Hello Paula,
I've tried to respond to your questions below:
Point 3: If outdoor air is provided through the VRF fan coils then you will
need to have the fans operate continuously (fan on).  If you have a separate
system to provide outdoor air then you can have the VRF fan coils cycle.
Point 4: It is difficult to help you respond to this without knowing more
about the building, your climate and the energy model.  VRF systems are very
efficient in providing heating in mild climates - you can refer to the COP
in your outdoor ambient temperature range.  If you have a heat recovery type
VRF, the recovered heat can also contribute to significant savings.
Regards,
Aaron
Aaron Smith, P.Eng
Principal, Mechanical Engineer
LEEDR AP BD+C, BEMP, BEAP, CGD
M&R Engineering Ltd.
Date: Wed, 7 Dec 2022 08:22:36 -0300
From: Paula A Hern?ndez <paulahernandez4 at fibertel.com.ar>
To: <hap-users at lists.onebuilding.org>
Subject: [Hap-users] VRF Controls
Message-ID: <00a001d90a2e$35b09a80$a111cf80$@fibertel.com.ar>
Content-Type: text/plain; charset="iso-8859-1"
Hello,
 
I am modeling a building with VRF systems.
 
The reviewer has made the following comments.
 
Point 3: If I chance the fan control to ?Fan On?, the energy savings falls
to 14%, which is not good.
How may I justify the fan control steel ?Fan Cycled? and that outdoor air is
delivered wheb the spaces area occupied?
 
Point 4: would you please help me to justify this amount of savings for
space heating.
 
Thank you,
 
 
 
 
 
Ingeniera Paula Andrea Hern?ndez LEED  AP (BD +C) / Edge Expert & Auditor
Capitulo Argentino de ASHRAE 
 
Estudio Ingeniero Mario Pedro Hern?ndez
Cel: 11 1559221377 (+54 9 1159221377)
Tel./Fax: 4302-9561 Tel.: 4303-3481
Av. Montes de Oca 1103 5? D - C.A.B.A.
Web Site:  <http://www.mphingenieria.com.ar/> www.mphingenieria.com.ar
e-mail:  <mailto:mphingenieria at fibertel.com.ar>
paulahernandez4 at fibertel.com.ar
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachment
s/20221207/302b598a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 267026 bytes
Desc: not available
URL:
<http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachment
s/20221207/302b598a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3723 bytes
Desc: not available
URL:
<http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachment
s/20221207/302b598a/attachment.jpg>
------------------------------
Subject: Digest Footer
_______________________________________________
Hap-users mailing list
Hap-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/hap-users-onebuilding.org
------------------------------
End of Hap-users Digest, Vol 86, Issue 1
****************************************
    
    
More information about the Hap-users
mailing list