[Trace-users] Heat Pump Auxiliary Heat (UNCLASSIFIED)
Eurek, John S NWO
John.S.Eurek at usace.army.mil
Thu Aug 2 14:49:17 PDT 2012
Classification: UNCLASSIFIED
Caveats: NONE
Short question:
What is the easiest way to have the electric heat to provide heating for packaged rooftop when the outside temperature is less than 40 degrees? Or is this even what the review is looking for?
The full comment from my good magnanimous friend from LEED.
6. It is unclear if the packaged rooftop heat pumps in the Baseline model were modeled according to Section G3.1.3.1, which requires that the electric air‐source heat pumps are modeled with electric auxiliary heat that only energizes on the last thermostat stage and when the outdoor air temperature is less than 40 degrees F. This means that the heat pump and auxiliary heat should operate together at low temperature conditions, with the compressor as the lead machine. The outside air cutoff temperature for the compressor must be no greater than the temperature associated with the low-temperature heating efficiency requirements of Table 6.8.1B (17 degrees F). Note that for packaged heat pump units smaller than 65,000 Btuh, the HSPF rating accounts for electric auxiliary operation, and includes test conditions at 17 degrees F. Please indicate the modeled characteristics of the electric auxiliary heat in Table 1.4 including the temperature at which the auxiliary heat engages, and the outside air temperature cutoff for the compressor. If the compressor low temperature cutoff is modeled as greater than 17 degrees F for packaged heat pump units smaller than 65,000 Btuh, describe how the Baseline efficiency of the heat pump was modeled to reflect the HSPF rating including auxiliary heating energy.
John Eurek
Classification: UNCLASSIFIED
Caveats: NONE
More information about the Trace-users
mailing list