<html><head></head><body style="zoom: 0%;"><div dir="auto">You can only have 1 system serving a zone. All but 1 system type (PIU) is either DX or hydronic chilled water. Even with PIU you have to specify the cooling source...it is not a schedule. That is a long "not really".<br><br></div>
<div dir="auto">I think I would model it as hydronic chilled water using Load Management to schedule between the main chiller and a recip small chiller set up to approximate the DX. My wiser colleague would recommend to post-proccess it.<br><br></div>
<div dir="auto">B</div>
<div class="gmail_quote" >On Jul 21, 2022, at 4:23 PM, John Aulbach via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div class="yahoo-style-wrap" style="font-family:verdana, helvetica, sans-serif;font-size:16px;"><div dir="ltr" data-setdir="false">I have been presented a drawing that has a CHW coil AND a DX coil for cooling in the same duct. THE DX coil only operates when the chiller if off.</div><div dir="ltr" data-setdir="false"><br></div><div dir="ltr" data-setdir="false">Can this be modeled in eQuest?</div><div dir="ltr" data-setdir="false"><br></div><div dir="ltr" data-setdir="false">John Aulbach, PE</div></div><pre class="blue"><hr><br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br></pre></blockquote></div></body></html>