I have used the same strategy. But raising the supply air volumes to the critical room above that required by your load simulation has the effect of raising the minimum air flow. That is what actually brings the percentage of OSA down. Raising the minimum stop on the VAV terminal unit that serves that room is probably the more correct way of handling this. Raising the minimum stop leads to re-heat to maintain room temperature which results in higher energy usage so watch your energy usage in your modeling runs and balance the re-heat need against higher OSA values. What will also help is to look at ASHRAE interpretation IC 62.1-2007-17. ASHRAE 62.1 does not require OSA in rooms that are not normally occupied.
Terry L. Wohlgenant, CIPE, BEMP, LEED AP BD+C
Mechanical Design | Senior Associate
twohlgenant at dlrgroup.com
DLR Group
Architecture Engineering Planning Interiors
o: 602-381-8580
6225 North 24th Street, Suite 250 Phoenix, AZ 85016-2042
dlrgroup.com | listen.DESIGN.deliver
dlrgroup.com is newly renovated and expanded. Click. Explore. http://www.dlrgroup.com
-----Original Message-----
From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of trace-users-request at lists.onebuilding.org
Sent: Wednesday, June 04, 2014 1:06 PM
To: trace-users at lists.onebuilding.org
Subject: Trace-users Digest, Vol 66, Issue 1
Send Trace-users mailing list submissions to
trace-users at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
trace-users-request at lists.onebuilding.org
You can reach the person managing the list at
trace-users-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific than "Re: Contents of Trace-users digest..."
Today's Topics:
1. Percent Outside Air (UNCLASSIFIED) (Eurek, John S NWO)
2. Re: Percent Outside Air (UNCLASSIFIED) (Scott Parker)
3. Re: Percent Outside Air (UNCLASSIFIED) (Michael Hardy)
4. REMINDER - onebuilding.org mailing lists (Jason Glazer)
----------------------------------------------------------------------
Message: 1
Date: Tue, 3 Jun 2014 20:16:01 +0000
From: "Eurek, John S NWO" <John.S.Eurek at usace.army.mil>
To: "trace-users at lists.onebuilding.org"
<trace-users at lists.onebuilding.org>
Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
Message-ID:
<E777FD5A41D3B04A83296213737A85D7092E376C at EIS-MB0501WPC.eis.ds.usace.army.mil>
Content-Type: text/plain; charset="us-ascii"
Classification: UNCLASSIFIED
Caveats: NONE
I have an Variable Volume Reheat (30% Min Flow Default) and used the System Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the system was running 100% Outside air. I looked at the 62.1 report and saw that there were corridors and storage rooms driving the 100%, so I set the air flow for those rooms higher. I repeated this process of finding the critical zones and increasing the supply cfm to drive down the outside air percentage.
I've got it down to 43.4%, but is there a better way to accomplish this?
When I run it with summing outside air requirements, the highest zone is 32% outside air, but the values don't comply with 62.1.
Is the best method just to find the critical zones and increasing the cfms and repeat?
Classification: UNCLASSIFIED
Caveats: NONE
------------------------------
Message: 2
Date: Tue, 3 Jun 2014 20:23:12 +0000
From: Scott Parker <sparker at aeieng.com>
To: "Eurek, John S NWO" <John.S.Eurek at usace.army.mil>,
"trace-users at lists.onebuilding.org"
<trace-users at lists.onebuilding.org>
Subject: Re: [Trace-users] Percent Outside Air (UNCLASSIFIED)
Message-ID: <6f376b91c33841e1a386a48256d00382 at MSN-EX2.aeieng.lan>
Content-Type: text/plain; charset="us-ascii"
I prefer manual calculations, but if you want to use Trace to do the ventilation calculations then you can set a "Max Vent (Z) Ratio Allowed". You can try a little trial and error but likely between 30 and 60%.
[cid:image001.png at 01CF7F48.1C2BF750]
SCOTT PARKER
-----Original Message-----
From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
Sent: Tuesday, June 03, 2014 4:16 PM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
Classification: UNCLASSIFIED
Caveats: NONE
I have an Variable Volume Reheat (30% Min Flow Default) and used the System Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the system was running 100% Outside air. I looked at the 62.1 report and saw that there were corridors and storage rooms driving the 100%, so I set the air flow for those rooms higher. I repeated this process of finding the critical zones and increasing the supply cfm to drive down the outside air percentage.
I've got it down to 43.4%, but is there a better way to accomplish this?
When I run it with summing outside air requirements, the highest zone is 32% outside air, but the values don't comply with 62.1.
Is the best method just to find the critical zones and increasing the cfms and repeat?
Classification: UNCLASSIFIED
Caveats: NONE
_______________________________________________
Trace-users mailing list
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 38150 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment-0001.png>
------------------------------
Message: 3
Date: Tue, 3 Jun 2014 13:24:48 -0700
From: "Michael Hardy" <mhardy at blackoakengineering.com>
To: "'Eurek, John S NWO'" <John.S.Eurek at usace.army.mil>,
<trace-users at lists.onebuilding.org>
Subject: Re: [Trace-users] Percent Outside Air (UNCLASSIFIED)
Message-ID: <008001cf7f69$de9b3140$9bd193c0$@blackoakengineering.com>
Content-Type: text/plain; charset="us-ascii"
I usually delete the ventilation rates for those non-critical "critical"
areas so they don't drive the minimum OSA settings. Janitor's closets are the worst, but then I use transfer air and exhaust for those which isn't modeled very well anyway.
Michael L. Hardy, PE, F.NSPE
Black Oak Engineering, Inc.
Cell 503.314.5244
-----Original Message-----
From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On
Behalf Of Eurek, John S NWO
Sent: Tuesday, June 03, 2014 1:16 PM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)
Classification: UNCLASSIFIED
Caveats: NONE
I have an Variable Volume Reheat (30% Min Flow Default) and used the System
Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the
system was running 100% Outside air. I looked at the 62.1 report and saw
that there were corridors and storage rooms driving the 100%, so I set the
air flow for those rooms higher. I repeated this process of finding the
critical zones and increasing the supply cfm to drive down the outside air
percentage.
I've got it down to 43.4%, but is there a better way to accomplish this?
When I run it with summing outside air requirements, the highest zone is 32%
outside air, but the values don't comply with 62.1.
Is the best method just to find the critical zones and increasing the cfms
and repeat?
Classification: UNCLASSIFIED
Caveats: NONE
_______________________________________________
Trace-users mailing list
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------
Message: 4
Date: Wed, 04 Jun 2014 15:03:00 -0500
From: Jason Glazer <jglazer at gard.com>
To: bldg-sim at onebuilding.org, equest-users at onebuilding.org,
hap-users at onebuilding.org, trace-users at onebuilding.org,
virtual-sim at onebuilding.org
Subject: [Trace-users] REMINDER - onebuilding.org mailing lists
Message-ID: <538F7B74.4060106 at gard.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed
Posting Guidelines
------------------
Please read the guidelines, especially if you want to post
information about a product or an available job or if you
want to post the same message to multiple lists.
http://onebuilding.org/guidelines.html
Share Your Answers
------------------
If you are answering a question posted by someone else,
please consider posting it to the list instead of privately
answering. It is likely that others would be interested in
the same question plus it makes both the question and the
answer available in the archives.
Cross Posting
-------------
If your question is specifically about eQUEST, HAP, or
TRACE, IES-VE, please post your question to the
eQUEST-users, HAP-users, TRACE-users or Virtual-Sim mailing
lists first. If you haven't gotten an answer within a day or
so, feel free to post the question to the BLDG-SIM mailing
list.
Other Mailing Lists
-------------------
To subscribe to the BLDG-SIM, eQUEST-users, HAP-users,
TRACE-users or Virtual-Sim mailing lists, send a blank email to:
bldg-sim-subscribe at onebuilding.org
equest-users-subscribe at onebuilding.org
hap-users-subscribe at onebuilding.org
trace-users-subscribe at onebuilding.org
virtual-sim-subscribe at onebuilding.org
In addition we have a mailing list for building performance
rating systems:
bldg-rate-subscribe at onebuilding.org
You can also subscribe to these lists from the
onebuilding.org web site. In addition,links to mailing
lists for some ASHRAE committees and USA chapter of IBPSA
are available at the site.
Unsubscribing
-------------
To unsubscribe, send a blank email to the appropriate email
address shown below:
bldg-sim-unsubscribe at onebuilding.org
bldg-rate-unsubscribe at onebuilding.org
equest-users-unsubscribe at onebuilding.org
hap-users-unsubscribe at onebuilding.org
trace-users-unsubscribe at onebuilding.org
virtual-sim-unsubscribe at onebuilding.org
901ecb-unsubscribe at onebuilding.org
901env-unsubscribe at onebuilding.org
901fc-unsubscribe at onebuilding.org
901ltg-unsubscribe at onebuilding.org
901mech-unsubscribe at onebuilding.org
spc140-l-unsubscribe at onebuilding.org
tc47-l-unsubscribe at onebuilding.org
tc28-l-unsubscribe at onebuilding.org
ibpsausa-unsubscribe at onebuilding.org
You can also unsubscribe on the onebuilding.org web site.
Help, I Can't Post
------------------
90% of the time if you cannot post it is because you are
sending from a different email address than the one you
originally subscribed from. Please see "Changing Options"
below to fix this. You can even change your email address
for all of the mailing lists at once.
Changing Options
----------------
Go to the main web page
http://onebuilding.org/
Click on the link on the left for the mailing list you want
to change your options on. At the bottom of the page for the
specific mailing list, in the field near the button
"unsubscribe or edit options" enter your email address and
press that button. The next page will ask for a password, if
you don't remember yours click on the remind button and one
will be emailed to you. From this page you can change to
digest mode or your email address or other options.
Archives
--------
Each of the building energy simulation mailing lists have
archives of the messages posted. There is a good chance you
can find the answer you are looking for by searching the
archives. Go to
http://onebuilding.org/
In each paragraph about the mailing list is a link to the
archives. You can search that list from that page. In
addition, you can use Google to search the entire site
across all mailing lists by going to:
http://onebuilding.org/search.html
Digest Mode
-----------
If you would rather receive a single email each day with all
of the messages within it, you can use Digest Mode. See the
"Changing Options" section above to turn on Digest Mode.
Links to Related Sites
----------------------
If you are interested in other simulation program mailing
lists or other sites related to building energy simulation,
see the list of links at:
http://onebuilding.org/links.html
If you have suggestions for additional links, please send me
an email.
Subject Lines
-------------
For BLDG-SIM, if the question is about a specific simulation
program, please include the name of the simulation program
in the subject line. Also please post a question about a
specific simulation program to the appropriate mailing list
first to see if you can get an answer and post to BLDG-SIM
the next day if you have not. If you are replying to a
message in a digest, please see the section below.
Replying to a Digest
--------------------
If you receive a digest, when replying to a message in the
digest, please copy the original subject line and don't
include the entire digest when replying. Just include the
original message.
I Still Need Help
-----------------
Please email me with your question, I'll try to help:
jglazer at gard.com
Suggestions
-----------
If you have suggestions on how to improve the mailing lists,
add a mailing list, improve the onebuilding.org web site, or
additions to this email message please send me an email.
jglazer at gard.com
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
------------------------------
Subject: Digest Footer
_______________________________________________
Trace-users mailing list
Trace-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
------------------------------
End of Trace-users Digest, Vol 66, Issue 1
******************************************
More information about the Trace-users
mailing list