<div dir="ltr">Hi Nick and everyone who replied - thank you all for your help. It's great to see so much support in the community :-)<div><br></div><div>So it turns out what I was actually after was a way to generate ground temperatures for a random set of weather data. Someone kindly send me the fortran script that E+ uses for its EPW files which is exactly what I needed.</div><div><br></div><div>Have a great new year all look forward to catching up in 2016.</div><div><br></div><div>Andrew</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div><span style="color:rgb(29,58,114);font-family:'Helvetica Neue';font-size:12px;font-weight:700;white-space:pre-wrap;line-height:1.38;background-color:transparent">Andrew Corney • PE, M.CIBSE, M.ASHRAE</span><br></div><div><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">Product Director </span></p><span style="font-size:12.8px"><p dir="ltr" style="line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">Sefaira - Sustainability • Performance • Design</span></p></span><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">M <a href="tel:%2B44%20%280%297887%20059%20722" value="+447887059722" style="color:rgb(17,85,204)" target="_blank">+44 (0)7887 059 722</a></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">T <a href="tel:%2B44%20%280%292037%20147%20619" value="+442037147619" style="color:rgb(17,85,204)" target="_blank">+44 (0)2037 147 619</a></span><br></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">Skype andrew.corney.sefaira</span></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px"><br></span></span></p><p style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">Read<a href="http://continuingeducation.bnpmedia.com/article.php?L=480&C=1446" target="_blank"> this article</a> in Architecture Record and complete a quiz to earl AIA and GBCI credit</span></span></p><div><br></div><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:10.6667px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">This email was sent from Sefaira UK Ltd.</span></p><span style="font-size:12.8px"><p dir="ltr" style="line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:10.6667px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">For company contact and registration information, please visit:</span><span style="font-size:10.6667px;font-family:'Helvetica Neue';vertical-align:baseline;white-space:pre-wrap;background-color:transparent"> </span><span style="color:rgb(17,85,204);text-decoration:underline;font-size:10.6667px;font-family:'Helvetica Neue';vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><a href="http://www.sefaira.com/info/contact" style="color:rgb(17,85,204);text-decoration:none" target="_blank">http://www.sefaira.com/info/contact</a></span></p><div><span style="color:rgb(29,58,114);font-family:'Helvetica Neue';font-size:12px;font-style:italic;line-height:16.56px;white-space:pre-wrap"><br></span></div><div><br></div></span></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Mon, Jan 4, 2016 at 2:47 PM, Nicholas Caton <span dir="ltr"><<a href="mailto:ncaton@catonenergy.com" target="_blank">ncaton@catonenergy.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><p dir="ltr">Hi Andrew!</p>
<p dir="ltr">Oklahoma State University in Stillwater, OK produces quite a bit of research concerning the developing science of ground source wellfield system design and verification. Also, individuals I personally consider leaders in our circles of energy simulation when it comes to anything ground source spent time with that department. </p>
<p dir="ltr">If there exists an established best practice for extrapolating ground temperatures (short of direct measurement), there's a good chance someone at that institution knows and possibly even derived the answer ;-). </p>
<p dir="ltr">Of course if you're lucky someone will reply with a direct answer - here's hoping!<br></p>
<p dir="ltr">~Nick</p>
<div class="gmail_quote"><div><div class="h5">On Dec 23, 2015 2:38 PM, "Andrew Corney" <<a href="mailto:andrew.corney@sefaira.com" target="_blank">andrew.corney@sefaira.com</a>> wrote:<br type="attribution"></div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5"><div dir="ltr">Hi All,<div><br></div><div>Does anyone know of a peer-reviewed paper / methodology they could share with me that describes a process for converting annual weather data into monthly groundwater temperatures?</div><div><br></div><div>Obviously a lot of EPW files already have ground water temperatures but many don't and a lot of other weather data doesn't have that information so it'd be great to know if there was a well-recognised process for making those estimates.</div><div><br></div><div>Thanks in advance for any help anyone can provide.</div><div><br></div><div>best regards,</div><div><br></div><div>Andrew</div><div><br clear="all"><div><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div><span style="color:rgb(29,58,114);font-family:'Helvetica Neue';font-size:12px;font-weight:700;white-space:pre-wrap;line-height:1.38;background-color:transparent">Andrew Corney • PE, M.CIBSE, M.ASHRAE</span><br></div><div><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">Product Director </span></p><span style="font-size:12.8px"><p dir="ltr" style="line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">Sefaira - Sustainability • Performance • Design</span></p></span><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">M <a href="tel:%2B44%20%280%297887%20059%20722" value="+447887059722" style="color:rgb(17,85,204)" target="_blank">+44 (0)7887 059 722</a></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">T <a href="tel:%2B44%20%280%292037%20147%20619" value="+442037147619" style="color:rgb(17,85,204)" target="_blank">+44 (0)2037 147 619</a></span><br></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">Skype andrew.corney.sefaira</span></span></p><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px"><br></span></span></p><p style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:12px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><span style="line-height:16.56px">Read<a href="http://continuingeducation.bnpmedia.com/article.php?L=480&C=1446" target="_blank"> this article</a> in Architecture Record and complete a quiz to earl AIA and GBCI credit</span></span></p><div><br></div><p dir="ltr" style="font-size:12.8px;line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:10.6667px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">This email was sent from Sefaira UK Ltd.</span></p><span style="font-size:12.8px"><p dir="ltr" style="line-height:1.38;margin-top:0pt;margin-bottom:0pt"><span style="font-size:10.6667px;font-family:'Helvetica Neue';color:rgb(68,68,68);vertical-align:baseline;white-space:pre-wrap;background-color:transparent">For company contact and registration information, please visit:</span><span style="font-size:10.6667px;font-family:'Helvetica Neue';vertical-align:baseline;white-space:pre-wrap;background-color:transparent"> </span><span style="color:rgb(17,85,204);text-decoration:underline;font-size:10.6667px;font-family:'Helvetica Neue';vertical-align:baseline;white-space:pre-wrap;background-color:transparent"><a href="http://www.sefaira.com/info/contact" style="color:rgb(17,85,204);text-decoration:none" target="_blank">http://www.sefaira.com/info/contact</a></span></p><div><span style="color:rgb(29,58,114);font-family:'Helvetica Neue';font-size:12px;font-style:italic;line-height:16.56px;white-space:pre-wrap"><br></span></div><div><br></div></span></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div>
</div></div>
<br></div></div><span class="">_______________________________________________<br>
Ibpsausa mailing list<br>
<a href="mailto:Ibpsausa@lists.onebuilding.org" target="_blank">Ibpsausa@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/ibpsausa-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/ibpsausa-onebuilding.org</a><br></span>
To unsubscribe from this mailing list send a blank message to <a href="mailto:IBPSAUSA-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">IBPSAUSA-UNSUBSCRIBE@ONEBUILDING.ORG</a><br></blockquote></div>
</blockquote></div><br></div>