[Simergy-users] Gas Unit Heater Zone HVAC Group Issue
End User Support
Support at DigitalAlchemyPro.com
Sat Oct 10 10:04:44 PDT 2015
Trevor,
If we understand you correctly, your Zone HVAC Group diagram should look
like this (note that the heating coil name references a Gas heating coil and
that the off-page reference says 'Gas'):
The error message you cite seems to indicate that the off-page reference
_might_ say 'HW' instead. If this is the case, then you have mistakenly
selected a HW heating coil which requires a cross-loop reference to a HW
loop.
Regards,
Simergy Support
Support at DigitalAlchemyPro.com <mailto:Support at DigitalAlchemyPro.com>
www.DigitalAlchemyPro.com <http://www.digitalalchemypro.com/>
From: Simergy-users [mailto:simergy-users-bounces at lists.onebuilding.org] On
Behalf Of Trevor Jaffe
Sent: Tuesday, September 1, 2015 11:45 AM
To: simergy-users at lists.onebuilding.org
Subject: [Simergy-users] Gas Unit Heater Zone HVAC Group Issue
Simergy list serve users,
I am having issues with a zone gas fired unit heater and DOAS/exhaust
system. The problem is that the gas fired zone unit heater seems to be
requiring some sort of loop. The error shown when validating the air loop
is as follows:
"Component (UHW-1) does not have a cross loop reference assigned. Assign
cross loop reference to this component."
My process for creating this system was as follows:
1. I created the zone HVAC group as a gas unit heater with a
temperature controller, temperature sensor, and uncontrolled single duct air
inlet. I built this template from scratch.
2. I assigned my thermal zone to this zone HVAC group.
3. I created the air loop. I built this template from the out of the
box CAV_dxC_gasH and removed the DX cooling coil.
4. I assigned my thermal zone to this air loop.
When I complete step 4, the gas heater in my zone changes to hot water.
When I check back to my zone HVAC group, the unit heater shows as gas like
before. Clicking back on the air loop again reveals the unit heater
magically restored to gas. But I'm thinking some remnant of the hot water
unit heater requirements remain and are causing the error shown above.
I have outlined a couple issues here and I'd like to understand what is
going on, but my foremost concern is to get the air loop validated with no
errors.
Thanks in advance for you help!
Trevor Jaffe | PE, LEED AP BD+C
Mechanical Engineer
Westlake
1634 Eye Street NW
Reed
Suite 900
Leskosky
Washington DC 20006
T 202 296 4344 x3108
F 202 296 6116
Washington DC | New York | Phoenix | Los Angeles | Cleveland
<http://www.wrldesign.com> www.wrldesign.com |
<http://www.facebook.com/wrldesign> Facebook |
<http://www.twitter.com/wrldesign> Twitter |
<http://www.linkedin.com/company/47906> LinkedIn
Architect Magazine 2014; Ranked #1 Overall among U.S. design firms; #5 in
Sustainability
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/05c0c915/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 68290 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/simergy-users-onebuilding.org/attachments/20151010/05c0c915/attachment.jpeg>
More information about the Simergy-users
mailing list