    <p>This is an oft-repeated question, and an important one that I
      would like to elaborate.</p>
    <p>DOE-2, the simulation engine behind eQUEST, simulates the
      building in steps.</p>
    <p> In the first LOADS step, it calculates the heat flows in and out
      of each zone at a user-defined temperature (default is 70F). These
      heat flows are what appears in the eQUEST output as "Building
      loads". <br>
    </p>
    <p>In the second SYSTEMS step, it simulates the HVAC system and
      controls to derive the actual temperature of the zones, with the
      heating or cooling input by the HVAC system reported in the eQUEST
      output as  the Building - HVAC".</p>
    <p>These two "loads" are very distinct.  In fact, I rarely look at
      the building loads except for debugging an input file.  Several
      things to remember:  <br>
    </p>
    <p>1. The Building Load (BL) contains information for each building
      component (walls, roofs, lighting, infiltration, etc.) because
      those are all individual heat flow paths that are simply added
      together to get the BL for the space or building.  <br>
    </p>
    <p>2. The Building - HVAC (BH) does not contain any of that because
      at this step DOE-2 is just using the total Space BL (SBL) in doing
      its simulation (note that in DOE-2 terminology,  it's called a
      "space" in Loads and a "zone" in Systems).  Furthermore, since
      DOE-2 derives the actual zone temperature in Systems, the SBL has
      to be adjusted, making it impossible to extract the component
      loads unless one does "reverse engineering" on the temperature
      difference, but would always be approximate due to thermal lag,
      thermostat deadband, etc.  (I can talk for days about extracting
      component-level loads from DOE-2 which I had to do for several
      DOE-2 projects back in the 1990s).<br>
    </p>
    <p>3. Natural or window ventilation is considered a Systems
      operation in DOE-2, so any effects from that will not appear in
      the BL, but only in the BH.</p>
    <p>So, I hope that clarifies why the BL is always different from the
      BH!</p>
    <p>Joe <br>
    </p>
    <p>Joe Huang</p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"</pre>
    <div class="moz-cite-prefix">On 3/11/2020 12:49 AM, Konstantina
      Kalliakoudi via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAEtzSjgoQ4Uv_BVOqp62fzTDbgDa-fe4OJQqB0zDDjF4TMAkQA@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div><img
            src="cid:part3.C3EF75F5.0B2EAF64@whiteboxtechnologies.com"
            alt="image.png" class="" width="542" height="338"><br>
        </div>
        <div><br>
        </div>
        <div>Dear equest users,</div>
        <div>I  generated  hourly report blocks looking for the loads.</div>
        <div>I saw that there are two options:</div>
        <div>1. "Building Loads" which as far I understood contains
          losses, gains etc....</div>
        <div>2. "Building - HVAC" - Coils - losses&gains 
          at te beginning I believed that it cantrained : The Loads from
          the fresh air +  "Building Loads". So in order to test that I
          made zero the fresh air at my AHUs. I was expecting that now
          the 
          "Building - HVAC" would be equal with 
          "Building Loads". But still there is a difference. 
          "Building - HVAC" is higher almost 50% than 
          "Building Loads".</div>
        <div><br>
        </div>
        <div>Any Ideas or Comments about what 
          "Building - HVAC" contains more than 
          "Building Loads"?</div>
        <div><br>
        </div>
        <div>Thank you for your help</div>
        <div><br>
        </div>
        <div>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US">Konstantina Kalliakoudi</span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US">Mechanical Engineer,M.Sc., LEED AP</span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US">KHM</span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US">Filolaou 28, Ilioupoli, Athens, Greece</span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US">Tel. 0030 210 99 69 680</span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span
              lang="EN-US"><a href="http://www.khmoe.gr"
                style="color:rgb(5,99,193)" moz-do-not-send="true">www.khmoe.gr</a></span></p>
          <p class="MsoNormal" style="margin:0cm 0cm
            0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"> </p>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>