<div dir="ltr">No, they are exterior walls.  Here's the view on the building.  The front of the building faces south.  Maybe these images will help.<div><br></div><div>↓South View </div><div><div><img src="cid:ii_kem94gx82" alt="image.png" width="562" height="270"><br></div></div><div><div>    </div><div>↓ North view<br></div></div><div><div><div><img src="cid:ii_kem95cle3" alt="image.png" width="562" height="256"><br></div></div></div><div id="m_3722246815959569258m_8025192075319092691crmio-track"><img src="https://apolloenergiesinc.agilecrm.com/open?e=DEldridge@grummanbutkus.com&d=Re:+[Equest-users]+Equest+and+high+rise+floors&fr=mark.stout@apolloenergiesinc.com&s=1599103606642&er=569273929" align="left" width="0" height="0" style="border:0;width:0px;height:0px;opacity:0" alt=""></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Sep 2, 2020 at 8:13 PM David Eldridge <<a href="mailto:DEldridge@grummanbutkus.com" target="_blank">DEldridge@grummanbutkus.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">



<div dir="auto">
Are any of the walls both inside and out? Try drawing an extra zone to separate the sections, or if the walls should be correct as-is go into the text editor and make sure the vertices are exactly a match. <br>
<br>
<div dir="ltr">DSE Mobile
<div>773.490.5038</div>
</div>
<div dir="ltr"><br>
<blockquote type="cite">On Sep 2, 2020, at 8:57 PM, Mark Stout via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<br>
<br>
</blockquote>
</div>
<blockquote type="cite">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">Using DD Wizard I modeled each floor as a separate zone and that helped.   The model correctly renders the footprint of each floor of the building, but still treats exterior walls as interior walls and I can't change them.  I can't do it in the
 wizard or in the spreadsheet.</div>
<div dir="ltr"><br>
</div>
<br>
<div class="gmail_quote">
<div dir="ltr" class="gmail_attr">On Tue, Sep 1, 2020 at 8:37 PM John Aulbach <<a href="mailto:jra_sac@yahoo.com" target="_blank">jra_sac@yahoo.com</a>> wrote:<br>
</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div>
<div style="font-family:verdana,helvetica,sans-serif;font-size:16px">
<div></div>
<div dir="ltr">Mark:</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">Sounds like you used the SD Wizard. Save and Copy to a DD Wizard format (name it different). Then go to 3rd-6th floors and redraw the footprint to match those floors. Make sure your spaces match your footprints.</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">That should take care of BOTH the walls that aren't there and the interior walls to exterior walls. </div>
<div dir="ltr"><br>
</div>
<div dir="ltr">John R Aulbach, PE</div>
<div><br>
</div>
</div>
<div id="gmail-m_3722246815959569258gmail-m_8025192075319092691gmail-m_-5975708458940714997gmail-m_8720218597247984272yahoo_quoted_9455387648">
<div style="font-family:"Helvetica Neue",Helvetica,Arial,sans-serif;font-size:13px;color:rgb(38,40,42)">
<div>On Tuesday, September 1, 2020, 07:36:19 PM PDT, Mark Stout via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:
</div>
<div><br>
</div>
<div><br>
</div>
<div>
<div id="gmail-m_3722246815959569258gmail-m_8025192075319092691gmail-m_-5975708458940714997gmail-m_8720218597247984272yiv6805642628">
<div dir="ltr">Hello,
<div><br>
</div>
<div>I'm modeling a 6 story building from plans.  All floors are equal from the rear.  The first two floors come out 165' and have the same footprint.  But floors 3-6 come out 115'. The 6th floor has a 25'x30' uncovered patio.  I used the custom zoning pattern
 to create the layout of the footprint for each floor.  When I look at the 3D model, I see the outlines of the different footprints for floors 3-6 correctly.  But what should be an exterior wall is showing as an interior adiabatic wall.</div>
<div>
<ol>
<li>How do I get the program to treat these interior walls as an exterior wall? </li><li>How do I get rid of the walls that followed floors 1 and 2 but are non-existing for floors 3-6? </li></ol>
</div>
<div><br>
</div>
<div><br>
</div>
<div>-- <br>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div><span style="font-family:arial,helvetica,sans-serif;font-size:small">Kind Regards,</span><br>
</div>
<div><font face="arial, helvetica, sans-serif" size="2">Mark Stout, President<br>
HERS I & II, BPI BA, MFBA, RESNET HERS</font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Lighting & Mechanical Acceptance Testing </font></div>
<div><span style="font-family:arial,helvetica,sans-serif;color:rgb(0,0,0)">CALGreen Inspector/Plans Examiner</span><br>
</div>
<div><font face="arial, helvetica, sans-serif" size="2"><br>
</font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Apollo Energies, Inc.<br>
888-614-8338 x101 Office<br>
888-614-8338 Fax<br>
916-240-2850 Cell<br>
<a rel="nofollow" href="http://www.apolloenergiesinc.com" target="_blank">www.apolloenergiesinc.com</a><br>
Follow us on <a rel="nofollow" href="http://twitter.com/apolloenergies" target="_blank">
Twitter</a> <a rel="nofollow" href="https://www.linkedin.com/company-beta/2061401/" target="_blank">LinkedIn</a> </font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Subscribe to <a rel="nofollow" href="http://dailydigest.apolloenergiesinc.com" target="_blank">Apollo Energies Daily News</a> </font></div>
<div><font face="arial, helvetica, sans-serif" size="2"><br>
</font></div>
<div><span style="font-size:8pt"><br>
</span></div>
<div><font face="arial, helvetica, sans-serif" size="1">DISCLAIMER:  I am not an attorney nor am I an accountant.  The information and/or opinions expressed by myself or my affiliates should not be considered nor are they intended to provide legal or financial
 advice to any individual or entity.  The information contained in this email is for general information purposes only.  Any reliance you place on such information is therefore strictly at your own risk.  Apollo Energies Inc., urges you to consult with your
 own legal and/or financial advisers before taking any further actions based on information provided in this correspondence.<br>
</font></div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<br clear="all">
<div><br>
</div>
-- <br>
<div dir="ltr">
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div>
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div><span style="font-family:arial,helvetica,sans-serif;font-size:small">Kind Regards,</span><br>
</div>
<div><font face="arial, helvetica, sans-serif" size="2">Mark Stout, President<br>
HERS I & II, BPI BA, MFBA, RESNET HERS</font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Lighting & Mechanical Acceptance Testing </font></div>
<div><span style="font-family:arial,helvetica,sans-serif;color:rgb(0,0,0)">CALGreen Inspector/Plans Examiner</span><br>
</div>
<div><font face="arial, helvetica, sans-serif" size="2"><br>
</font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Apollo Energies, Inc.<br>
888-614-8338 x101 Office<br>
888-614-8338 Fax<br>
916-240-2850 Cell<br>
<a href="http://www.apolloenergiesinc.com" target="_blank">www.apolloenergiesinc.com</a><br>
Follow us on <a href="http://twitter.com/apolloenergies" target="_blank">Twitter</a> <a href="https://www.linkedin.com/company-beta/2061401/" target="_blank">LinkedIn</a> </font></div>
<div><font face="arial, helvetica, sans-serif" size="2">Subscribe to <a href="http://dailydigest.apolloenergiesinc.com" target="_blank">Apollo Energies Daily News</a> </font></div>
<div><font face="arial, helvetica, sans-serif" size="2"><br>
</font></div>
<div><span style="font-size:8pt"><br>
</span></div>
<div><font face="arial, helvetica, sans-serif" size="1">DISCLAIMER:  I am not an attorney nor am I an accountant.  The information and/or opinions expressed by myself or my affiliates should not be considered nor are they intended to provide legal or financial
 advice to any individual or entity.  The information contained in this email is for general information purposes only.  Any reliance you place on such information is therefore strictly at your own risk.  Apollo Energies Inc., urges you to consult with your
 own legal and/or financial advisers before taking any further actions based on information provided in this correspondence.<br>
</font></div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<span>_______________________________________________</span><br>
<span>Equest-users mailing list</span><br>
<span><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br>
<span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br>
</div>
</blockquote>
</div>

</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div><span style="font-family:arial,helvetica,sans-serif;font-size:small">Kind Regards,</span><br></div><div><font face="arial, helvetica, sans-serif" size="2">Mark Stout, President<br>HERS I & II, BPI BA, MFBA, RESNET HERS</font></div><div><font face="arial, helvetica, sans-serif" size="2">Lighting & Mechanical Acceptance Testing </font></div><div><span style="font-family:arial,helvetica,sans-serif;color:rgb(0,0,0)">CALGreen Inspector/Plans Examiner</span><br></div><div><font face="arial, helvetica, sans-serif" size="2"><br></font></div><div><font face="arial, helvetica, sans-serif" size="2">Apollo Energies, Inc.<br>888-614-8338 x101 Office<br>888-614-8338 Fax<br>916-240-2850 Cell<br><a href="http://www.apolloenergiesinc.com" target="_blank">www.apolloenergiesinc.com</a><br>Follow us on <a href="http://twitter.com/apolloenergies" target="_blank">Twitter</a> <a href="https://www.linkedin.com/company-beta/2061401/" target="_blank">LinkedIn</a> </font></div><div><font face="arial, helvetica, sans-serif" size="2">Subscribe to <a href="http://dailydigest.apolloenergiesinc.com" target="_blank">Apollo Energies Daily News</a> </font></div><div><font face="arial, helvetica, sans-serif" size="2"><br></font></div><div><span style="font-size:8pt"><br></span></div><div><font face="arial, helvetica, sans-serif" size="1">DISCLAIMER: 
I am not an attorney nor am I an accountant.  The information and/or
opinions expressed by myself or my affiliates should not be considered nor are
they intended to provide legal or financial advice to any individual or
entity.  The information contained in this email is for general
information purposes only.  Any reliance you place on such information is
therefore strictly at your own risk.  Apollo Energies Inc., urges you to
consult with your own legal and/or financial advisers before taking any further
actions based on information provided in this correspondence.<br></font></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div>