        <div dir="ltr" data-setdir="false">Thank you every one for the help and for your clarification Brian. What you explained below in your email make sense and very helpful to me.</div><div dir="ltr" data-setdir="false"><br></div><div dir="ltr" data-setdir="false">Regards</div><div dir="ltr" data-setdir="false"><br></div><div dir="ltr" data-setdir="false">Ahmad</div><div><br></div>
        
        </div><div id="ydp5668ea7dyahoo_quoted_0373349536" class="ydp5668ea7dyahoo_quoted">
            <div style="font-family:'Helvetica Neue', Helvetica, Arial, sans-serif;font-size:13px;color:#26282a;">
                
                <div>
                        On Friday 6 June 2025 at 10:55:11 pm AEST, Brian Fountain <brian.fountain@sa-footprint.com> wrote:
                    </div>
                    <div><br></div>
                    <div><br></div>
                
                
                <div><div id="ydp5668ea7dyiv6108996187"><div>
<div class="ydp5668ea7dyiv6108996187WordSection1">
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>Your strategy for showing the impact of cycling fans on and off using the parametric run and the indoor fan mode keyword is appropriate.  There appear to be a few things going on in the model that
 are combining to give the results you are seeing.  To begin with, please note that when the indoor fan mode is set to intermittent, outdoor air for ventilation is only supplied when the fan is running.  The internal gains in the model are relatively high –
 especially the lighting at 2 W/ft² as well as the people load.  The R23 roof is pretty good, minimal glazing.  So, a very large portion of the heating for this model is going to conditioning the outdoor air.  By switching the fans to ‘intermittent’, you are
 removing most of this outdoor air through the heating season and the fans are only being called on for heating beyond what is covered by the internal gains for a relatively small number of hours. 
</span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>  </span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>Other notes – the 70% combustion efficiency on the RTUs seems low to me.</span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>  </span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>I hope this is helpful.
</span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>  </span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>Brian</span></p> 
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span>  </span></p> 
<div id="ydp5668ea7dyiv6108996187yqt83406" class="ydp5668ea7dyiv6108996187yqt0482569114"><div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0cm 0cm 0cm;">
<p class="ydp5668ea7dyiv6108996187MsoNormal"><b><span lang="EN-US">From:</span></b><span lang="EN-US"> Equest-users <equest-users-bounces@lists.onebuilding.org>
<b>On Behalf Of </b>Ahmad Fraij via Equest-users<br clear="none">
<b>Sent:</b> June 5, 2025 6:33 PM<br clear="none">
<b>To:</b> BldgSim Mailing List <bldg-sim@onebuilding.org>; PKConsulting via Equest-users <equest-users@lists.onebuilding.org>; equest-users@onebuilding.org<br clear="none">
<b>Subject:</b> [Equest-users] Parametric Run for Fan Cycling on Demand</span></p> 
</div>
</div>
<p class="ydp5668ea7dyiv6108996187MsoNormal">  </p> 
<div>
<p class="ydp5668ea7dyiv6108996187MsoNormal"><strong><span style="font-family:sans-serif;">CAUTION: This message originated from outside Smith + Andersen</span></strong></p> 
<div align="center" style="text-align:center;" class="ydp5668ea7dyiv6108996187MsoNormal">
<hr align="center" size="2" width="100%">
</div>
</div>
<div>
<div>
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span style="font-size:10.0pt;font-family:sans-serif;">Hello All,</span></p> 
</div>
<div>
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span style="font-size:10.0pt;font-family:sans-serif;">  </span></p> 
</div>
<div>
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span style="font-size:10.0pt;font-family:sans-serif;">I am trying to add a parametric run to make the supply fan cycle based on cooling and heating demands but when I set up the parametric run as per the screenshot below and
 run simulation, all the space heating energy consumption disappear from the report as there is no heating system. So, am I setting up the correct parametric run as below or I am missing something? I have also attached the Equest files for this project if anyone
 can help please. Thank you</span></p> 
</div>
<div>
<p class="ydp5668ea7dyiv6108996187MsoNormal"><span style="font-size:10.0pt;font-family:sans-serif;">  </span></p> 
</div>
<div>
<p style="margin-bottom:12.0pt;" class="ydp5668ea7dyiv6108996187MsoNormal"><span style="font-size:10.0pt;font-family:sans-serif;"><img id="ydp5668ea7dyiv6108996187_x0000_i1026" style="width: 100%; max-width: 800px;" src="cid:3AlQi9dtfuc4IYWaw8tm" alt="Inline image" data-inlineimagemanipulating="true"></span></p> 
</div>
</div></div>
</div>
</div></div></div>
            </div>
        </div></body></html>