John/Other Bob-<div><br></div><div>Yes, I see where the confusion comes in. Sorry about that. I was answering Robert's question, which I interpreted as, "should I model as 1 system - with no DOA?" or "1 system with 1 cooling coil only". </div>
<div><br></div><div><b>To clarify, it should be modeled as 1 system + 1 dedicated OA system/unit</b> (which many people refer to as two systems, but TRACE does not! Thus, the confusion). Anyway, I hope that clarifies what I meant. The method that John suggested (of two actual systems in TRACE, is a possibility I suppose - this is what many eQUEST users do).</div>
<div><br></div><div>However, you really should take advantage of TRACE's ability to model DOA, which is a feature that other programs don't have.</div><div><br></div><div>Regarding John's question</div><div><br>
</div><div>Yes, TRACE will know where to recover energy. If you have a fan coil system, and specified DOA, plus energy recovery:</div><div><br></div><div>Model the DOA, as mentioned earlier</div><div>Then, add the energy recovery.</div>
<div>It is critical that you specify the deck locations (that way TRACE will know that it affects the DOA unit, and not the FCU).</div><div>Specify the decks, as ventilation deck and exhaust side deck and VOILA!</div><div>
<br></div><div>TRACE understands that the ventilation deck goes to the DOA, and is also pre-conditioned by the exhaust air.</div><div><br></div><div>Please let me know if there is other confusion. </div><div><br></div><div>
Bob Fassbender</div><div><br></div><div><br></div><div><br></div><div><br><div class="gmail_quote">On Fri, Feb 4, 2011 at 10:24 AM, Eurek, John S NWO <span dir="ltr"><<a href="mailto:John.S.Eurek@usace.army.mil">John.S.Eurek@usace.army.mil</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">Classification: UNCLASSIFIED<br>
Caveats: NONE<br>
<br>
Bob(s)<br>
<br>
Mr. Fassbender, Your answer confuses me.<br>
<br>
You say it is not acceptable to model as 1 system, but the image you<br>
attached shows that you are using the "dedicated OA" tab.<br>
<br>
The second concern I have is that my outside air unit has energy recovery,<br>
but the fan coils do not.  Like Mr. Arnott's system, the heating and cooling<br>
unit is return only with no outside air.  So if I make a fan coil system,<br>
then input the information under the 'dedicated OA' tab, if I input my<br>
energy recovery under with 'options' tab will Trace know to credit the<br>
energy recovery to the DOA unit, because the fan coil has no energy recovey.<br>
<br>
Mr. Fassbender, can you explain what you meant by not modeling with 1<br>
system?<br>
<br>
Also, I need to look deeper into the exhaust situation, thanks for the tip<br>
before I even needed it.<br>
<br>
<br>
John Eurek PE, LEED AP<br>
Mechanical Engineer,<br>
US Army Corps of Engineers<br>
Omaha District CENWO-ED-DA<br>
1616 Capitol Avenue<br>
Omaha, NE 68102<br>
Phone: (402) 995-2134<br>
email: <a href="mailto:john.s.eurek@usace.army.mil">john.s.eurek@usace.army.mil</a><br>
<div class="im"><br><br></div>
<br>
</blockquote></div><br></div>