[Trace-users] Part load conditions
Houcine Tlemsani
houcine at mepengsolutions.com
Thu Jan 24 09:30:49 PST 2013
To All
We have submitted the trace report fan power calcs to LEED on multiple
jobs and we had no problems.
The calcs are accurate.
Houcine Tlemsani
Mechanical Designer
MEP Engineering Solutions
houcine at mepengsolutions.com
Phone: 850.429.8288
Fax: 850.429.8334
________________________________
From: trace-users-bounces at lists.onebuilding.org
[mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of
Caballero, Catalina
Sent: Thursday, January 24, 2013 8:44 AM
To: 'Scott Parker'; trace-users at lists.onebuilding.org
Cc: Varghese, Saju
Subject: Re: [Trace-users] Part load conditions
Scott,
What we have seen is that the Trace700 PRM Sizing works correctly and
you just need to submit the PRM report but I don't know if that
particular requirement for G3.1.3.15 Part 2 can be done using it.
Thanks.
Catalina Caballero, AIA. Assoc., LEED GA.
Johnson, Avedano, Lopez, Rodriguez & Walewski
Engineering Group, Inc.
2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
Visit us online: www.jalrw.com <http://www.jalrw.com/>
HVAC - Electrical - Plumbing - Fire Protection
Sustainable Development - Commissioning
This email and any files transmitted with it are confidential and are
intended solely for the use of the individual or entity to which they
are addressed. If you are not the intended recipient or the person
responsible for delivering the email to the intended recipient, be
advised that you have received this email in error and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly prohibited.
From: Scott Parker [mailto:sparker at aeieng.com]
Sent: Thursday, January 24, 2013 9:15 AM
To: Caballero, Catalina; trace-users at lists.onebuilding.org
Subject: RE: Part load conditions
Catalina,
I would guess that you are working on a LEED project. From my
experience the LEED reviewer will not accept the automatic fan
calculation within Trace. You need to manually calculate the maximum
break HP for each fan for the baseline systems. I recommend putting
them in units of kW/CFM. You will need to manually do the fan power
calculations according to 90.1 and adjust for any "allowances" per 90.1.
Please don't use the Full Load Energy Rate numbers I have used. You'll
need to calculate these for your specific conditions per 90.1
requirements.
Scott
From: Caballero, Catalina [mailto:ccaballero at jalrw.com]
Sent: Thursday, January 24, 2013 9:03 AM
To: Scott Parker; trace-users at lists.onebuilding.org
Subject: RE: Part load conditions
Can the software calculate it automatically with the following feature
on?
Regards,
Catalina
From: Scott Parker [mailto:sparker at aeieng.com]
Sent: Thursday, January 24, 2013 9:01 AM
To: Caballero, Catalina; trace-users at lists.onebuilding.org
Subject: RE: Part load conditions
Catalina,
You can define a custom fan curve based on the 90.1 cubic equation, but
I would recommend that you use the 90.1 fan curve library member that
comes with the program. The curve is the same for 2004 and 2007
versions of 90.1.
Scott
From: trace-users-bounces at lists.onebuilding.org [
mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of
Caballero, Catalina
Sent: Thursday, January 24, 2013 8:53 AM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Part load conditions
Hi all,
How do you show this method on Trace 700 for System 6?
Thanks,
Catalina Caballero, AIA. Assoc., LEED GA.
Johnson, Avedano, Lopez, Rodriguez & Walewski
Engineering Group, Inc.
2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
Visit us online: www.jalrw.com <http://www.jalrw.com/>
HVAC - Electrical - Plumbing - Fire Protection
Sustainable Development - Commissioning
This email and any files transmitted with it are confidential and are
intended solely for the use of the individual or entity to which they
are addressed. If you are not the intended recipient or the person
responsible for delivering the email to the intended recipient, be
advised that you have received this email in error and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4129 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 38071 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0011.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4787 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0012.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 252 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 58052 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0013.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13052 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130124/7459551e/attachment-0014.jpeg>
More information about the Trace-users
mailing list