Hello Ahmad:</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
When considering air-source heat pumps you also need to carefully in cold climates to watch for large peak heating demand since the heat pump simulation in PSZ will switch-over to electric resistance heating as temperatures below apx. 30F. This results in a
 large jump in electric demand as the unit cannot maintain space temperatures at outdoor temperatures below 30F. </div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
This was one of the reasons for the large, unexpected load on the grid during the winter storm a few years back because of the large number of Texas residences with air to air heat pumps.  </div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Avoiding this is possible with a ground heat exchanger for the heat pump (if this is possible on the site). </div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Also, several manufacturers are solving this with new technologies that allow the heat pump to continue to provide heat in cold climate conditions. However, defining these new HP systems in DOE-2, Equest or EP+ requires some work with adjusting the equipment
 parameters.</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Jeff</div>
<div class="elementToProof" style="font-family: Calibri, Arial, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof">
<div id="Signature">
<div>
<div name="divtagdefaultwrapper" style="margin:0px; font-family:Calibri,Arial,Helvetica,sans-serif">
</div>
<div name="divtagdefaultwrapper" style="margin:0px; font-family:Calibri,Arial,Helvetica,sans-serif">
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE, FIBPSA               <i>We are like fluttering leaves on the branches of trees</i></p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
Liz & Nelson Mitchell Professor in Residential Design           <i>in the forest of the landscape that surrounds us.</i></p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
Department of Architecture                                                       <i>If we could, for just a moment, flutter together,</i> </p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
Texas A&M University                                                                 
<i>we could lift the earth up to be a better place.  JSH</i> 2022</p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
College Station, TX 77845-3581                                                 </p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
<span style="font-family:Calibri,Arial,Helvetica,sans-serif">Office: 979-845-6507, Lab: 979-845-6065</span></p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
Fax 979-862-2457</p>
<p style="margin-top: 0px; margin-bottom: 0px;margin-top:0px; margin-bottom:0px">
<a href="mailto:jhaberl@tamu.edu,www.esl.tamu.edu" tabindex="0" id="OWA32320006-11d5-82ca-1ab6-988b759f318a" class="OWAAutoLink">jhaberl@tamu.edu,www.esl.tamu.edu</a></p>
</div>
</div>
</div>
</div>
<div id="appendonsend"></div>
<hr tabindex="-1" style="display:inline-block; width:98%">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size: 11pt; color: rgb(0, 0, 0);"><b>From:</b> Equest-users <equest-users-bounces@lists.onebuilding.org> on behalf of Brian Fountain via Equest-users <equest-users@lists.onebuilding.org><br>
<b>Sent:</b> Monday, September 4, 2023 5:55 AM<br>
<b>To:</b> Ahmad Fraij <fraij@yahoo.com><br>
<b>Cc:</b> equest-users@onebuilding.org <equest-users@onebuilding.org><br>
<b>Subject:</b> Re: [Equest-users] Modeling HVAC system with heat recovery</font>
<div> </div>
</div>
<div>
<div style="visibility: hidden; font-size: 1px; line-height: 1px; height: 0px; max-height: 0px; opacity: 0; overflow: hidden; display: none !important; color: rgb(255, 255, 255);">
You have a couple of options regarding system type. There is a HP heat pump system type that is zonal meaning you would not need a system per zone.    However it has some keyword limitations including no ventilation heat recovery.    So to work
</div>
<div style="visibility: hidden; font-size: 1px; line-height: 1px; height: 0px; max-height: 0px; opacity: 0; overflow: hidden; display: none !important; color: rgb(255, 255, 255);">
ZjQcmQRYFpfptBannerStart</div>
<div dir="ltr" id="x_pfptBanneroiucj6i" style="visibility: visible !important; opacity: 1 !important; max-width: none !important; max-height: none !important; display: block !important; text-align: left !important; margin: 16px 0px !important; padding: 8px 16px !important; border-radius: 4px !important; min-width: 200px !important; border-top: 4px solid rgb(144, 164, 174) !important; background-color: rgb(208, 216, 220);">
<div id="x_pfptBanneroiucj6i" style="visibility: visible !important; opacity: 1 !important; max-height: none !important; float: left !important; display: block !important; margin: 0px 0px 1px !important; max-width: 600px !important; background-color: rgb(208, 216, 220);">
<div id="x_pfptBanneroiucj6i" style="opacity: 1 !important; max-width: none !important; max-height: none !important; display: block !important; visibility: visible !important; font-family: Arial, sans-serif !important; font-weight: bold !important; font-size: 14px !important; line-height: 18px !important; color: rgb(0, 0, 0); background-color: rgb(208, 216, 220);">
This Message Is From an External Sender </div>
<div id="x_pfptBanneroiucj6i" style="font-weight: normal; opacity: 1 !important; max-width: none !important; max-height: none !important; display: block !important; visibility: visible !important; font-family: Arial, sans-serif !important; font-size: 12px !important; line-height: 18px !important; margin-top: 2px !important; color: rgb(0, 0, 0); background-color: rgb(208, 216, 220);">
This message came from outside your organization. </div>
</div>
<div style="clear:both!important; display:block!important; visibility:hidden!important; line-height:0!important; font-size:0.01px!important; height:0px">
 </div>
</div>
<div style="visibility: hidden; font-size: 1px; line-height: 1px; height: 0px; max-height: 0px; opacity: 0; overflow: hidden; display: none !important; color: rgb(255, 255, 255);">
ZjQcmQRYFpfptBannerEnd</div>
<div dir="auto">You have a couple of options regarding system type. There is a HP heat pump system type that is zonal meaning you would not need a system per zone.   However it has some keyword limitations including no ventilation heat recovery.   So to work
 around model heat recovery you will scale back the OA volume by the heat recovery effectiveness.   ( Not terrific. )<br>
<br>
</div>
<div dir="auto">I recommend creating a system per zone and using the PVVT system type. PSZ would also work.  PVVT enables a few more keywords.   Both allow ventilation heat recovery to be directly modelled.<br>
<br>
</div>
<div dir="auto">Whichever system you choose, set your heating to Heat Pump.   The keywords on the heating-supplementary tab will be enabled where you can add the OAT below which your electric resistance heating is enabled (default 40F) and the OAT below which
 the heat pump doesn't run. <br>
</div>
<div class="x_gmail_quote">On Sep 4, 2023, at 12:38 AM, fraij via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" id="OWA85a1147c-1a9e-0aeb-d94b-5c594c3261e2" class="OWAAutoLink">equest-users@lists.onebuilding.org</a>> wrote:
<blockquote class="x_gmail_quote" style="margin:0pt 0pt 0pt 0.8ex; border-left:1px solid rgb(204,204,204); padding-left:1ex">
<div dir="auto">Hello,</div>
<div dir="auto"><br>
</div>
<div dir="auto">I have a model in eQUEST that has FCU as the HVAC system with heat pump chiller for a residential building. </div>
<div dir="auto"><br>
</div>
<div dir="auto">Now I need to change this HVAC system to DX heat pump and this heat pump is small and self contained in which it can be installed inside the room and will have inlet and out let ducts for the condenser air to the outside (I.e. without outdoor
 unit). This unit will have also heat recovery option and supplementary electric resistance heater.</div>
<div dir="auto"><br>
</div>
<div dir="auto">My question is, what is the best HVAC system in eQUEST that I can use for this heat pump and in the same time enable the heat recovery option tab and the supplementary heater option tab? And also, do I need to assign a new HVAC system for each
 zone or I can assign one HVAC system for a group of zones similar to the FCU system?</div>
<div dir="auto"><br>
</div>
<div dir="auto">Thank you very much for the help.</div>
<div dir="auto"><br>
</div>
<div dir="auto">Regards</div>
<div dir="auto"><br>
</div>
<div dir="auto">Ahmad</div>
<div dir="auto"><br>
</div>
<div dir="auto"><br>
</div>
<div dir="auto"><br>
</div>
<pre class="x_blue"><hr><br>Equest-users mailing list<br><a href="https://urldefense.com/v3/__http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org__;!!KwNVnqRv!EiakQNtQC5AZsJvXTPyN55u_vD41_hLocGUlxtGE0aZ1glHRyWkZvSsjNzo7FR3olWrwh315sM-2dAOGb6wYm1S8VV6Ko4vP$" data-auth="NotApplicable" id="OWA278065e4-e2ee-4f6f-c4d1-ee6f136e1b9a" class="OWAAutoLink">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br></pre>