some work. Now I
> have some questions about the "Thermo-active Building Elements" model
> in TRNBUILD. I want to know how to input the inlet mass flow rate in
> the massage box? for example, the water flow into the floor at a inlet
> flow rate of 15kg/h then flow out and the floor area is one square
> meter. so how to input the "in let mass flow" into the massage box.
> the number filled in the massage box should 15 or 30? Many thanks.
>
>
> It would be appreciate to receive your kindly response.
> Thank you.
>
> Yours
> Weihua Lv
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171114/3c4bb428/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: D5EE9D47 at BAE05903.5999095A.jpg.jpg
Type: image/jpeg
Size: 65607 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171114/3c4bb428/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: D6EB6DEE at D128125B.5999095A.jpg.jpg
Type: image/jpeg
Size: 98756 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171114/3c4bb428/attachment-0003.jpg>
More information about the TRNSYS-users
mailing list