<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=us-ascii">
<meta name="Generator" content="Microsoft Word 15 (filtered medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Aptos;}
@font-face
{font-family:remialcxesans;
panose-1:0 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:zone-1;
panose-1:0 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:zones-AQ;
panose-1:0 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:template-4F-DxhvKEfCLPQAiSCarSw;
panose-1:0 0 0 0 0 0 0 0 0 0;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
font-size:11.0pt;
font-family:"Aptos",sans-serif;
mso-ligatures:standardcontextual;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Aptos",sans-serif;
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:11.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang="EN-US" link="#467886" vlink="#96607D" style="word-wrap:break-word">
<div class="WordSection1">
<p class="MsoNormal">Hoping someone can untangle my confusion.<o:p></o:p></p>
<p class="MsoNormal">Have an eQuest model where the PVVT systems will not increase the heating airflow up above the minimum flow ratio causing significant unmet hours (1,000s). This occurs with both auto-sized and hard sized airflows & capacities, so its not
a capacity issue. If the min-flow-ratio is set to 30% (as per design) and reverse acting t-stat the heating airflow does not increase. I can ‘force’ the heating airflow increase by specifying the heating-min-flow ratio, but that’s not really the design. Checking
with wizard, the default min-flow-ratio is 0.67. <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I can’t see or think of anything that would prevent the system from increasing its airflow and heating output to increase to meet the load. Hourly report for the ‘amount of heating needed to hold setpoint’ show the need heating capacity
is less than the system capacity and that the model recognizes there is a heating need – but will not allow airflow & heating output to increase.<o:p></o:p></p>
<p class="MsoNormal">Initially thought this was a custom schedule or other ‘junk’ in the model, but this is occurring even with a dummy wizard model. The PVVT system(s) wont increase airflows from the min-flow-ratio in heating even with reverse acting t-stats.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">What could be causing the model to not increase airflow in heating when the capacities are sufficient?<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks,<o:p></o:p></p>
<div>
<div>
<div>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" width="100%" style="width:100.0%;border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:6.0pt 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.5pt;font-family:"Arial",sans-serif;color:#000001">DARIC ADAIR<o:p></o:p></span></b></p>
</td>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001"> <o:p></o:p></span></p>
</td>
<td valign="bottom" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="bottom" style="padding:0in .75pt .75pt 0in">
<p class="MsoNormal"><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#000001">PE, BEMP, CEM<o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001">Energy Modeling Technical Manager<o:p></o:p></span></p>
</td>
</tr>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001">Strategic Consulting Sector<o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
<tr>
<td valign="top" style="padding:11.25pt 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001">Henderson Companies | <o:p></o:p></span></b></p>
</td>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><b><u><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001"><a href="https://www.hendersonengineers.com/employee-owned/?utm_source=Signature&utm_medium=Email&utm_campaign=Short_Engineers" target="_blank"><span style="color:#000001">Employee Owned</span></a></span></u></b><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001"><o:p></o:p></span></b></p>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#000001">TEL <a href="tel:(913)%20742-5530" target="_blank"><span style="color:#000001;font-weight:normal;text-decoration:none">(913) 742-5530</span></a><o:p></o:p></span></b></p>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
<tr>
<td valign="top" style="padding:7.5pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#000001">LICENSED IN</span></b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#000001"> KS<o:p></o:p></span></p>
</td>
</tr>
<tr>
<td valign="top" style="padding:7.5pt 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:1.0pt"><o:p> </o:p></span></p>
</td>
</tr>
<tr>
<td valign="top" style="padding:7.5pt 0in 0in 0in">
<p class="MsoNormal"><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#000001"><o:p> </o:p></span></p>
</td>
</tr>
<tr>
<td valign="top" style="padding:11.25pt 0in 0in 0in"></td>
</tr>
</tbody>
</table>
</td>
</tr>
</tbody>
</table>
</td>
</tr>
</tbody>
</table>
</div>
</div>
<p class="MsoNormal"><span style="font-size:1.0pt;font-family:"remialcxesans",serif"> </span><span style="font-size:1.0pt;font-family:"template-4F-DxhvKEfCLPQAiSCarSw",serif"> </span><span style="font-size:1.0pt;font-family:"zone-1",serif"> </span><span style="font-size:1.0pt;font-family:"zones-AQ",serif"> </span><o:p></o:p></p>
</div>
</div>
<p style="display:none;visibility:hidden;font-size:8px">AT:2|</p>
<br>
<hr>
<font face="Arial" color="Gray" size="1"><br>
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect
those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing,
or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator@hendersonengineers.com.<br>
</font>
</body>
</html>