<DIV><SPAN class=458390719-11052010><FONT face=Arial size=2>I am a little 
confused on how to apply fan power to the baseline building using Appendix 
G. Per G3.1.2.8 ".... If return or relief fans are specified in the 
proposed design, the baseline building design shall also be modeled with fans 
serving the same functions and sized for the baseline system supply fan air 
quantity less the minimum outdoor air, or 90% of the supply fan air quantity, 
whichever is larger." </FONT></SPAN></DIV>
<DIV><SPAN class=458390719-11052010><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=458390719-11052010><FONT face=Arial size=2>Following are 
comments from two USGBC reviewers on different projects:</FONT></SPAN></DIV>
<UL>
  <LI><SPAN class=458390719-11052010><FONT face=Arial size=2><FONT 
  face="Times New Roman" size=3>Please note that the Baseline fan power 
  calculated in Section G3.1.2.9 refers to the sum of the supply, return, 
  exhaust, and relief fans for each HVAC system.</FONT></FONT></SPAN></LI>
  <LI><SPAN class=458390719-11052010><FONT face=Arial size=2><FONT 
  face="Times New Roman" size=3>Finally, the fan power for the Baseline Case 
  must be calculated according to Table G3.1.2.9 where CFM refers to the supply 
  CFM (not supply + exhaust + dedicated outside air), and where the fan power 
  refers to the sum of all supply, return, exhaust, and relief fans for each 
  zone.</FONT></FONT></SPAN></LI></UL>
<DIV><SPAN class=458390719-11052010><FONT face=Arial size=2>Should the airflows 
be summed, calculate the fan power and then prorate the power to each fan based 
on cfm?</FONT></SPAN></DIV>
<DIV><SPAN class=458390719-11052010><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=458390719-11052010><FONT face=Arial 
size=2>Thanks</FONT></SPAN></DIV>
<DIV><SPAN class=458390719-11052010><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV align=left>
<DIV align=left><STRONG><FONT face=Arial size=2>Robert 
Vogt</FONT></STRONG></DIV>
<DIV align=left><FONT face=Arial size=1>Mechanical Group, LEED Accredited 
Professional</FONT></DIV>
<DIV align=left><STRONG><FONT face=ar color=#ff0000>Luckett & 
Farley</FONT></STRONG></DIV>
<DIV align=left><FONT size=2><FONT face=Arial>      
<STRONG>[smart design]</STRONG></FONT></FONT></DIV>
<DIV align=left><FONT face=Arial size=1><EM>Best Places to Work in Kentucky 2009 
& 2010</EM></FONT></DIV>
<DIV align=left><FONT face=Arial size=1>737 South Third Street</FONT></DIV>
<DIV align=left><FONT face=Arial size=1>Louisville, Kentucky 40202</FONT></DIV>
<DIV align=left><FONT face=Arial size=1>502-585-4181 x105</FONT></DIV>
<DIV align=left><FONT face=Arial size=1>502-587-0488 Fax</FONT></DIV>
<DIV align=left><FONT face=Arial size=1><A title=mailto:Bvogt@luckett-farley.com 
href="mailto:Bvogt@luckett-farley.com">Bvogt@luckett-farley.com</A></FONT></DIV>
<DIV align=left><FONT face=Arial size=1><A title=http://www.luckett-farley.com/ 
href="http://www.luckett-farley.com/">www.luckett-farley.com</A></FONT></DIV>
<DIV align=left><FONT face=Arial size=1>Founded 1853</FONT></DIV>
<DIV align=left><FONT face=Arial size=2></FONT> </DIV>
<DIV align=left>
<DIV align=left><FONT face=Arial size=2><SPAN style="COLOR: red"><?xml:namespace 
prefix = o ns = "urn:schemas-microsoft-com:office:office" /><O:P><FONT 
size=1><FONT face=Arial color=#000000><SPAN><SPAN style="FONT-SIZE: 9pt">
<DIV align=left><FONT face=Arial size=2><SPAN style="COLOR: red"><o:p><FONT 
size=1><FONT face=Arial color=#000000><SPAN><SPAN style="FONT-SIZE: 9pt"><SPAN 
style="FONT-SIZE: 16pt; COLOR: #1c7c00; FONT-FAMILY: Webdings">P</SPAN><SPAN 
style="FONT-SIZE: 8pt; COLOR: #1c7c00; FONT-FAMILY: Webdings"> </SPAN><I><SPAN 
style="FONT-SIZE: 8pt; COLOR: #1c7c00">Please consider the environment before 
printing this e-mail.</SPAN></I><SPAN 
style="FONT-SIZE: 8pt; COLOR: #006666"> </SPAN></SPAN></SPAN></FONT></FONT></o:p></SPAN></FONT></DIV>
<DIV align=left><FONT size=2><SPAN style="COLOR: red"><o:p><FONT 
size=1><SPAN><SPAN style="FONT-SIZE: 9pt"><SPAN 
style="FONT-SIZE: 8pt; COLOR: #006666"><SPAN style="FONT-SIZE: 8pt"><FONT 
color=#000000>This electronic message is intended for transmission to authorized 
persons only. It may contain information that is confidential, privileged, 
proprietary or subject to other confidentiality protections.  It is not 
intended for transmission to, or receipt by, any unauthorized persons. If you 
are not authorized to receive this message, you may not review, copy, forward or 
otherwise distribute this message. If you have received this message in error, 
please notify the sender by reply e-mail and delete it from your system. Thank 
you</FONT></SPAN></SPAN></SPAN></SPAN></FONT></o:p></SPAN></FONT></DIV></SPAN></SPAN></FONT></FONT></SPAN></FONT></DIV></DIV></DIV></O:P>
<DIV> </DIV></BODY></HTML>