Hi There-<div><br></div><div>It may interest you to consider that Demand in TRACE is determined by the COOLING DESIGN day schedule. Often, this is set to Midnight-Midnight at 100%, a more proper schedule</div><div><br></div>
<div>The reason for using the cooling design schedule is because TRACE works in 1 hour intervals, while Demand charges are based off of 15 or 20 minute intervals (which will be slightly higher than the peak average for 1 hour in most cases).</div>
<div><br></div><div>So, Scott's explanation is the right way to proceed, but in this case, the cooling design day schedule is what influences demand. </div><div><br></div><div>Good Luck,<br></div><div><br></div><div>Bob Fassbender</div>
<div>Energy-models.com</div><div><br><div class="gmail_quote">On Wed, Nov 7, 2012 at 3:09 PM,  <span dir="ltr"><<a href="mailto:trace-users-request@lists.onebuilding.org" target="_blank">trace-users-request@lists.onebuilding.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send Trace-users mailing list submissions to<br>
        <a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:trace-users-request@lists.onebuilding.org">trace-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:trace-users-owner@lists.onebuilding.org">trace-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Trace-users digest..."<br>
<br>
<br>
Today's Topics:<br>
<br>
   1. Lowering Demand for Energy Modeling (Ben)<br>
   2. Re: Lowering Demand for Energy Modeling (Scott Parker)<br>
<br>
<br>
----------------------------------------------------------------------<br>
<br>
Message: 1<br>
Date: Wed, 7 Nov 2012 11:30:51 -0600<br>
From: "Ben" <<a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a>><br>
To: <<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a>><br>
Subject: [Trace-users] Lowering Demand for Energy Modeling<br>
Message-ID: <002701cdbd0d$a34c3f00$e9e4bd00$@<a href="http://antella-inc.com" target="_blank">antella-inc.com</a>><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Would anyone have any thoughts/experience with lowering demand to line up<br>
with an energy model?<br>
<br>
Our consumption lines up nearly perfect, while demand is significantly<br>
larger in the summer months.<br>
<br>
Any ideas welcome!<br>
<br>
cid:image003.png@01CDAB78.6524ACE0<br>
Ben Hollon EIT, LEEDR AP BD+C, MBA<br>
Mechanical Engineer<br>
 <mailto:<a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a>> <a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a><br>
O. <a href="tel:816.421.0950%20Ext%20-%20104" value="+18164210950">816.421.0950 Ext - 104</a><br>
F. <a href="tel:816.249.2439" value="+18162492439">816.249.2439</a><br>
M. <a href="tel:816.536.3434" value="+18165363434">816.536.3434</a><br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/26fceae5/attachment.html" target="_blank">http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/26fceae5/attachment.html</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: not available<br>
Type: image/png<br>
Size: 17316 bytes<br>
Desc: not available<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/26fceae5/attachment-0001.png" target="_blank">http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/26fceae5/attachment-0001.png</a>><br>

<br>
------------------------------<br>
<br>
Message: 2<br>
Date: Wed, 7 Nov 2012 18:53:42 +0000<br>
From: Scott Parker <<a href="mailto:sparker@aeieng.com">sparker@aeieng.com</a>><br>
To: Ben <<a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a>>, "<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a>"<br>
        <<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a>><br>
Subject: Re: [Trace-users] Lowering Demand for Energy Modeling<br>
Message-ID:<br>
        <CDD24FBBB7660944A466B133EB5519C516FF8A85@AEI-EX2.aeieng.lan><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Ben,<br>
<br>
You mentioned that the demand is larger ... I am guessing that you mean larger in your model, but I am not sure (visa-versa if higher in actual measured building).  Since you mentioned that it is higher in summer I would check to see if the summer occupancy is like you expect or if (like a typical university building) the occupancy is lower in summer.<br>

<br>
It sounds like your daily load profile is much flatter than you have modeled.  For example, you could model 12 hours at 100% lights, people, plug load, etc. or model 12 hours at 75% and 12 hours at 25%.  Either way you can get the same consumption, but the demand will not be correct.  I have just given a simple example, and it is not quiet this simple since the load cannot be spread out exactly as I have noted and keep the exact same consumption.  However, this general idea will get you in the right direction ... flatter daily load profiles as defined by people, light and plug load schedules will help you keep the same consumption and reduce the demand.<br>

<br>
Scott<br>
<br>
From: <a href="mailto:trace-users-bounces@lists.onebuilding.org">trace-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:trace-users-bounces@lists.onebuilding.org">trace-users-bounces@lists.onebuilding.org</a>] On Behalf Of Ben<br>

Sent: Wednesday, November 07, 2012 12:31 PM<br>
To: <a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a><br>
Subject: [Trace-users] Lowering Demand for Energy Modeling<br>
<br>
Would anyone have any thoughts/experience with lowering demand to line up with an energy model?<br>
<br>
Our consumption lines up nearly perfect, while demand is significantly larger in the summer months.<br>
<br>
Any ideas welcome!<br>
<br>
[cid:image003.png@01CDAB78.6524ACE0]<br>
Ben Hollon EIT, LEED(r) AP BD+C, MBA<br>
Mechanical Engineer<br>
<a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a><mailto:<a href="mailto:bhollon@antella-inc.com">bhollon@antella-inc.com</a>><br>
O. <a href="tel:816.421.0950%20Ext%20-%20104" value="+18164210950">816.421.0950 Ext - 104</a><br>
F. <a href="tel:816.249.2439" value="+18162492439">816.249.2439</a><br>
M. <a href="tel:816.536.3434" value="+18165363434">816.536.3434</a><br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/5b1c75be/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/5b1c75be/attachment-0001.htm</a>><br>

-------------- next part --------------<br>
A non-text attachment was scrubbed...<br>
Name: image001.png<br>
Type: image/png<br>
Size: 17316 bytes<br>
Desc: image001.png<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/5b1c75be/attachment-0001.png" target="_blank">http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121107/5b1c75be/attachment-0001.png</a>><br>

<br>
------------------------------<br>
<br>
_______________________________________________<br>
Trace-users mailing list<br>
<a href="mailto:Trace-users@lists.onebuilding.org">Trace-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
<br>
<br>
End of Trace-users Digest, Vol 49, Issue 1<br>
******************************************<br>
</blockquote></div><br></div>