<div dir="ltr"><div><p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">Hello to all equest -users,</span></p><p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">I am trying to model my
Baseline building based on ASHRAE 90.1-2010.</span></p><p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">In my case:</span></p>
<p class="gmail-MsoListParagraphCxSpFirst" style="line-height:150%;margin:0cm 0cm 0.0001pt 36pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">1.<span style="font-variant-numeric:normal;font-variant-east-asian:normal;font-stretch:normal;font-size:7pt;line-height:normal;font-family:"Times New Roman"">
</span></span><span lang="EN-US">In
my case based on paragraph G3.1.2.11 and in accordance with Section 6.5.6.1 due
to the climate zone and the %outdoor air at full design airflow rate “my
baseline building” require Heat Recovery System.</span></p>
<p class="gmail-MsoListParagraphCxSpLast" style="line-height:150%;margin:0cm 0cm 8pt 36pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">2.<span style="font-variant-numeric:normal;font-variant-east-asian:normal;font-stretch:normal;font-size:7pt;line-height:normal;font-family:"Times New Roman"">
</span></span><span lang="EN-US">Due
to the climate Zone from Table G3.1.2.6A an Economizer is not required.</span></p>
<p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">My question is about the control of the heat exchanger in the baseline
building. In paragraph 6.5.6.1 is mentioned: “Provisions shall be made to
bypass or control the energy recovery system to permit air economizer operation
as required by 6.5.1.1”.</span></p>
<p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">The tables of 6.5.1.1, Table 6.5.1.1A and B mention about control of
Economizer.</span></p>
<p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">Also is in the baseline building required an economizer required or not?
I mean, Table G3.1.2.6A and tables
6.5.1.1A and B seems to be in contradiction.</span></p>
<p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">I have modeled this in equest as following: What do you think;</span></p><p class="MsoNormal" style="line-height:150%;margin:0cm 0cm 8pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US"></span></p><div><img src="cid:ii_k694v1on1" alt="image.png" width="542" height="327"><br></div></div><div><br></div><div><br></div><div><br></div><div><div><img src="cid:ii_k694vcfd2" alt="image.png" width="542" height="326"><br></div></div><div><br></div><div>Thank you</div><div><br></div><div>Konstantina Kalliakoudi</div><div><br></div><div><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><span lang="EN-US">Konstantina
Kalliakoudi</span></p>
<span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif">Mechanical Engineer,M.Sc., </span><br></div><div><br></div></div>