[Trace-users] Pool Dehumidification Equipment Sizing
Scott Hackel
shackel at ecw.org
Tue May 11 12:17:52 PDT 2010
Calculating an accurate evaporation rate is the most important piece so you're most of the way there... I've had good luck in modeling pools as a miscellaneous heat gain to the space (in 'Internal loads' in whichever room you are using as your pool); be sure you create the load in the library to be 90-100% latent.
Then assign the same load to the pool heater; you can tie it directly by calling it a heating load, or enter it as a 'Base utility' under Plants.
You'll also need to assign a humidity control to the pool room so that the HVAC system keeps it appropriately dry. You may also need to set the supply air temperature; TRACE may respond strangely otherwise.
Good luck -
Scott Hackel, P.E., LEED AP
Energy Engineer
Energy Center of Wisconsin
455 Science Drive, Suite 200
Madison, WI 53711
608.238.8276 x129
shackel at ecw.org
The Buildings Team
Design decisions through energy, economics and emissions analysis.
www.ecw.org/Buildings
-----Original Message-----
From: trace-users-bounces at lists.onebuilding.org [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of trace-users-request at lists.onebuilding.org
Sent: Monday, May 10, 2010 2:07 PM
To: trace-users at lists.onebuilding.org
Subject: Trace-users Digest, Vol 22, Issue 3
Send Trace-users mailing list submissions to
trace-users at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
trace-users-request at lists.onebuilding.org
You can reach the person managing the list at
trace-users-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Trace-users digest..."
Today's Topics:
1. Pool Dehumidification Equipment Sizing (Jon Bruneau)
----------------------------------------------------------------------
Message: 1
Date: Mon, 10 May 2010 14:11:19 -0400
From: Jon Bruneau <jon at f7engineers.com>
To: "trace-users at lists.onebuilding.org"
<trace-users at lists.onebuilding.org>
Subject: [Trace-users] Pool Dehumidification Equipment Sizing
Message-ID:
<EADD21123407AE4C8C9F8CA7F3273BCE9D39557D60 at mse21be1.mse21.exchange.ms>
Content-Type: text/plain; charset="us-ascii"
Does anyone know of a good way to model indoor swimming pools in Trace? I estimated the pool evaporation rate using the formula from the ASHRAE Handbook - Applications but I'm unsure of the best way to plug this into the Trace model.
Thanks,
Jon
Jon Bruneau, PE, LEED AP BD+C
Mechanical Engineer
F7 Engineering Group
400 10th Street NE, Suite B, Charlottesville, VA 22902
ph. 434.244.0023
fax 434.977.0023
www.F7engineers.com<http://www.f7engineers.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20100510/2a445ff5/attachment.html>
------------------------------
_______________________________________________
Trace-users mailing list
Trace-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
End of Trace-users Digest, Vol 22, Issue 3
******************************************
More information about the Trace-users
mailing list