[Hap-users] Constant Air Flow
C. J. Gann
cjg04austin at swbell.net
Thu Mar 18 04:46:46 PDT 2010
Matt,
Am not sure what kind of system you are sizing, CAV reheat or VAV,
however HAP will size the reheat coil to provide reheat of the supply
air at your min setting (2 ACH) which you have set to 55F plus any
additional heat needed to warm the zone to 57F (60-3), which is
heating Tstat - throttling range. The "zone sizing summary" report
will indicate the reheat coil load. Given that you have such low Tstat
setpoint there may be very little zone heat required. Hope this helps.
BTW, you should just call Carrier software support with questions as
this is free provided you have a license. 800-253-1794.
-Craig
Sent from my iPhone
On Mar 17, 2010, at 10:09 PM, "Kimball, Matthew" <Matthew.Kimball at jacobs.com
> wrote:
> I am not looking for HAP to size, I just want to know the btu output
> from the coils. It gave me preheat coil btu's and cooling coil
> btu's, but not reheat btu's.
> -----Original Message-----
> From: C. J. Gann [mailto:cjg04austin at swbell.net]
> Sent: Wed 3/17/2010 6:26 PM
> To: Kimball, Matthew
> Cc: <hap-users at lists.onebuilding.org>
> Subject: Re: [Hap-users] Constant Air Flow
>
> HAP will not size your reheat coil because you specified "user-
> defined" sizing. Use computer sizing and it will size it.
>
> Regards,
>
> Craig J. Gann, P.E.; LEED AP
> www.EnergySimulators.com
>
> Sent from my iPhone
>
> On Mar 17, 2010, at 4:59 PM, "Kimball, Matthew" <Matthew.Kimball at jacobs.com
> > wrote:
>
>> Anyone care to analyze what I am doing below and tell me why I'm
>> not getting a terminal heating coil load when I run a simulation on
>> the system? Thanks, Matt.
>>
>>
>> <Outlook.jpg><Outlook.jpg>
>> <Outlook.jpg><Outlook.jpg>
>> <Outlook.jpg><Outlook.jpg>
>>
>> <Outlook.jpg><Outlook.jpg>
>> <Outlook.jpg>
>> From: Brendan Arnold [mailto:BrendanA at MKE-Inc.com]
>> Sent: Tuesday, March 16, 2010 12:58 PM
>> To: Kimball, Matthew; hap-users at lists.onebuilding.org
>> Subject: RE: [Hap-users] Constant Air Flow
>>
>> You can specify a constant volume system under your "general" tap.
>> Make sure if you are using chilled water select "Chilled Water Air
>> Handling Units" under Equipment Type. Then select CAV single zone
>> or terminal reheat (dependant on your situation) in the Air System
>> Type. Under the "sizing data" tap you can select "user define",
>> then specify your supply air and ventilation CFM's.
>>
>> In order to determine cost for heating and cooling water you will
>> need to construct a building to be simulated. Thus you will need
>> to create a chiller and boiler plant and specify all pump
>> requirements. Then implement these into your building.
>>
>>
>> Brendan
>>
>> From: hap-users-bounces at lists.onebuilding.org [mailto:hap-users-
>> bounces at lists.onebuilding.org] On Behalf Of Kimball, Matthew
>> Sent: Tuesday, March 16, 2010 9:12 AM
>> To: hap-users at lists.onebuilding.org
>> Subject: [Hap-users] Constant Air Flow
>>
>> Is there a way to force HAP to supply a constant air flow through a
>> "system" (this includes specifying return air and outside air
>> requirements) and calculate the cost of providing the cooling and
>> heating water to the "system" and "zone" reheats? Any explanations
>> would be helpful.
>>
>> Thanks,
>>
>> <New Logo.jpg>
>>
>> Matthew Kimball
>> **LEED Green Associate
>> Piping Designer II
>> Jacobs Engineering Raleigh
>> 110 Corning Rd. Suite 2500
>> Cary, NC 27518
>> 919-859-5019 office
>> 574-265-3193 cell
>> 919-859-5151 fax
>>
>>
>>
>> NOTICE - This communication may contain confidential and privileged
>> information that is for the sole use of the intended recipient. Any
>> viewing, copying or distribution of, or reliance on this message by
>> unintended recipients is strictly prohibited. If you have received
>> this message in error, please notify us immediately by replying to
>> the message and deleting it from your computer.
>>
>>
>> NOTICE - This communication may contain confidential and privileged
>> information that is for the sole use of the intended recipient. Any
>> viewing, copying or distribution of, or reliance on this message by
>> unintended recipients is strictly prohibited. If you have received
>> this message in error, please notify us immediately by replying to
>> the message and deleting it from your computer.
>
>> _______________________________________________
>> Hap-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/hap-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to HAP-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received
> this message in error, please notify us immediately by replying to
> the message and deleting it from your computer.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20100318/9e18e46f/attachment-0002.htm>
More information about the Hap-users
mailing list