<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-2022-jp">
<meta name="Generator" content="Microsoft Word 15 (filtered medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
{font-family:Helvetica;
panose-1:2 11 6 4 2 2 2 2 2 4;}
@font-face
{font-family:SimSun;
panose-1:2 1 6 0 3 1 1 1 1 1;}
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:"Yu Gothic";
panose-1:2 11 4 0 0 0 0 0 0 0;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:"MS PGothic";
panose-1:2 11 6 0 7 2 5 8 2 4;}
@font-face
{font-family:"\@Yu Gothic";
panose-1:2 11 4 0 0 0 0 0 0 0;}
@font-face
{font-family:"\@MS PGothic";}
@font-face
{font-family:"\@SimSun";
panose-1:2 1 6 0 3 1 1 1 1 1;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
font-size:12.0pt;
font-family:SimSun;
mso-fareast-language:ZH-CN;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
p.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal, li.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal, div.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal
{mso-style-name:ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:SimSun;
mso-fareast-language:ZH-CN;}
p.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msipfooter17e78546, li.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msipfooter17e78546, div.ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msipfooter17e78546
{mso-style-name:ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msipfooter17e78546;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:SimSun;
mso-fareast-language:ZH-CN;}
span.EmailStyle20
{mso-style-type:personal-reply;
font-family:"Calibri",sans-serif;
color:windowtext;}
p.msipfooter17e78546, li.msipfooter17e78546, div.msipfooter17e78546
{mso-style-name:msipfooter17e78546;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"MS PGothic",sans-serif;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang="EN-US" link="blue" vlink="purple" style="word-wrap:break-word">
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA">Presuming space heating is being delivered/accomplished (unmet hours are under control)$B!D(B<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA">If you move your project to Anchorage, Alaska by reassigning the weather file, does the space cooling end-use jump up in response? If so, I$B!G(Bd wager
all energies consumed by the heatpump chiller are being allocated to / reported under the space cooling end-use.
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA">I$B!G(Bm not entirely sure what$B!G(Bs normal behavior to expect with the current version of eQuest/doe2, so some $B!H(Bkicking of the tires$B!I(B like this is probably
in order unless someone has immediate familiarity to impart.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA">If it is the case it$B!G(Bs all just lumped into one end-use, I anticipate you could reasonably extract/distinguish heating vs. cooling energies by pairing
your hourly chiller energy with your hourly snap temperature conditions. Please advise if you need an example.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA">~Nick<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46;mso-fareast-language:JA"><img width="624" height="8" style="width:6.5in;height:.0833in" id="Picture_x0020_1" src="cid:image001.jpg@01D8144B.BBB16EE0"></span><span style="font-size:10.5pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" width="624" style="width:6.5in;border-collapse:collapse">
<tbody>
<tr style="height:11.25pt">
<td width="303" colspan="4" style="width:227.25pt;padding:0in 0in 0in .05in;height:11.25pt">
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46;mso-fareast-language:JA">Nick Caton, P.E. (US), BEMP<o:p></o:p></span></b></p>
</td>
<td width="321" colspan="3" style="width:240.75pt;padding:0in 0in 0in 0in;height:11.25pt">
<p class="MsoNormal" align="right" style="text-align:right"><b><span lang="JA" style="font-size:11.0pt;font-family:"Yu Gothic",sans-serif;color:#3A7A46;mso-fareast-language:JA">$B%K%C%/(B</span></b><b><span lang="JA" style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46;mso-fareast-language:JA">
</span></b><b><span lang="JA" style="font-size:11.0pt;font-family:"Yu Gothic",sans-serif;color:#3A7A46;mso-fareast-language:JA">$B%1!<%H%s(B</span></b><b><span style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46;mso-fareast-language:JA">, P.E. (US),
BEMP</span></b><span style="font-size:9.0pt;font-family:"Calibri",sans-serif;color:#626469;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:.7in">
<td width="12" valign="top" style="width:9.0pt;padding:0in 0in 0in .05in;height:.7in">
</td>
<td width="216" valign="top" style="width:2.25in;padding:0in 0in 0in 0in;height:.7in">
<p class="MsoNormal" style="line-height:150%"><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA">Senior Energy Engineer</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:JA"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA">Energy Manager, Yokota Airbase
<o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:150%"><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA">ESS - Energy & Sustainability Services</span><span style="font-size:11.0pt;line-height:150%;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
<td width="42" valign="top" style="width:31.5pt;padding:0in 0in 0in .05in;height:.7in">
<p class="MsoNormal" style="line-height:150%"><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069;mso-fareast-language:JA">M JP</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:JA"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069;mso-fareast-language:JA">M US</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:JA"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069;mso-fareast-language:JA">Email</span><span style="font-size:9.0pt;line-height:150%;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:JA">
</span><span style="font-size:11.0pt;line-height:150%;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
<td width="138" colspan="2" valign="top" style="width:103.5pt;padding:0in 0in 0in .05in;height:.7in">
<p class="MsoNormal" style="line-height:150%"><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA">+81 . 070 . 3366 . 3317</span><span style="font-size:11.0pt;line-height:150%;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:150%"><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA">+1 . 785 . 410 . 3317</span><span style="font-size:11.0pt;line-height:150%;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:150%"><span style="font-size:11.0pt;line-height:150%;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><a href="mailto:nicholas.caton@se.com"><span style="font-size:9.0pt;line-height:150%;color:#0563C1">nicholas.caton@se.com</span></a><o:p></o:p></span></p>
</td>
<td width="204" valign="top" style="width:153.0pt;padding:0in 0in 0in .05in;height:.7in">
<p class="MsoNormal" align="right" style="text-align:right"><span lang="JA" style="font-size:9.0pt;font-family:"Yu Gothic",sans-serif;color:#626469;mso-fareast-language:JA">$B%7%K%"%(%M%k%.!<%(%s%8%K%"(B</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA"><br>
</span><span lang="JA" style="font-size:9.0pt;font-family:"Yu Gothic",sans-serif;color:#626469;mso-fareast-language:JA">$B2#ED4pCO%(%M%k%.!<%^%M!<%8%c!<(B</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#626469;mso-fareast-language:JA"><br>
ESS - </span><span lang="JA" style="font-size:9.0pt;font-family:"Yu Gothic",sans-serif;color:#626469;mso-fareast-language:JA">$B%(%J%8!<;}B32DG=@-%5!<%S%9(B</span><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
<td width="12" valign="top" style="width:9.0pt;padding:0in 0in 0in 0in;height:.7in">
<p class="MsoNormal" align="right" style="text-align:right"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
</td>
</tr>
<tr style="height:23.4pt">
<td width="303" colspan="4" style="width:227.25pt;padding:0in 0in 0in .05in;height:23.4pt">
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46;mso-fareast-language:JA"><img border="0" width="162" height="41" style="width:1.6875in;height:.427in" id="image011.png_x0040_01D6B128.239DA330" src="cid:image002.png@01D8144B.BBB16EE0"></span><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
<td width="321" colspan="3" style="width:240.75pt;padding:0in 0in 0in 0in;height:23.4pt">
<p class="MsoNormal" align="right" style="text-align:right"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46;mso-fareast-language:JA"><img border="0" width="240" height="45" style="width:2.5in;height:.4687in" id="image012.png_x0040_01D6B128.239DA330" src="cid:image003.png@01D8144B.BBB16EE0"></span><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
</td>
</tr>
<tr>
<td width="12" style="width:9.0pt;padding:0in 0in 0in 0in"></td>
<td width="216" style="width:2.25in;padding:0in 0in 0in 0in"></td>
<td width="42" style="width:31.5pt;padding:0in 0in 0in 0in"></td>
<td width="33" style="width:24.75pt;padding:0in 0in 0in 0in"></td>
<td width="105" style="width:78.75pt;padding:0in 0in 0in 0in"></td>
<td width="204" style="width:153.0pt;padding:0in 0in 0in 0in"></td>
<td width="12" style="width:9.0pt;padding:0in 0in 0in 0in"></td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"> </span><span style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46;mso-fareast-language:JA"><img border="0" width="624" height="8" style="width:6.5in;height:.0833in" id="image010.jpg_x0040_01D6B128.239DA330" src="cid:image001.jpg@01D8144B.BBB16EE0"></span><span style="font-size:10.5pt;font-family:"Yu Gothic",sans-serif;mso-fareast-language:JA"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-family:"MS PGothic",sans-serif;mso-fareast-language:JA"><o:p> </o:p></span></p>
<p class="msipfooter17e78546" align="center" style="margin:0in;text-align:center">
<span style="font-size:6.0pt;font-family:"Arial",sans-serif;color:#626469">Internal</span><o:p></o:p></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span style="font-size:11.0pt;font-family:"Calibri",sans-serif"> Ahmad Fraij <fraij@yahoo.com>
<br>
<b>Sent:</b> Thursday, January 27, 2022 3:06 PM<br>
<b>To:</b> Phil Jordan <phil.jordan@clearesult.com>; Nicholas CATON <Nicholas.Caton@se.com><br>
<b>Cc:</b> equest-users@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Equest-users] Modeling Under Floor Air Distribution (UFAD) system & Heat Pump Chiller<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p><span style="color:red">[External email: Use caution with links and attachments]</span><o:p></o:p></p>
<div class="MsoNormal" align="center" style="text-align:center">
<hr size="2" width="100%" align="center">
</div>
<div>
<div id="ydpe5ee17byahoo_quoted_3927080463">
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<div id="ydpe5ee17byiv3774800381">
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Hello Nicholas,<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Thanks for your detailed reply.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">I have changed the chilled water loop to 2-pipe loop and changed the chiller type to "Heat Pump" as shown below but when I run the simulation I don't get in
the summary report electric consumption for the space heating. I get only for the space cooling electric consumption. Could you or any body else in this forum help me out? I am stuck with this problem and can't complete my project.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">I have also attached to this email the .pd2 and .inp files<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><img border="0" width="1391" height="487" style="width:14.4895in;height:5.0729in" id="Picture_x0020_2" src="cid:image004.png@01D8144B.BBB16EE0" alt="Inline image"></span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><img border="0" width="1465" height="600" style="width:15.2604in;height:6.25in" id="Picture_x0020_3" src="cid:image005.png@01D8144B.BBB16EE0" alt="Inline image"></span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Regards<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Ahmad <o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
</div>
<div id="ydpe5ee17byiv3774800381yqt64010">
<div id="ydpe5ee17byiv3774800381ydpa0617c8yahoo_quoted_3399823610">
<div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">On Thursday, 27 January 2022, 03:05:40 pm AEDT, Nicholas CATON <<a href="mailto:nicholas.caton@se.com">nicholas.caton@se.com</a>> wrote:
<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
</div>
<div>
<div id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524">
<div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Heatpump chillers with UFAD is the system type of the very first building energy simulation model I was ever tasked
with building. Suffice to say, like most first efforts in life, that was probably the worst model I ever built$B!D(B but I sure learned a lot and the challenges of modeling that system arrangement stuck with me! I haven$B!G(Bt been actively practicing eQuest for a
while, but I think I can offer a leg up in this instance.<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">The EDR guidelines Phil extracted/shared will probably forever stand as a useful and appropriate resource to reference
for bridging/informing approach for energy simulation in DOE2. It specifically addresses UFAD from an general/office occupancy perspective. Today, I draw this distinction only to point out if you are dealing with a
<u>data center</u>, the best approach with modern DOE2.3 may look a little different than typical/office scenarios.<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Also I$B!G(Bd add for context that the EDR guidelines were published chronologically before ASHRAE Standard 62.1 made
some substantial advancements/developments in addressing thermal displacement ventilation. I would treat the specific guidance within that EDR document as a $B!H(Bfoundation$B!I(B to be considered, understood, then tweaked to align with your present-day system designers$B!G(B
considerations, calculations, and decisions around ventilation delivery. By way of example, you can go further than suggested/prescribed by the EDR document to not only re-appropriate thermal loads, but to also create new/dedicated under-ceiling $B!H(Binterstitial$B!I(B
plenum zones (with air walls) to better simulate a situation where you can assert buoyancy effects will be in play (as opposed to perfect mixing). I$B!G(Bve taken those lessons learned and applied to simulations of other spaces without UFAD and deliberate TDV
such as auditoriums, atriums, and ice hockey rinks.<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">That said, you are also asking about heat pump chillers. In DOE2 terms (semantics), if I$B!G(Bm correctly guessing
the real-world equipment is 2-pipe (there$B!G(Bs a hydronic loop delivering either chilled or hot water to a single coil), then in DOE2.3 terms I think you might be happy with a CHILLER of TYPE = HEAT-PUMP and CONDENSER-TYPE = AIR-COOLED. I$B!G(Bd suggest review/reference
at Volume 2: Dictionary > HVAC Components > CHILLER > Air-to-Water Heat-Pump (HEAT-PUMP, AIR-COOLED). Be mindful the number of air-side systems which can attach to a circulation loop of type 2-PIPE are limited and that probably merits separate consideration
against your actual equipment.<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Following is a visual example I slapped together to show what that may look like in the interface if you were
to define post-wizards$B!D(B I$B!G(Bm not certain this sort of chiller arrangement is something the wizards can set up for you however, so you may need to do what I did and create the associated loop/pump/chiller manually (after wizards):<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="margin-left:.5in">
<span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><img border="0" width="1624" height="925" style="width:16.9166in;height:9.6354in" id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524Picture_x0020_6" src="cid:image006.png@01D8144B.BBB16EE0"></span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">I hope some of this is helpful!<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">~Nick<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img border="0" width="624" height="8" style="width:6.5in;height:.0833in" id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524Picture_x0020_1" src="cid:image001.jpg@01D8144B.BBB16EE0"></span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" width="624" style="width:6.5in;border-collapse:collapse">
<tbody>
<tr style="min-height:11.25pt">
<td width="303" colspan="4" style="width:227.25pt;padding:0in 0in 0in .05in;min-height:11.25pt">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><b><span style="font-family:"Arial",sans-serif;color:#3A7A46">Nick Caton, P.E. (US), BEMP</span></b><o:p></o:p></p>
</td>
<td width="321" colspan="3" style="width:240.75pt;padding:0in 0in 0in 0in;min-height:11.25pt">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" align="right" style="text-align:right">
<b><span lang="JA" style="color:#3A7A46;mso-fareast-language:JA">$B%K%C%/(B $B%1!<%H%s(B</span></b><b><span style="font-family:"Arial",sans-serif;color:#3A7A46">, P.E. (US), BEMP</span></b><o:p></o:p></p>
</td>
</tr>
<tr style="min-height:.7in">
<td width="12" valign="top" style="width:9.0pt;padding:0in 0in 0in .05in;min-height:.7in">
</td>
<td width="216" valign="top" style="width:2.25in;padding:0in 0in 0in 0in;min-height:.7in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469">Senior Energy Engineer</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469">Energy Manager, Yokota Airbase
</span><o:p></o:p></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469">ESS - Energy & Sustainability Services</span><o:p></o:p></p>
</td>
<td width="42" valign="top" style="width:31.5pt;padding:0in 0in 0in .05in;min-height:.7in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069">M JP</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069">M US</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#57B069">Email</span><span style="font-size:9.0pt;line-height:150%;color:#1F497D">
</span><o:p></o:p></p>
</td>
<td width="138" colspan="2" valign="top" style="width:103.5pt;padding:0in 0in 0in .05in;min-height:.7in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469">+81 . 070 . 3366 . 3317</span><o:p></o:p></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<span style="font-size:9.0pt;line-height:150%;font-family:"Arial",sans-serif;color:#626469">+1 . 785 . 410 . 3317</span><o:p></o:p></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" style="line-height:150%">
<a href="mailto:nicholas.caton@se.com" target="_blank"><span style="font-size:9.0pt;line-height:150%">nicholas.caton@se.com</span></a><o:p></o:p></p>
</td>
<td width="204" valign="top" style="width:153.0pt;padding:0in 0in 0in .05in;min-height:.7in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" align="right" style="text-align:right">
<span lang="JA" style="font-size:9.0pt;color:#626469;mso-fareast-language:JA">$B%7%K%"%(%M%k%.!<%(%s%8%K%"(B</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#626469"><br>
</span><span lang="JA" style="font-size:9.0pt;color:#626469;mso-fareast-language:JA">$B2#ED4pCO%(%M%k%.!<%^%M!<%8%c!<(B</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#626469"><br>
ESS - </span><span lang="JA" style="font-size:9.0pt;color:#626469;mso-fareast-language:JA">$B%(%J%8!<;}B32DG=@-%5!<%S%9(B</span><o:p></o:p></p>
</td>
<td width="12" valign="top" style="width:9.0pt;padding:0in 0in 0in 0in;min-height:.7in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" align="right" style="text-align:right">
<o:p></o:p></p>
</td>
</tr>
<tr style="min-height:23.4pt">
<td width="303" colspan="4" style="width:227.25pt;padding:0in 0in 0in .05in;min-height:23.4pt">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="color:#3A7A46"><img border="0" width="162" height="41" style="width:1.6875in;height:.427in" id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524image011.png_x0040_01D6B128.239DA330" src="cid:image002.png@01D8144B.BBB16EE0"></span><o:p></o:p></p>
</td>
<td width="321" colspan="3" style="width:240.75pt;padding:0in 0in 0in 0in;min-height:23.4pt">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal" align="right" style="text-align:right">
<span style="color:#3A7A46"><img border="0" width="240" height="45" style="width:2.5in;height:.4687in" id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524image012.png_x0040_01D6B128.239DA330" src="cid:image003.png@01D8144B.BBB16EE0"></span><o:p></o:p></p>
</td>
</tr>
<tr>
<td width="12" style="width:9.0pt;padding:0in 0in 0in 0in"></td>
<td width="216" style="width:2.25in;padding:0in 0in 0in 0in"></td>
<td width="42" style="width:31.5pt;padding:0in 0in 0in 0in"></td>
<td width="33" style="width:24.75pt;padding:0in 0in 0in 0in"></td>
<td width="105" style="width:78.75pt;padding:0in 0in 0in 0in"></td>
<td width="204" style="width:153.0pt;padding:0in 0in 0in 0in"></td>
<td width="12" style="width:9.0pt;padding:0in 0in 0in 0in"></td>
</tr>
</tbody>
</table>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:white"> </span><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img border="0" width="624" height="8" style="width:6.5in;height:.0833in" id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524image010.jpg_x0040_01D6B128.239DA330" src="cid:image001.jpg@01D8144B.BBB16EE0"></span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
</div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msipfooter17e78546" align="center" style="margin:0in;text-align:center">
<span style="font-size:6.0pt;font-family:"Arial",sans-serif;color:#626469">Internal</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<div id="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524yqt56116">
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><b><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">From:</span></b><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> Equest-users
<<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>>
<b>On Behalf Of </b>Phil Jordan via Equest-users<br>
<b>Sent:</b> Thursday, January 27, 2022 2:05 AM<br>
<b>To:</b> Ahmad Fraij <<a href="mailto:fraij@yahoo.com">fraij@yahoo.com</a>>; <a href="mailto:equest-users@lists.onebuilding.org">
equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Modeling Under Floor Air Distribution (UFAD) system & Heat Pump Chiller<o:p></o:p></span></p>
</div>
</div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:red">[External email: Use caution with links and attachments]</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
<div class="MsoNormal" align="center" style="text-align:center"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">
<hr size="2" width="100%" align="center">
</span></div>
<p><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Hi Ahmad,<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">I have some guidance from the now-defunct
<a href="https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.av8rdas.com%2Fenergy-design-resources.html&data=04%7C01%7Cnicholas.caton%40se.com%7Cabfbd65e2dfe47d0469f08d9e15b1db6%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637788604149190094%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0&sdata=9Ep3sPmK1dfPgKPxk4q3Or5GyRIQrMfpm7T%2BlPdvGkQ%3D&reserved=0" target="_blank">
Energy Design Resources</a> that discusses how to model underfloor air distribution in eQUEST (attached – I extracted this from a larger document to reduce the filesize); I believe this guidance is from 2006 but hopefully it still holds.<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Regards,<o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><b><span style="font-size:10.5pt;font-family:"Arial",sans-serif;color:#005E68">Phil Jordan</span></b><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><b><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">From:</span></b><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> Equest-users
<<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>>
<b>On Behalf Of </b>Ahmad Fraij via Equest-users<br>
<b>Sent:</b> Tuesday, January 25, 2022 4:33 PM<br>
<b>To:</b> Fraij via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br>
<b>Subject:</b> [Equest-users] Modeling Under Floor Air Distribution (UFAD) system & Heat Pump Chiller<o:p></o:p></span></p>
</div>
</div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><strong><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:maroon">EXTERNAL email. Please exercise caution. This e-mail is from a sender outside of CLEAResult. Do not click any
links or open any attachments from unknown senders or unexpected email. </span></strong><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:maroon">***************************************************</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">
<o:p></o:p></span></p>
<div>
<div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">Hello Guys,</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">I am modeling a building, which has Under Floor Air Distribution (UFAD) system so, how to model this system in eQUEST
software? I could not find a specific system called UFAD or </span><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Under Floor Air Distribution to select in eQUEST software.</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">Further, the building has air source heat pump chiller that provide cooling in summer and heating in winter so, how
we can model heat pump chiller in eQUEST software? How can we assign the same heat pump chiller for both the chilled water loop and the hot water loop?</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">Your help will be highly appreciated.</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">Regards</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A"> </span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
<div>
<p class="ydpe5ee17byiv3774800381ydpa0617c8yiv3809172524msonormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#26282A">Ahmad</span><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<div id="ydpe5ee17byqt03196">
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">_______________________________________________<br>
Equest-users mailing list<br>
<a href="https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=04%7C01%7Cnicholas.caton%40se.com%7Cabfbd65e2dfe47d0469f08d9e15b1db6%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637788604149190094%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0&sdata=dDYcxQJtiVyPaUMXk0H%2FpwalBhPv8CHKdwgj%2FZI%2BhAI%3D&reserved=0" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></span></p>
</div>
</div>
</div>
</div>
</div>
</div>
</body>
</html>