[Trace-users] Cooling Only (Design) Schedules and LEED Energy Modeling
Jason Dietterick
Dietterick at stonehousegroup.net
Mon Sep 16 08:31:12 PDT 2013
Ben,
I don't think there is necessarily a problem using this schedule as far as LEED goes, but I think you are hurting yourself by doing so. By making all loads 100% 24/7 you will drive energy consumption way up and dilute potential savings with high annual costs. LEED requires that systems cycle with occupancy and using this schedule indicates that all spaces are occupied all the time, therefore systems will run all the time. This schedule is ideal for load calculations as it presents you with a worst case scenario... 100% of loads for cooling and 0% for heating, however this will likely never be the case during actual operation. Personally, I like to create my own schedules that still include 100% 24/7 for cooling design, but weekday/weekend schedules that reflect actual occupancy. Keep in mind that heating design should always be zero, as you don't want people/light/receptacle loads to help heat the space when designing for worst case scenario. Ventilation schedules however should be set to 100% for heating design however, as this needs to be factored in for your heating worst case scenario.
Hope that helps!
Best,
Jay
Jason Dietterick
Associate, Energy Modeler
The Stone House Group
DIRECT DIAL 484.548.4007
301 Broadway Ave
Bethlehem, PA 18015
Tel 610.868.9600
Fax 610.868.2272
From: trace-users-bounces at lists.onebuilding.org [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Ben
Sent: Monday, September 16, 2013 11:16 AM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Cooling Only (Design) Schedules and LEED Energy Modeling
I am working on an energy model for a LEED project using Trace, it's my first one, and I was going through the error comments Trace generates and I saw a warning about using the Cooling Only (Design) schedule. Essentially the warning was that ASHRAE requires schedules to be reflective of actual occupant uses, and cooling only schedules wouldn't be realistic.
I use this schedule all the time when using Trace for HVAC loads but I'm nervous now using it from energy modeling. Will this get me a review comment if a reviewer see's that I used this schedule, or is this schedule pretty typically used in an energy model?
Thanks.
[cid:image001.png at 01CEB2CF.65618F70]
Ben Hollon, EIT, LEED(r) AP BD+C, MBA
email: bhollon at antella-inc.com<mailto:xxxxxx at antella-inc.com>
Cell (816) 536-3434 * Tele: (816) 421-0950 ext. 104
________________________________
Antella Consulting Engineers, inc.
1600 Genessee, Suite 667 * Kansas City, MO 64102 * Tele: (816) 421-0950 * Fax: (816) 249-2439 * www.antella-inc.com<http://www.antella-inc.com>
DISCLAIMER: The information contained in this electronic communication, as well as in any attachments, is privileged and confidential and intended solely for use by the addressee(s). Any other use, dissemination, or copying of this electronic communication is strictly prohibited and is an interference with Antella Consulting Engineers, inc. confidential business relationships. If you received this communication in error, please notify me immediately and permanently delete the original and any electronic or printed copies of this electronic communication.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130916/62e6c5a5/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 17316 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130916/62e6c5a5/attachment-0002.png>
More information about the Trace-users
mailing list