<div dir="ltr">Hi Tom-<br><br>Design schedules are a common confusion point for new (and intermediate) TRACE users.<br><br>It is wise to consider that TRACE is essentially two programs packaged as 1. First, it is a load design program. Then, it is an energy-simulation program.<br>
<br>The heating design schedule is only used to size heating equipment. If you run the "Design" portion of the program, it only uses the "Cooling Design, and Heating Design Schedules". Then, when you run the rest of the program "system, energy, economics", it incorporates the weekdays schedules, etc. It would be very difficult for non-advanced users to "spin the meter" with lights or receptacles and ignore the impact on heating the load.<br>
<br>I would recommend looking at a checksums report to more clearly see the impact when changing design schedules. Any of the checksum reports would certainly show lights, misc, and people. I'm guessing you are looking at an energy report? It would help to know the specific reports.<br>
<div><br>As to why the heating energy increased with the change in schedules, that would depend on what you changed in the schedules.. Seeing that the cooling energy increased tells me that you changed more than just the heating design schedule. (when experimenting with schedules, it's best to change 1 thing at a time - i.e. just set change the heating design schedule)<br>
<br>Taking a stab in the dark, are you running a VAV system with Std 62 enabled? The load design troubles you are encountering may actually be a result of something other than internal heat gains.<br><br></div><div>Let's start there and see what else we can find out,<br>
<br>Bob Fassbender<br>Energy-models.com/training/trace-700</div><div hspace="streak-pt-mark" style="max-height:1px"><img style="width:0px; max-height:0px;" src="https://mailfoogae.appspot.com/t?sender=aYm9iZmFzczExQGdtYWlsLmNvbQ%3D%3D&type=zerocontent&guid=fdaa31dd-35ff-404f-b371-3b36a75f6d65"><font color="#ffffff" size="1">ᐧ</font></div>
</div><div class="gmail_extra"><br><br><div class="gmail_quote">On Mon, Jun 23, 2014 at 1:35 PM, Tom Ferrel <span dir="ltr"><<a href="mailto:Tom@mail.ra-solutions.com" target="_blank">Tom@mail.ra-solutions.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal">Heating design in the library schedules I am using (*-Midrise Bldg) ignores internal loads for heating design purposes.  I am performing a LEED energy performance analysis, and I want to be sure I
<u>am</u> including the internal loads in the space heating calculations.  The assurances I got from the Trace help was not overwhelming, and the space heating requirements of the model seem intuitively too high.<u></u><u></u></p>

<p class="MsoNormal">As a check, I created my own custom schedules for people, lighting, and process loads, with a heating design schedule which matched the cooling design schedule.  The results showed increased receptacle and lighting loads (people loads were
 not listed in the report) as if the program were somehow double accounting for the two schedules.  The space cooling energy use increased, as would be expected if the loads were counted twice.  Surprisingly, the space heating energy use also
<u>increased</u>.  This has me concerned.<u></u><u></u></p>
<p class="MsoNormal">Does someone out there have knowledge about how Trace handles internal heat loads when calculating space heating energy use?<span class="HOEnZb"><font color="#888888"><u></u><u></u></font></span></p>
<span class="HOEnZb"><font color="#888888">
<p class="MsoNormal">-Tom<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
</font></span></div>
</div>