[Trace-users] Transfer air & room exhaust calculations & system calculations

Eisenbarth, Brad via Trace-users trace-users at lists.onebuilding.org
Wed Jan 18 11:57:01 PST 2017


I am trying to use Trane Trace 700 to calculate my room airflows and system airflows & load requirements for the room air balance diagram show in the snip it below, also attached.

I have set up a Trace model with the 3 spaces shown (CIRCULATION 196, ANTE ROOM 115, & CONTAINMENT SUITE 116).  I have input information for exterior walls, windows, doors, lighting loads, & miscellaneous loads.  I want Trace to do the usual load calculation for these spaces but also include the transfer air requirements.  I'm having trouble getting the transfer air to be included in the room and system level airflow calculations.  See snip it below & attached for my inputs in the Create Rooms - Airflow Tab for each of the 3 spaces mentioned.

The resulting System & Room Checksums are attached.  The transfer air is not being calculated correctly.  CONTAINMENT SUITE is negative but not by 100 CFM as it should be.  CIRCULATION supply air and return air are equal which is also incorrect, 100 CFM of the supply air (which is greater than the 89 CFM calculated, I'll have to artificial bump this up to at least 100 CFM) should be couted as transfer air to CONTAINMENT SUITE, therefore there shouldn't be any return air for this space.

Questions:


1.       Has anyone been successful specifying a transfer air value vs letting Trane Trace 700 calculate it? If so, how?

2.       Does anyone know why my transfer air from CIRCULATION isn't being calculated in the return air value?  Again, is there a way to set the transfer air from a space?  If so, how?

3.       Does anyone have recommendations how to potentially fix this (under create rooms - airflow tab, system level, or potentially other ways)?

[cid:image003.jpg at 01D27192.B83F5D50]


[cid:image005.png at 01D2718F.E8E501B0]

[cid:image006.png at 01D2718F.E8E501B0]

[cid:image007.png at 01D2718F.E8E501B0]

Thanks,

Brad Eisenbarth, CDT
[cid:image001.png at 01D089A3.3AF406D0]
T 314.425.8799

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6945 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 38762 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 39706 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 39002 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 43772 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Clean Room Pressurization Diagram.bmp.jpg
Type: image/jpeg
Size: 88660 bytes
Desc: Clean Room Pressurization Diagram.bmp.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 196 CIRCULATION - AIRFLOW INPUTS.jpg
Type: image/jpeg
Size: 115726 bytes
Desc: 196 CIRCULATION - AIRFLOW INPUTS.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 116 CONTAINMENT SUITE - AIRFLOW INPUTS.jpg
Type: image/jpeg
Size: 118096 bytes
Desc: 116 CONTAINMENT SUITE - AIRFLOW INPUTS.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 115 ANTE ROOM - AIRFLOW INPUTS.jpg
Type: image/jpeg
Size: 115261 bytes
Desc: 115 ANTE ROOM - AIRFLOW INPUTS.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: System & Room Checksums.pdf
Type: application/pdf
Size: 166538 bytes
Desc: System & Room Checksums.pdf
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20170118/85b41eec/attachment-0001.pdf>


More information about the Trace-users mailing list