[Trace-users] nominal ventilation for heating and cooling

Oscar Buchely L. obuchely at ses-ingenieria.com
Wed May 21 13:46:10 PDT 2014


Thanks Hilary and Hayssam.

The system is constant volumen. In airflow I have NO in apply ASHRAE 
62.1 so Clg Ez and Htg Ez are not activated. I have tried ASHRAE Std 
62.1... vent resets and  Sum Room OA Reqs under System ventilation flag 
but still the Nom vent are not the same.

On 21/05/2014 12:52 p.m., Hilary Giffen wrote:
> Is the system VAV?  If the minimum heating cfm is below the ventilation cfm, it will only deliver the minimum cfm.
>
> -----Original Message-----
> From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Oscar Buchely L.
> Sent: Wednesday, May 21, 2014 12:45 PM
> To: trace-users at lists.onebuilding.org
> Subject: [Trace-users] nominal ventilation for heating and cooling
>
> Hello.
>
> We are modelling residential building for LEED purposes. In room check sum reports AIRFLOW section, Nom Vent cfm are different for cooling and heating. We already checked that cfm and schedule are the same for heating and cooling in CREATE ROOM airflow  tab, ventilation section.
>
> Does anyone know why even though we have the same cfm and schedule?
>
> Thanks.
>