[Hap-users] DX with Natural Ventilation
Khaled Fouda
KFouda at nrg-concepts.com
Wed Mar 16 09:08:33 PDT 2016
Hi Hap Users,
I am filing a project for LEED Certification. It is a Residential Building where the Baseline Model uses PTAC with Mechanical Ventilation and the Proposed Design uses DX with Natural Ventilation (Trickle Vents).
This is how I am modeling the two buildings and I would like to see what the experts out there think.
Baseline Model:
- Space Inputs:
o OA Ventilation: (Dwelling Units - ASHRAE 62.1)
o Infiltration: (Only when fan is off - Using Manual J Table 5B values for the ACH)
- System Input:
o Fan Control: (Fan On)
o Zone Sizing Ventilation (Computer Generated - auto calculated from the space inputs as ASHRAE 62.1)
- Design Load Summary Results:
o Since the infiltration happens when the fan is OFF, but it is set to be ON 24/7 then my infiltration value is ZERO.
o Ventilation is calculated to be 6000CFM for the whole residential portion of the building.
Proposed Model:
- Space Inputs:
o OA Ventilation: (Dwelling Units - ASHRAE 62.1), this is technically useless and these values will not be used anywhere.
o Infiltration: (All Hours - Pluged in the ASHRAE 62.1 manually calculated values)
- System Input:
o Fan Control: (Fan Cycled)
o Zone Sizing Ventilation (User Defined - Pluged in Zero value because no mechanical ventilation exist at the terminal units)
- Design Load Summary Results:
o Since the infiltration happens All Hours, I get an output cooling load for the infiltration.
o Ventilation is calculated to be ZERO because it was pluged in as Zero under the Zone Sizing Ventilation.
I am satisfied with this way of designing the two buildings but I need to show the LEED Reviewer that Mechanical Ventilation in the Baseline Building is equal to the Natural Ventilation (infiltration in this case). I couldn't find a way to generate a hap report that shows the infiltration air flow in CFM! Any help with that would be appreciated.
Best Regards,
Khaled Fouda, LEED GA
Integrated Energy Concepts Engineering, P.C.
Rochester Office:
3445 Winton Place, Suite 240
Rochester, New York 14623
Phone: 585-272-4650 ext.29
Toll Free: 866-666-4626
eFax: 718-228-5154
kfouda at nrg-concepts.com<mailto:kfouda at nrg-concepts.com>
[linked in]<https://www.linkedin.com/company/integrated-energy-concepts-engineering-pc?trk=nav_account_sub_nav_company_admin>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20160316/ff9d4821/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1295 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20160316/ff9d4821/attachment.gif>
More information about the Hap-users
mailing list