Hi,

 

You can size systems based on ACH when you describe your system.  Go to the
"Zone Components" tab then down to "Terminal Units".  If each zone requires
a different ACH, uncheck the box that says "All zones are the same".  Beside
Minimum Airflow you'll see a dropdown menu, the default it "cfm/person",
change that to "ACH" and you can enter your required ACH for that zone. You
can then use the arrows move onto each zone and adjust as required.

 

Aaron

 



 

 

Aaron Smith, P.Eng 

M&R Engineering 

-----Original Message-----
Date: Tue, 25 Nov 2014 20:33:27 +0200

From: ahmed zahran <az_zahran at hotmail.com>

To: "hap-users at lists.onebuilding.org"

      <hap-users at lists.onebuilding.org>

Subject: [Hap-users] ACH

Message-ID: <DUB127-W69DACE857E820BE0F65FD685730 at phx.gbl>

Content-Type: text/plain; charset="windows-1256"

 

Dear ,All.HOW TO ADDED THE ACH FOR SPACE (HOSPITAL  SURGERY OPERATION ROOM)
ACH IS 25 TIME.THANKS                                 