[Simergy-users] Functional Plenum Zones
Simergy Beta Program
SimergyBetaProgram at DigitalAlchemyPro.com
Sat Oct 10 11:11:18 PDT 2015
Fred,
To make plena work (shared or dedicated), you need to do all of the
following:
1) When you create your building stories - do the following:
* In the Create/Edit Building palette/"Building Stories" tab -
select "Ceiling Plena"' in 'Plenum Configuration and also set the above
'Ceiling Configuration' (we used "Single zone" in our example below - to
have a single shared plenum) --- See Image-1 below
* Then click "Preview", followed by "Save" --- to create your
building stories
This will make the above ceiling spaces into plena that are available of use
in the HVAC loop. See Image-2 (note the Ceiling Plena highlighted in the
tree)
2) When making your Zone HVAC Groups
* Include a supply plenum above Air Terminal - drag/drop from the
stencil - just like the components (in our example, we used a Shared Supply
Plenum). See Image-3
3) Assigning the Zone group to an Air Loop is just as before - but with
one additional step
* Select the Zone HVAC Group in the tree > right-click > "Assign to
Air Loop"
* In the Air Loop Diagram workspace > select the Plenum > select the
appropriate Plenum zone in the Zone Name field of the Component Data (lower
left). In our example, this loop is conditioning the first floor, so the
appropriate plenum zone is "Ceiling Plenum Zone 1-1". See Image-4 (note
that it validates)
Regards,
Simergy Beta Test Program
SimergyBetaProgram at DigitalAlchemyPro.com
<mailto:SimergyBetaProgram at DigitalAlchemyPro.com>
www.DigitalAlchemyPro.com <http://www.DigitalAlchemyPro.com>
_____
Image-1
Image-2
Image-3
Image-4
From: Simergy-users [mailto:simergy-users-bounces at lists.onebuilding.org] On
Behalf Of Porter, Frederick NOR
Sent: Thursday, October 1, 2015 4:38 PM
To: simergy-users at lists.onebuilding.org
Subject: [Simergy-users] Functional Plenum Zones
I'm just getting started and am trying the latest Simergy Pro. Can anyone
tell me if return and supply plenum zones are really supported?
If so, is there some clear set of procedures for getting from the geometric
"ceiling plena or voids" to airflow through them?
As far as I can tell, only the ASHRAE System 7 model shows plenum zones
under the "spatial zones" branch of the project tree. However none of these
are referenced in the Zone HVAC Groups, which requires an entry of a
"shared" or "dedicated" plenum component between the zone outlet and the
"supply" inlet. But when I've tried this, Simergy itself hangs or the model
doesn't run. The model as supplied runs, but the "plena" are just simulated
as unconditioned zones/spaces when I examine the IDF.
I tried importing a E+ 8.0 sample idf with floor/supply and return plenums,
and that didn't go anywhere either.
Thanks,
Fred
Fred Porter, BEMP, LEEDC AP
Principal Engineer
Sustainability Services
NORESCO
2540 Frontier Ave, Suite 100, Boulder, CO 80301
fporter at noresco.com <mailto:fporter at noresco.com>
www.noresco.com <http://www.noresco.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/dd33307c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 76303 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/dd33307c/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 77066 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/dd33307c/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 71401 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/dd33307c/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 73369 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/dd33307c/attachment-0003.jpeg>
More information about the Simergy-users
mailing list