<html><head></head><body style="zoom: 0%;"><div dir="auto">This one would likely be easier to troubleshoot if you could provide the .inp file.<br><br></div>
<div dir="auto">How did you set up the controls on the 2-pipe loop to switch between heating and cooling?  Was there an explicit schedule or is it snapping on outdoor temperature?  If the latter there may be hours in the winter above your snap temperature flipping the loop to cooling mode.  An explicit schedule will preclude that.  The 2-pipe loop is either-or so what you describe is unusual. <br><br></div>
<div class="gmail_quote" >On Jul 11, 2022, at 8:15 AM, Konstantina Kalliakoudi via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div dir="ltr"><div dir="ltr">Dear equest users,<div><br></div><div>I have following:</div><div><br></div><div>I have a two pipe system with Boiler or Chiller and terminal units: Fan Coil.</div><div><br></div><div>When I run the file, the results are showing at the winter months,  Cooling and Heating consumption.</div><div><br></div><div>I was expecting to see either Cooling or Heating consumption since it is a two pipe system.</div><div><br></div><div>Do you have any ideas or suggestions?</div><div><br></div><div><br></div><div>Thank you</div><div><br></div><div><p class="MsoNormal" style="margin-bottom:0cm;line-height:normal"><span lang="EN-US" style="font-size:12pt;font-family:"Times New Roman",serif">Konstantina Kalliakoudi<span></span></span></p>
<p class="MsoNormal" style="margin-bottom:0cm;line-height:normal"><span style="font-size:12pt;font-family:"Times New Roman",serif">Μ</span><span lang="EN-US" style="font-size:12pt;font-family:"Times New Roman",serif">echanical
Engineer M.Sc, LEED AP<span></span></span></p>
<p class="MsoNormal" style="margin-bottom:0cm;line-height:normal"><br></p>
<p class="MsoNormal" style="margin-bottom:0cm;line-height:normal"><br></p></div><div><br></div><div><br></div><div><br></div></div></div>
<pre class="blue"><hr><br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br></pre></blockquote></div></body></html>