Hi Karen-

To Add to the correct answer given by Grant

No, you cannot have two lighting schedules on the same room. But that
doesn't mean that you can't do what you intend to do.

Two options I've used:

1) Find the peak watts/square foot for all lights, and use a lighting
schedule (the schedule just multiplies the peak watts/square foot by a
percent - so you can essentially "merge" two schedules into one and account
for the hourly lighting). However, this may not be possible if you are
concerned about heat to the plenum

2) Create custom misc. load called something like  "Process lighting" in
the library/template editor. You can set up the percentage of the lights
that goes to the plenum and set everything but the ballast factor, which
isn't necessary in such a case. You can have multiple receptacle loads per
room and thus add a 2nd lighting schedule as well as have plug loads.

Hope that helps, but let me know as I can guess at a few questions that
might come up, but I don't wish to be long-winded as Grant probably
answered the question for you.

Bob Fassbender
Energy-modelscom

On Tue, Oct 9, 2012 at 3:07 PM,
<trace-users-request at lists.onebuilding.org>wrote:

> Send Trace-users mailing list submissions to
>         trace-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> or, via email, send a message with subject or body 'help' to
>         trace-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
>         trace-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Trace-users digest..."
>
>
> Today's Topics:
>
>    1. 2 lighting schedules on the same room (Karen Smith)
>       (Page, Grant B)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Tue, 9 Oct 2012 14:18:53 -0400
> From: "Page, Grant B" <Grant.Page at masonandhanger.com>
> To: "trace-users at lists.onebuilding.org"
>         <trace-users at lists.onebuilding.org>
> Subject: [Trace-users] 2 lighting schedules on the same room (Karen
>         Smith)
> Message-ID:
>         <
> 9A307EE77FAD5B4FB69F8C6E951F0E185E65E85197 at LEXMAIL1.corp.dayzim.com>
> Content-Type: text/plain; charset="us-ascii"
>
> I would set it up as a misc load with a specific schedule.
>
> Grant Page, PE, CGD, LEED AP BD+C
> Mechanical Engineer
> Mason & Hanger
>
> -----Original Message-----
> From: trace-users-bounces at lists.onebuilding.org [mailto:
> trace-users-bounces at lists.onebuilding.org] On Behalf Of
> trace-users-request at lists.onebuilding.org
> Sent: Saturday, October 06, 2012 4:07 PM
> To: trace-users at lists.onebuilding.org
> Subject: Trace-users Digest, Vol 48, Issue 4
>
> Send Trace-users mailing list submissions to
>         trace-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> or, via email, send a message with subject or body 'help' to
>         trace-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
>         trace-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific than
> "Re: Contents of Trace-users digest..."
>
>
> Today's Topics:
>
>    1. 2 lighting schedules on the same room (Karen Smith)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Sat, 6 Oct 2012 10:00:33 -0400
> From: Karen Smith <skaren758 at gmail.com>
> To: trace-users at lists.onebuilding.org
> Subject: [Trace-users] 2 lighting schedules on the same room
> Message-ID:
>         <
> CANwPo+mzsodDMpvLZxuZmSCooOcGT5-OJWwXhJUu_Gg2iQsBCA at mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Hello all,
>
> Does anybody know if its possible to put 2 lighting schedules in the same
> room?
>
> Regards,
>
> Karen Smith
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121006/2b7ed21d/attachment.html
> >
>
> ------------------------------
>
> _______________________________________________
> Trace-users mailing list
> Trace-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>
> End of Trace-users Digest, Vol 48, Issue 4
> ******************************************
>
>
> ------------------------------
>
> _______________________________________________
> Trace-users mailing list
> Trace-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>
>
> End of Trace-users Digest, Vol 48, Issue 5
> ******************************************
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20121009/57019e6d/attachment.htm>


More information about the Trace-users mailing list