[Trace-users] Percent Outside Air (UNCLASSIFIED)

Scott Parker sparker at aeieng.com
Tue Jun 3 13:23:12 PDT 2014


I prefer manual calculations, but if you want to use Trace to do the ventilation calculations then you can set a "Max Vent (Z) Ratio Allowed".  You can try a little trial and error but likely between 30 and 60%.



[cid:image001.png at 01CF7F48.1C2BF750]



SCOTT PARKER



-----Original Message-----
From: Trace-users [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
Sent: Tuesday, June 03, 2014 4:16 PM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Percent Outside Air (UNCLASSIFIED)



Classification: UNCLASSIFIED

Caveats: NONE





I have an Variable Volume Reheat (30% Min Flow Default) and used the System Ventilation Flag to ASHRAE 62.1 with Vent Rest. When I ran the model the system was running 100% Outside air.  I looked at the 62.1 report and saw that there were corridors and storage rooms driving the 100%, so I set the air flow for those rooms higher.  I repeated this process of finding the critical zones and increasing the supply cfm to drive down the outside air percentage.



I've got it down to 43.4%, but is there a better way to accomplish this?



When I run it with summing outside air requirements, the highest zone is 32% outside air, but the values don't comply with 62.1.



Is the best method just to find the critical zones and increasing the cfms and repeat?







Classification: UNCLASSIFIED

Caveats: NONE





_______________________________________________

Trace-users mailing list

http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 38150 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20140603/164aa4f5/attachment.png>


More information about the Trace-users mailing list