<div dir="ltr" data-setdir="false">Thanks, Ahmed. But I need guidance as to where in the Detail Edit to put these items. I cannot unmask the inputs.</div><div dir="ltr" data-setdir="false"><br></div><div dir="ltr" data-setdir="false">john</div><div><br></div>
</div><div id="yahoo_quoted_9204738056" class="yahoo_quoted">
<div style="font-family:'Helvetica Neue', Helvetica, Arial, sans-serif;font-size:13px;color:#26282a;">
<div>
On Sunday, July 24, 2022 at 01:54:10 AM PDT, Ahmad Fraij <fraij@yahoo.com> wrote:
</div>
<div><br></div>
<div><br></div>
<div><div id="yiv8957633750"><div><div style="font-family:Helvetica Neue, Helvetica, Arial, sans-serif;font-size:13px;" class="yiv8957633750ydp4d9b887fyahoo-style-wrap"><div></div>
<div dir="ltr">Hello John,</div><div dir="ltr"><br clear="none"></div><div dir="ltr">The heat recovery of the DX cooling units come with either partial heat recovery or full heat recovery. Partial heat recovery can provide heating capacity of 20 to 30% of the total capacity of the DX unit using a heat exchanger called the de-superheater. Depending on the DX unit capacity, this 20 to 30% heating energy can be used for reheat coils or for DHW.</div><div dir="ltr"><br clear="none"></div><div dir="ltr">The full heat recovery can recover all the condenser heat of the DX unit and use it for different purposes. The new 4-Pipe heat recovery chillers in the market these days can do full heat recovery and can provide simultaneous cooling and heating to the building and not only for reheat coils and DHW.</div><div dir="ltr"><br clear="none"></div><div dir="ltr">I hope the above will help.</div><div dir="ltr"><br clear="none"></div><div dir="ltr">Regards</div><div dir="ltr"><br clear="none"></div><div dir="ltr">Ahmad</div><div><br clear="none"></div>
</div><div id="yiv8957633750ydp5e5fb928yahoo_quoted_9182786776" class="yiv8957633750ydp5e5fb928yahoo_quoted">
<div style="font-family:'Helvetica Neue', Helvetica, Arial, sans-serif;font-size:13px;color:#26282a;">
<div id="yiv8957633750yqt59253" class="yiv8957633750yqt7786053618"><div>
On Sunday, 24 July 2022 at 03:37:06 am AEST, John Aulbach via Equest-users <equest-users@lists.onebuilding.org> wrote:
</div>
<div><br clear="none"></div>
<div><br clear="none"></div>
<div><div id="yiv8957633750ydp5e5fb928yiv9342070084"><div><div style="font-family:verdana, helvetica, sans-serif;font-size:16px;" class="yiv8957633750ydp5e5fb928yiv9342070084yahoo-style-wrap"><div dir="ltr">Does anyone have a simply model example of this process? Can this heat be used for both reheat coils and DHW?</div><div dir="ltr"><br clear="none"></div><div dir="ltr">Thank you in advance.</div><div dir="ltr"><br clear="none"></div><div dir="ltr">John</div></div></div></div>_______________________________________________<br clear="none">Equest-users mailing list<br clear="none"><a rel="nofollow noopener noreferrer" shape="rect" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br clear="none">To unsubscribe from this mailing list send a blank message to <a rel="nofollow noopener noreferrer" shape="rect" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br clear="none"></div></div>
</div>
</div></div></div></div>
</div>
</div></body></html>