Ravinda,
There is a pressure reducing valve component in the TESS CHP library.
It is typically used in steam applications and assumes steam as the
working fluid.
Typically we do not model refrigeration systems at the heat exchanger
/ compressor / expansion valve level but take the whole cycle as a
component. The time constant of the transient behavior within the
refrigeration cycle is so small that a typical TRNSYS time step (1-5
minutes in the kind of systems that we work with) that the refrigeration
loop can be seen as steady state. We therefore assign a COP that is
dependent on the external inlet conditions (such as temperature and
humidity of the air on the condenser and evaporator sides).
kind regards,
David
On 12/19/2017 04:19, v ravindra via TRNSYS-users wrote:
> What is the component that models a Throttle valve used in
> Refrigeration cycles in TRNSYS.
>
> V.Ravindra
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171219/53839b32/attachment.html>
More information about the TRNSYS-users
mailing list