[Trace-users] nominal ventilation for heating and cooling

Oscar Buchely L. obuchely at ses-ingenieria.com
Wed May 21 15:00:41 PDT 2014


Thanks Hilary. As you said heating design is Zero. Thanks for the help.

Take care

On 21/05/2014 04:13 p.m., Hilary Giffen wrote:
>
> Check your "People-Hospital Patient Rm" schedule.  You may have Zero 
> percent at "heating design," which would be typical.
>
> *From:*Oscar Buchely L. [mailto:obuchely at ses-ingenieria.com]
> *Sent:* Wednesday, May 21, 2014 4:07 PM
> *To:* trace-users at lists.onebuilding.org; Hilary Giffen
> *Subject:* Re: [Trace-users] nominal ventilation for heating and cooling
>
> I did like this:
>
>   
>
> On 21/05/2014 03:55 p.m., Hilary Giffen wrote:
>
>     How do you have your ventilation entered?  Cfm/person?  Cfm/sf? Cfm? %heating? %cooling?
>
>       
>
>     -----Original Message-----
>
>     From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Oscar Buchely L.
>
>     Sent: Wednesday, May 21, 2014 3:46 PM
>
>     To:trace-users at lists.onebuilding.org  <mailto:trace-users at lists.onebuilding.org>
>
>     Subject: Re: [Trace-users] nominal ventilation for heating and cooling
>
>       
>
>     Thanks Hilary and Hayssam.
>
>       
>
>     The system is constant volumen. In airflow I have NO in apply ASHRAE
>
>     62.1 so Clg Ez and Htg Ez are not activated. I have tried ASHRAE Std 62.1... vent resets and  Sum Room OA Reqs under System ventilation flag but still the Nom vent are not the same.
>
>       
>
>     On 21/05/2014 12:52 p.m., Hilary Giffen wrote:
>
>         Is the system VAV?  If the minimum heating cfm is below the ventilation cfm, it will only deliver the minimum cfm.
>
>           
>
>         -----Original Message-----
>
>         From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Oscar Buchely L.
>
>         Sent: Wednesday, May 21, 2014 12:45 PM
>
>         To:trace-users at lists.onebuilding.org  <mailto:trace-users at lists.onebuilding.org>
>
>         Subject: [Trace-users] nominal ventilation for heating and cooling
>
>           
>
>         Hello.
>
>           
>
>         We are modelling residential building for LEED purposes. In room check sum reports AIRFLOW section, Nom Vent cfm are different for cooling and heating. We already checked that cfm and schedule are the same for heating and cooling in CREATE ROOM airflow  tab, ventilation section.
>
>           
>
>         Does anyone know why even though we have the same cfm and schedule?
>
>           
>
>         Thanks.
>
>           
>
>         _______________________________________________
>
>         Trace-users mailing list
>
>         http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>         To unsubscribe from this mailing list send  a blank message to
>
>         TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG  <mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>       
>
>     _______________________________________________
>
>     Trace-users mailing list
>
>     http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>     To unsubscribe from this mailing list send  a blank message toTRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG  <mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140521/d3ae756a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 19465 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140521/d3ae756a/attachment.png>


More information about the Trace-users mailing list