<html><head><meta http-equiv="Content-Type" content="text/html; charset=UTF-8"></head><body dir="auto"><div dir="auto">Hello Ethan,</div><div dir="auto"><br></div><div dir="auto">Thanks for your reply</div><div dir="auto"><br></div><div dir="auto">I am trying to change the OA CFM. I created schedules as you suggest below but I could not find the OA CFM fora each zone after I apply these schedules and the OA CFM in the report SV-A did not change.</div><div dir="auto"><br></div><div dir="auto">Do you know where can I find the OA CFM after I apply the new miniminum outside air schedule?</div><div dir="auto"><br></div><div dir="auto">Thanks for the help again</div><div dir="auto"><br></div><div dir="auto">Regards</div><div dir="auto"><br></div><div dir="auto">Ahmad</div><div dir="auto"><br></div><div dir="auto"><br></div><div dir="auto"><br></div><div id="composer_signature" dir="auto"><div style="font-size:12px;color:#575757" dir="auto"><br></div></div><div dir="auto"><br></div><div><br></div><div align="left" dir="auto" style="font-size:100%;color:#000000"><div>-------- Original message --------</div><div>From: "Seaman, Ethan" <eseaman@smma.com> </div><div>Date: 29/9/23  9:36 pm  (GMT+10:00) </div><div>To: Ahmad Fraij <fraij@yahoo.com>, equest-users@onebuilding.org </div><div>Subject: RE: [Equest-users] Changing Ventilation Rate for some months in the year </div><div><br></div></div>
<div class="WordSection1">
<p class="MsoNormal">Ahmad,<br>
<br>
Are you trying to vary the system CFM or OA CFM?  See below for eQuest’s definition of Minimum OA Sch.  The minimum OA schedule varies the hourly OA ratio.  To create an annual schedule to vary the CFM seasonally you can create an additional set of weekly/daily
 schedules, and then set the run times in the annual schedule.<br>
<br>
<img src="cid:com_samsung_android_email_attachmentprovider_1_4126_RAW_1695989632756" id="Picture_x0020_1" style="width:13.25in;height:2.7187in" height="261" width="1272" onmouseover="imageMousePointerUpdate(true)" onmouseout="imageMousePointerUpdate(false)" name="com_samsung_android_email_attachmentprovider_1_4126_RAW_1695989632756"></p>
<p class="MsoNormal"> </p>
<div>
<p style="margin-bottom:12.0pt;line-height:13.5pt;mso-line-height-rule:exactly" class="MsoNormal">
<b><span style="font-size:9.0pt;font-family:"Minion Pro",serif;color:#11B4E8;letter-spacing:.25pt">_______________________________________________</span></b><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;letter-spacing:.25pt"><br>
<span style="color:black">Ethan Seaman</span></span></b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black;letter-spacing:.25pt"><br>
Sustainable Design Analyst</span><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#1F497D;letter-spacing:.25pt"></span></b></p>
<p style="margin-bottom:12.0pt;line-height:13.5pt;mso-line-height-rule:exactly" class="MsoNormal">
<b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black;letter-spacing:.75pt">SMMA</span></b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black;letter-spacing:.25pt">
<br>
t: </span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">617.520.9288</span><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#1F497D;letter-spacing:.25pt"></span></b></p>
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">www.smma.com</span></p>
</div>
<p class="MsoNormal"> </p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users <equest-users-bounces@lists.onebuilding.org>
<b>On Behalf Of </b>Ahmad Fraij via Equest-users<br>
<b>Sent:</b> Friday, September 29, 2023 6:16 AM<br>
<b>To:</b> equest-users@onebuilding.org<br>
<b>Subject:</b> Re: [Equest-users] Changing Ventilation Rate for some months in the year</p>
</div>
</div>
<p class="MsoNormal"> </p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">Hello Guys,</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">Did  anyone have a chance to review my question in my email below?</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">I found the option to add "Minimum OA Schedule" but this schedule is fraction of what? Is it fraction of the CFM/person values that we enter in the Zones? I have added this
 schedule and changed the fractions and the energy consumption and the heating loads have been changed but the OA air flow rate & ratio in the report SV-A has not changed? Am I missing something? </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">If the "Minimum OA Schedule" changes the OA flow rate, then where can I find this value? I am trying to change the OA flow rate for a specific value for only three months
 per year for pandemic mitigation so how can I do that?</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">Any help will be highly appreciated</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">Regards</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif">Ahmad</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif"> </span></p>
</div>
</div>
<div id="ydpbceddb9eyahoo_quoted_6575083606">
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">On Thursday, 28 September 2023 at 04:29:56 pm AEST, Ahmad Fraij <fraij@yahoo.com> wrote:
</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<div id="ydpbceddb9eyiv8717301262">
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Hello Guys,</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">How can I change the ventilation rate for a building in eQUEST software for only three months of the year (Dec, Jam & Feb)?</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Your help will be highly appreciated.</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Regards</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Ahmad</span></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>


</body></html>