[Trace-users] Part load conditions
Scott Parker
sparker at aeieng.com
Thu Jan 24 10:59:03 PST 2013
Catalina,
The check box for "Apply ECB/PRM rules to fan sizing?" just sets the design fan power. The fan curve must be applied separately as I showed on the "Fans" tab under Systems section of Trace. Every project will have the exact same baseline fan curve, but the design fan power for the baseline is unique for each project, and that checkbox allows the program to calculate it rather than you doing it manually. I leave it up to you as whether you trust the output from Trace or not on the fan power design power. You can see the originally input value and the corrected kW value for each fan on the Equipment Energy Consumption report if you allow Trace to calculate the fan power.
Scott
From: Caballero, Catalina [mailto:ccaballero at jalrw.com]
Sent: Thursday, January 24, 2013 9:44 AM
To: Scott Parker; trace-users at lists.onebuilding.org
Cc: Varghese, Saju
Subject: RE: Part load conditions
Scott,
What we have seen is that the Trace700 PRM Sizing works correctly and you just need to submit the PRM report but I don't know if that particular requirement for G3.1.3.15 Part 2 can be done using it.
Thanks.
Catalina Caballero, AIA. Assoc., LEED GA.
Johnson, Avedano, Lopez, Rodriguez & Walewski
Engineering Group, Inc.
2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
Visit us online: www.jalrw.com<http://www.jalrw.com/>
[JALRW Logo]
HVAC - Electrical - Plumbing - Fire Protection
Sustainable Development - Commissioning
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited.
From: Scott Parker [mailto:sparker at aeieng.com]
Sent: Thursday, January 24, 2013 9:15 AM
To: Caballero, Catalina; trace-users at lists.onebuilding.org<mailto:trace-users at lists.onebuilding.org>
Subject: RE: Part load conditions
Catalina,
I would guess that you are working on a LEED project. From my experience the LEED reviewer will not accept the automatic fan calculation within Trace. You need to manually calculate the maximum break HP for each fan for the baseline systems. I recommend putting them in units of kW/CFM. You will need to manually do the fan power calculations according to 90.1 and adjust for any "allowances" per 90.1. Please don't use the Full Load Energy Rate numbers I have used. You'll need to calculate these for your specific conditions per 90.1 requirements.
[cid:image002.png at 01CDFA3A.C7EBD0E0]
Scott
From: Caballero, Catalina [mailto:ccaballero at jalrw.com]
Sent: Thursday, January 24, 2013 9:03 AM
To: Scott Parker; trace-users at lists.onebuilding.org<mailto:trace-users at lists.onebuilding.org>
Subject: RE: Part load conditions
Can the software calculate it automatically with the following feature on?
[cid:image003.png at 01CDFA3A.C7EBD0E0]
Regards,
Catalina
From: Scott Parker [mailto:sparker at aeieng.com]
Sent: Thursday, January 24, 2013 9:01 AM
To: Caballero, Catalina; trace-users at lists.onebuilding.org<mailto:trace-users at lists.onebuilding.org>
Subject: RE: Part load conditions
Catalina,
You can define a custom fan curve based on the 90.1 cubic equation, but I would recommend that you use the 90.1 fan curve library member that comes with the program. The curve is the same for 2004 and 2007 versions of 90.1.
[cid:image004.png at 01CDFA3A.C7EBD0E0][cid:image005.jpg at 01CDFA3A.C7EBD0E0]
Scott
From: trace-users-bounces at lists.onebuilding.org<mailto:trace-users-bounces at lists.onebuilding.org> [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Caballero, Catalina
Sent: Thursday, January 24, 2013 8:53 AM
To: trace-users at lists.onebuilding.org<mailto:trace-users at lists.onebuilding.org>
Subject: [Trace-users] Part load conditions
Hi all,
How do you show this method on Trace 700 for System 6?
[cid:image006.png at 01CDFA3A.C7EBD0E0]
Thanks,
Catalina Caballero, AIA. Assoc., LEED GA.
Johnson, Avedano, Lopez, Rodriguez & Walewski
Engineering Group, Inc.
2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
Visit us online: www.jalrw.com<http://www.jalrw.com/>
[JALRW Logo]
HVAC - Electrical - Plumbing - Fire Protection
Sustainable Development - Commissioning
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4129 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 19569 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1719 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 189 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 58052 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 17488 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/10d93a48/attachment-0011.png>
More information about the Trace-users
mailing list