Matt -<br><br>Is the refrigeration equipment modeled? Or is it just assumed as a process load?<div><br></div><div>If it is just an assumed process load, then you will need to know the amount of recoverable heat (and a schedule). Let's say it is 10 MBH:</div>
<div><br></div><div>Then, you would have to create a heating plant for the makeup air. That heating plant would contain at least two pieces of equipment, the first being the "recovered heat". Set the capacity to 10 Mbh (in this case), and then you set the rate to something like .001 KW. Finally, set your schedule for that equipment if it is not running 24/7. </div>
<div><br></div><div>Then you would have "free" heat up to 10 mbh for that makeup air plant, the remainder of which would come from the next piece of equipment.</div><div><br></div><div>Anyway, we might be able to come up with something better, but we'd need to know more about the particular setup.</div>
<div><br></div><div>Bob Fassbender</div><div>Energy-models.com</div><div><br></div><div><br><br><div class="gmail_quote">On Wed, Mar 21, 2012 at 3:37 PM, <span dir="ltr"><<a href="mailto:trace-users-request@lists.onebuilding.org">trace-users-request@lists.onebuilding.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send Trace-users mailing list submissions to<br>
<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
or, via email, send a message with subject or body 'help' to<br>
<a href="mailto:trace-users-request@lists.onebuilding.org">trace-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
<a href="mailto:trace-users-owner@lists.onebuilding.org">trace-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Trace-users digest..."<br>
<br>
<br>
Today's Topics:<br>
<br>
1. Trace Process Refrigeration (Matt Cale)<br>
<br>
<br>
----------------------------------------------------------------------<br>
<br>
Message: 1<br>
Date: Wed, 21 Mar 2012 12:08:12 -0400<br>
From: Matt Cale <<a href="mailto:Matt.Cale@cadmusgroup.com">Matt.Cale@cadmusgroup.com</a>><br>
To: "<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a>"<br>
<<a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a>><br>
Subject: [Trace-users] Trace Process Refrigeration<br>
Message-ID:<br>
<<a href="mailto:197E0C924E33A54BB41B2921100AFF2516E8F393A2@mail.cadmusgroup.org">197E0C924E33A54BB41B2921100AFF2516E8F393A2@mail.cadmusgroup.org</a>><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
Hello all,<br>
<br>
I am working on a model in which the designer has included heat recovery from process refrigeration equipment which is used to preheat makeup air. Any suggestions on how to get this process to react properly?<br>
<br>
Thanks in advance,<br>
<br>
Matt Cale, PE, LEED AP<br>
Associate<br>
The Cadmus Group<<a href="http://www.cadmusgroup.com/" target="_blank">http://www.cadmusgroup.com/</a>><br>
M: <a href="tel:321-663-2336" value="+13216632336">321-663-2336</a><br>
<a href="mailto:matt.cale@cadmusgroup.com">matt.cale@cadmusgroup.com</a><br>
<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a href="http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20120321/cce5e997/attachment.html" target="_blank">http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20120321/cce5e997/attachment.html</a>><br>
<br>
------------------------------<br>
<br>
_______________________________________________<br>
Trace-users mailing list<br>
<a href="mailto:Trace-users@lists.onebuilding.org">Trace-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
<br>
<br>
End of Trace-users Digest, Vol 41, Issue 3<br>
******************************************<br>
</blockquote></div><br></div>