size=2 face=Arial>You can specify a constant volume system under your "general"
tap. Make sure if you are using chilled water select "Chilled Water
Air Handling Units" under Equipment Type. Then select CAV single zone or
terminal reheat (dependant on your situation) in the Air System
Type. Under the "sizing data" tap you can select "user define",
then specify your supply air and
ventilation CFM's. </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=379144116-16032010><FONT color=#0000ff
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN
class=379144116-16032010>In order to determine cost for heating and cooling
water you will need to construct a building to be simulated. Thus you will
need to create a chiller and boiler plant and specify all pump
requirements. Then implement these into your building.
</SPAN></FONT></DIV>
<DIV><FONT color=#0000ff size=2 face=Arial></FONT> </DIV>
<DIV><SPAN class=379144116-16032010></SPAN><SPAN class=379144116-16032010><FONT
color=#0000ff size=2 face=Arial></FONT></SPAN> </DIV>
<DIV><SPAN class=379144116-16032010><FONT color=#0000ff size=2
face=Arial>Brendan</FONT></SPAN></DIV>
<DIV><BR></DIV>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> hap-users-bounces@lists.onebuilding.org
[mailto:hap-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Kimball,
Matthew<BR><B>Sent:</B> Tuesday, March 16, 2010 9:12 AM<BR><B>To:</B>
hap-users@lists.onebuilding.org<BR><B>Subject:</B> [Hap-users] Constant Air
Flow<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT size=2 face=Arial><SPAN class=527570416-16032010>Is there a way to
force HAP to supply a constant air flow through a "system" (this includes
specifying return air and outside air requirements) and calculate the
cost of providing the cooling and heating water to the "system" and "zone"
reheats? Any explanations would be helpful.</SPAN></FONT></DIV>
<DIV><FONT size=2 face=Arial><SPAN
class=527570416-16032010></SPAN></FONT> </DIV>
<DIV><FONT size=2 face=Arial><SPAN
class=527570416-16032010>Thanks,</SPAN></FONT></DIV>
<DIV> </DIV>
<DIV align=left><FONT size=1 face=Arial><STRONG><IMG
style="WIDTH: 158px; HEIGHT: 24px" border=0 hspace=0 alt="" align=baseline
src="cid:379144116@16032010-2CA3" width=296 height=29></STRONG></FONT></DIV>
<DIV align=left><FONT size=1 face=Arial><STRONG></STRONG></FONT> </DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>Matthew
Kimball</EM></STRONG></FONT></DIV>
<DIV align=left><STRONG><EM><FONT size=2 face=Arial>**LEED Green
Associate</FONT></EM></STRONG></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>Piping Designer
II</EM></STRONG></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>Jacobs Engineering
Raleigh</EM></STRONG></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>110 Corning Rd. Suite
2500</EM></STRONG></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>Cary, NC
27518</EM></STRONG></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>919-859-5019
office</EM></STRONG></FONT></DIV>
<DIV align=left><FONT size=2 face=Arial><STRONG><EM>574-265-3193
cell</EM></STRONG></FONT></DIV>
<DIV align=left><STRONG><FONT size=2 face=Arial><EM>919-859-5151
fax</EM></FONT></STRONG></DIV>
<DIV> </DIV>
<DIV> </DIV><BR>NOTICE - This communication may contain confidential and
privileged information that is for the sole use of the intended recipient. Any
viewing, copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in error,
please notify us immediately by replying to the message and deleting it from
your computer. </BODY></HTML>