[Trace-users] Unmet Loads (UNCLASSIFIED)
Scott Parker
sparker at aeieng.com
Mon Aug 6 12:11:01 PDT 2012
John,
The best way to look at unmet load hours in Trace is to use the Building Temperature Report. This will show you which rooms have unmet load hours, and the output will be sorted by system. Therefore your step of creating multiple models is time consuming and not required. The image below shows the report checked in the output.
Also, this report will show you when the unmet hours occur for the rooms that have unmet load hours. This report makes it quick to focus on spaces with unmet load hours.
[cid:image001.png at 01CD73E5.6FA6A670]
[cid:image002.png at 01CD73E5.AFE26FD0]
Regards,
Scott Parker
-----Original Message-----
From: trace-users-bounces at lists.onebuilding.org [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
Sent: Monday, August 06, 2012 3:04 PM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Unmet Loads (UNCLASSIFIED)
Classification: UNCLASSIFIED
Caveats: NONE
I know there are many ways to get rid of unmet load hours. What I want it to look at the output in an excel format and see the unmet load hours. How can I see the actual numeric output? I have many systems so I'm not even sure which system I need to trouble shoot.
Right now I'm making multiple copies of the project and in each file deleting all systems but 1, so I can identify the offending system.
Classification: UNCLASSIFIED
Caveats: NONE
_______________________________________________
Trace-users mailing list
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20120806/cf532c64/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25719 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20120806/cf532c64/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 19248 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20120806/cf532c64/attachment-0005.png>
More information about the Trace-users
mailing list