<font size=2 face="sans-serif">Hi John,</font>
<br>
<br><font size=2 face="sans-serif">I wasn't able to make any changes to
the model to correct the difference in fan power. However, I noticed a
couple of things.</font>
<br>
<ol>
<li value=1><font size=2 face="sans-serif">The Baseline Case "Pretend"
doesn't include any pressure drop adjustments from Table 6.5.3.1.1B. This
will help increase the baseline fan power. Note that credit for heat recovery
devices may not be taken unless it is required in the Baseline Case system
(see note under Table G3.1.2.9).</font>
<li value=2><font size=2 face="sans-serif">The Proposed Case "Actual"
fan power seems high. See attached pdf for a range of BHPs for a sample
TRANE AHU at 3,000 cfm. They range from 0.88 to 3.08 depending on the system
total static pressure. The system in the model has a nominal HP of 10 which
is being modeled as 7.46 kW.</font>
<li value=3></ol><font size=2 face="sans-serif">Hope that helps,</font>
<br><font size=2 face="sans-serif">Alex Chapin</font>
<br>
<br>
<br>
<br><font size=2 color=#3f803f face="Arial"><b>Alex N. Chapin</b></font>
<br><font size=2 color=#5f5f5f face="Arial"><b>Sustainability Program Engineer</b></font>
<br><font size=2 color=#5f5f5f face="Arial"><b>SRI Green Building Certification,
LLC</b></font>
<br><font size=2 color=#5f5f5f face="Arial">300 Northpointe Circle • Suite
304</font>
<br><font size=2 color=#5f5f5f face="Arial">Seven Fields, PA 16046 • USA</font>
<br>
<br><a href="file:///\\\\SRI-FS1\\WPDOCS\\07%20Marketing%20&%20Sales\\01Marketing-PARTIAL\\01Marketing\\Email%20Footer\\www.SRIRegistrar.com"><font size=2 color=#5f5f5f face="Arial"><u>www.SRIRegistrar.com</u></font></a>
<br><font size=2 color=#5f5f5f face="Arial">achapin@SRIRegistrar.com</font>
<br><font size=2 color=#5f5f5f face="Arial">T: (724) 934-9000 x619</font>
<br><font size=2 color=#5f5f5f face="Arial">F: (724) 935-6825</font>
<br>
<br><font size=2 color=#3f803f face="Arial"><b>Building Sustainability</b></font>
<p><font size=1 color=#5f5f5f face="Arial">This message and any included
attachments are from SRI Quality System Registrar, and are intended only
for the addressee. The information contained herein may include privileged
or confidential information. Unauthorized review, forwarding, printing,
copying, distributing or using such information is strictly prohibited
and may be unlawful. If you have received this message in error, or have
reason to believe that you are not authorized to receive it, please promptly
delete it and notify the sender by e-mail with a copy to mail@sriregistrar.com.
 Thank you.</font>
<p>
<p><tt><font size=2>Date: Thu, 10 Apr 2014 18:01:15 +0000<br>
From: "Eurek, John S NWO" <John.S.Eurek@usace.army.mil><br>
To: "'trace-users@lists.onebuilding.org'"<br>
                
<trace-users@lists.onebuilding.org><br>
Subject: [Trace-users] Fan power (UNCLASSIFIED)<br>
Message-ID:<br>
                
<E777FD5A41D3B04A83296213737A85D7092442FB@EIS-MB0501WPC.eis.ds.usace.army.mil><br>
                
<br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Classification: UNCLASSIFIED<br>
Caveats: NONE<br>
<br>
Anybody,<br>
<br>
I need a little help.  The fan energy usage of the Actual/Purposed
building is 4.5X more than the Pretend building.<br>
<br>
I've looked and looked and looked for something that is causing such a
huge difference.<br>
<br>
One thing I tried that really confused me was to set the system for the
pretend building as 'same as Alternate 1' and the pretend building fan
energy usage went up....  So then I went tab-by-tab and matched Alternative
1 to the setting that the Pretend building was using and the fan energy
for Alternate 1 was still over 2 times the Pretend building.<br>
<br>
<br>
<br>
John<br>
<br>
<br>
Classification: UNCLASSIFIED<br>
Caveats: NONE<br>
</font></tt>