What are your inputs for the floor conditions? Does the unconditioned space have any heat generating equipment? I would check your unconditioned max and minimum temperatures to make sure they are in line with what you might expect.
Thank You,
Matthew J. Baron, PE
[cid:image003.jpg at 01D35EB8.AAA57580]
Wendel, Centerpointe Corporate Park, 375 Essjay Road, Suite 200, Williamsville, NY 14221
p. 716.688.0766 tf. 877.293.6335 e. mbaron at wendelcompanies.com<mailto:mbaron at wendelcompanies.com> w. wendelcompanies.com<http://www.wendelcompanies.com/>
architecture | engineering | planning | energy efficiency | construction management
CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Any distribution, copying or disclosure of this email is strictly prohibited.
From: Hap-users [mailto:hap-users-bounces at lists.onebuilding.org] On Behalf Of ARUNSHANKAR via Hap-users
Sent: Thursday, November 16, 2017 2:27 AM
To: hap-users at lists.onebuilding.org
Subject: Re: [Hap-users] HAP - Energy simulation
Hi Hap Users,
I have been modelling the two identical spaces with the following options.
Option 1: Roof - Exposed, Floor - Above conditioned space
Option 2: Roof - Exposed, Floor - Above Unconditioned space
But I face the dramatical issue in HAP. That the point is below,
1. The Peak design result that is total coil load from the HAP Option 2 is higher than the Option 1. I agreed.
1. But I have noticed the total coil load Hourly simulation & Monthly simulation from HAP Option 2 is lower than the Option 1 at all month except peak month (May & June). The peak month also not huge difference between the Option 2 & Option 1.
The above queries I made the assumption the HAP simulation will not considered the Option 1 Floor above A/C space design condition. I think so that is take the outdoor weather condition. In this case how to model the Floor - Above conditioned space.
I have the lot confusion to conclude the above queries. Any one please gives me the clear picture.
Thanks & Regards,
Arun shankar
Cell: 91-9600034602
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20171116/a367ea89/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2262 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20171116/a367ea89/attachment.jpg>
More information about the Hap-users
mailing list