[Trace-users] heat pump cut off
Mark Denyer
mark.denyer at mfia-eng.com
Tue Aug 20 13:22:21 PDT 2013
This is how I replied to the very same review comment about heat pump
operating temps, and elect strip heat.
This screen capture shows the efficiencies of the PTHPs used for the
baseline. The Unloading curves show that the system is designed to
calculate efficiencies and capacities as outdoor temperatures vary.
This screen capture shows that the PTHPs will operate down to 17 degrees
F, and the electric strip heat is the second stage of heating if the
compressor cannot keep up.
The secondary capacity curve prevents the strip heat from being
activated when the outdoor temp is above 40 F.
On 8/20/2013 1:11 PM, trace-users-request at lists.onebuilding.org wrote:
> Send Trace-users mailing list submissions to
> trace-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> trace-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> trace-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Trace-users digest..."
>
>
> Today's Topics:
>
> 1. Heat Pump Cut Off (UNCLASSIFIED) (Eurek, John S NWO)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Tue, 20 Aug 2013 16:56:19 +0000
> From: "Eurek, John S NWO" <John.S.Eurek at usace.army.mil>
> To: "trace-users at lists.onebuilding.org"
> <trace-users at lists.onebuilding.org>
> Subject: [Trace-users] Heat Pump Cut Off (UNCLASSIFIED)
> Message-ID:
> <E777FD5A41D3B04A83296213737A85D7070018D9 at EIS-MB05WPC.eis.ds.usace.army.mil>
>
> Content-Type: text/plain; charset="us-ascii"
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
> How do you have the Heat Pumps use electric heat below 40 degrees and cut off the compressor entirely below 17 degrees?
>
> -Here is the insightful comment from the leed reviewing oracle.
>
> Additionally, ensure that the Baseline heat pumps are modeled according to Section G3.1.3.1, which requires that the electric air?source heat pumps are modeled with electric auxiliary heat that only energizes on the last thermostat stage and when the outdoor air temperature is less than 40 degrees F. This means that the heat pump and auxiliary heat should operate together at low temperature conditions, with the compressor as the lead machine. The outside air cutoff temperature for the compressor must be no greater than the temperature associated with the low-temperature heating efficiency requirements of Table 6.8.1B (17 degrees F).
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
>
>
> ------------------------------
>
> _______________________________________________
> Trace-users mailing list
> Trace-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>
> End of Trace-users Digest, Vol 57, Issue 1
> ******************************************
>
>
--
Mark Denyer P.E. LEED^(TM) AP BD&C
Principal
MFIA, Inc. Consulting Engineers
2007 SE Ash St.
Portland, Oregon 97214
(503) 234-0548
mark.denyer at mfia-eng.com
www.mfia-eng.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130820/c9f5de48/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: bdhfecab.png
Type: image/png
Size: 121412 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130820/c9f5de48/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: clip_image002.jpg
Type: image/jpeg
Size: 56545 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130820/c9f5de48/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: clip_image004.jpg
Type: image/jpeg
Size: 38138 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130820/c9f5de48/attachment-0003.jpg>
More information about the Trace-users
mailing list