[Trace-users] Metal framing in concrete block wall (how to model correctly for LEED)
Caballero, Catalina
ccaballero at jalrw.com
Tue Oct 21 08:31:33 PDT 2014
Good morning experts,
I have a question, we have received a comment from a LEED reviewer requesting for the following information:
Table 1.4 of the template appears to indicate that all the assembly U-value for the exterior walls in the Proposed model may not account for the thermal breaks due to the steel-framing portion of the construction assembly. Each construction assembly U-value is not a direct inverse of the insulation R-value for that construction assembly. The R-value of the insulation located between the steel framing must be de-rated when determining the assembly U-value for the exterior wall assembly to account for the reduced thermal resistance of the metal framing components. Revise the Proposed model, as needed, so that all components of the exterior wall construction assembly are accounted for when calculating the assembly U-value for assembly type in the actual design. In addition, update Table 1.4 reflecting the changes. Refer to Table A3.3 in ASHRAE Standard 90.1-2004 for additional guidance regarding how to de-rate the R-value for insulation located between steel framing assemblies.
We have the following wall composition in the project:
[cid:image008.jpg at 01CFED22.90970100]
And we are using the following assembly value: U-0.125 (= R8 Assembly) based on table A3.1A .
[cid:image010.jpg at 01CFED22.90970100]
[cid:image011.jpg at 01CFED22.90970100]
However since this table in my understanding is only accounting for the concrete block, the insulation and the metal framing, I have added the 5/8” gypsum board (layer 1) and the 5/8” hardie board (layer 7) to the modeled assembly as below.
[cid:image015.jpg at 01CFED22.90970100]
Do you think the reviewer would object in any of this process? Or do you consider it should be done differently?
Thank you for your answers, greatly appreciated.
Catalina Caballero. AIA. Assoc., LEED GA.
Sustainability Coordinator
Johnson, Avedano, Lopez, Rodriguez & Walewski Engineering Group, Inc.
Engineering for High Performance Buildings.
MEPF - BIM - LEED - Cx
2510 NW 97 Ave, Ste 220, Miami, FL 33172.
P: 305.594.0660 Ext: 217 Ӏ F: 305.594.0907
www.jalrw.com<http://www.jalrw.com> | ccaballero at jalrw.com<ccaballero at jalrw.com%20>
[cid:image001.png at 01CFED1F.9B489CB0]<http://www.facebook.com/jalrw> [cid:image002.png at 01CFED1F.9B489CB0] <http://www.linkedin.com/company/johnson-avedano-lopez-rodriguez-&-walewski-engineering-group-inc./> [cid:image003.png at 01CFED1F.9B489CB0] <https://www.twitter.com/JALRW/> [cid:image004.png at 01CFED1F.9B489CB0] <https://plus.google.com/u/0/b/112470263254966771834/112470263254966771834/posts>
This email and any files transmitted with it are confidential and intended solely for the addressee.
If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 682 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 736 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 804 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1187 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 26191 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 26929 bytes
Desc: image010.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 13470 bytes
Desc: image011.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.jpg
Type: image/jpeg
Size: 45979 bytes
Desc: image015.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20141021/d4fed30a/attachment-0007.jpg>
More information about the Trace-users
mailing list