  </head><body style="zoom: 0%;"><div dir="auto">Omer<br><br></div>
<div dir="auto">It seems to me that a loop-to-loop heat pump would better represent the system you are describing.   It can feed hot water and chilled water loops rather than requiring a 2-pipe loop to dictate whether it is in heating or cooling mode.   Further,  it can respond to the higher of the heating or cooling loop loads.<br><br></div>
<div dir="auto">Brian</div>
<div class="gmail_quote" >On Jan 22, 2023, at 9:58 AM, Omer Moltay via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">

  
    <p>Dear All,</p>
    <p>I am using two different 2 pipe loops for both HW and CHW
      produced by a ground coupled heat pump. Each of these loops is
      only in heating or cooling mode throughout the year. This is
      necessary as eQuest requires a 2 pipe loop for modeling a chiller
      heat pump (although the CHW 2 pipe loop might also have been a
      cooling loop - but the result does not change).</p>
    <p>Attached is a simple model that features what I have just
      described. The simulation run always gives the error that there is
      zero design flow in the loops, whatever I try (I have tried using
      secondary loops as well but did not work).</p>
    <p>It would help me a lot if anyone could point out what could be
      wrong with this set-up?</p>
    <p>Best,</p>
    <p>Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP <br>
      Mimta EcoYapi, LEED Proven Provider <br>
      Hekimsuyu Cad. 559. Sk. <br>
      No:39 34255 Kucukkoy Istanbul Turkey <br>
      Tel: 90-212-617-2296 <br>
      Fax: 90-212-617-2297 <br>
      Mobile: 90-533-957-1394 <br>
      <a href="http://www.eco-yapi.com" target="_blank">www.eco-yapi.com</a>
    </p>
    <img id="Picture_x0020_1" src="cid:part1.d63W4iV3.cR42gVL1@mimtarch.com" class="" width="300" height="120" border="0">
    <p></p>
  
<pre class="blue"><hr><br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br></pre></blockquote></div></body></html>