    <p>I can't confirm this, but my recollection is that DOE-2 will
      report an unmet hour anytime the zone temperature exceeds the
      thermostat setting plus the throttling range, if that's defined.<br>
    </p>
    <p>Joe<br>
    </p>
    <div class="moz-cite-prefix">On 3/26/2019 8:18 AM, The Energy
      Simulation Academy wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CA+-pTU-HUd2ZX0GQvcfv3s-O6c2sX4dOcj+NCZqxhypv+6ZkaQ@mail.gmail.com">
      <div dir="ltr">Thanks Joe!<br>
        <br>
        Your participation prompts me to ask the question that is at the
        heart of this discussion - it looks like an attempt to "reverse
        engineer" a definition. We have all done it. FYI - and it's a
        massive but educational time pit. Does anyone [Joe] know the
        programmed definition for eQUEST, [probably from DOE2] on unmet
        hours?<br>
        <i>i.e DOE2 will mark an Unmet hour if a zone is: Outside the
          throttling range? How many degrees outside range (.1, 1 etc)?
          Plus Occupied? Plus Coil capacities are exceeded? Plus Any
          other conditions?</i><br>
        <br>
        Agreed about the hourly reports. The hourly one for eQUEST that
        I use is under thermal zone for the "amount of load that's
        unmet" for an hour. Include the zone temperature that hour and
        that should get you what you want (but possibly not what you
        need). There is probably an unmet hours flag to enable (0 or 1),
        but I might be thinking of the wrong software package? I try not
        to look at individual unmet hours for spaces - the space/zone is
        usually not the actual problem.<br>
        <br>
        A few notables from the images sent:<br>
        <ul>
          <li>Fans are running over 7500 hours per year. I doubt the
            building is occupied that many hours.</li>
          <li>Schedule seems to be a default schedule from the wizard?
            Defaults like this are often unoccupied on weekends and 12
            hours per day.</li>
          <li>That would be around 3000 occupied hours.</li>
          <li>Similar default schedules allow 82 degrees for unoccupied
            hours --> Possibly >5500 hours requiring 85 to be
            outside the throttling range, and they are unoccupied</li>
        </ul>
        <br>
        Best Regards,<br>
        <br>
        Bob<br>
        <br>
        <a href="http://Energy-models.com" target="_blank"
          moz-do-not-send="true">Energy-models.com</a><br>
        <a href="http://Simulate.Energy" target="_blank"
          moz-do-not-send="true">Simulate.Energy</a></div>
      <div><img alt="" moz-do-not-send="true">ᐧ</div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Mon, Mar 25, 2019 at 3:40
          PM Joe Huang via Equest-users <<a
            href="mailto:equest-users@lists.onebuilding.org"
            target="_blank" moz-do-not-send="true">equest-users@lists.onebuilding.org</a>>
          wrote:<br>
        </div>
        <blockquote class="gmail_quote">
          <div>
            <p>Paul, others,</p>
            <p>Being an old DOE-2 user, I would recommend getting the
              hourly reports for zone temperature, setpoint
              temperature,  and cooling load, and then aggregating these
              by hour of day and month, i.e., get 12 average hourly
              profiles by month, which would tell you what's going on. I
              don't know if there's an hourly report variable for unmet
              load, but it should be detectable as hours where the zone
              temperature exceeds the setpoint temperature.  I know how
              to  set up hourly reports in DOE-2, but  don't know how
              can be done in eQUEST.<br>
            </p>
            <p>Joe<br>
            </p>
            <pre class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">yjhuang@whiteboxtechnologies.com</a>
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com" target="_blank" moz-do-not-send="true">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
            <div
class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-cite-prefix">On
              3/25/2019 6:27 AM, Bishop, Bill via Equest-users wrote:<br>
            </div>
            <blockquote type="cite">
              <div
class="gmail-m_6304813575628337139gmail-m_1866183690012848749WordSection1">
                <p class="MsoNormal">Hi Paul,</p>
                <p class="MsoNormal">The <span>75 °F input that you
                    shared below for “Indoor Design Temperature” is the
                    DESIGN-COOL-T which is used for sizing calculations
                    (and is optional when using DOE-2.3). The hourly
                    thermostat setpoint is part of the thermostat
                    schedule so you need to look at the day schedules
                    within the S1 Sys1 (PSZ) Cool Sch.</span></p>
                <p class="MsoNormal">Regards,</p>
                <p class="MsoNormal">~Bill</p>
                <p class="MsoNormal"> </p>
                <div>
                  <p class="MsoNormal"><b><span>William Bishop, PE,
                        BEMP, BEAP, CEM, LEED AP</span></b></p>
                  <p class="MsoNormal"><b><span>Senior Energy Engineer</span></b></p>
                  <p class="MsoNormal"><b><span> </span></b></p>
                  <p class="MsoNormal"><img src="cid:169ba614cb25b006a1"
                      alt="Pathfinder-EA-logo-2" moz-do-not-send="true"
                      width="91" height="59"><b><i><span>T: (585)
                          698-1956</span></i></b><b><i><span>             
                        </span> </i></b><span>          </span><span>F:
                      (585) 325-6005</span></p>
                  <p class="MsoNormal"><a
                      href="mailto:wbishop@pathfinder-ea.com"
                      target="_blank" moz-do-not-send="true"><span>bbishop@pathfinder-ea.com</span></a><span>        </span><a
                      href="http://www.pathfinder-ea.com/"
                      target="_blank" moz-do-not-send="true"><span>www.pathfinder-ea.com</span></a><span></span></p>
                  <p class="MsoNormal"><span>134 South Fitzhugh Street</span></p>
                  <p class="MsoNormal"><span>Rochester, NY
                      14608               <img
id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_1"
                        src="cid:169ba614cb2afa3b82"
                        moz-do-not-send="true" width="26" height="23">       
                    </span><i><span>Ask me why Carbon Fee & Dividend
                        may be right for you.</span></i><span></span></p>
                </div>
                <p class="MsoNormal"> </p>
                <div>
                  <div>
                    <p class="MsoNormal"><b>From:</b> Equest-users <a
class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-rfc2396E"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank"
                        moz-do-not-send="true"><equest-users-bounces@lists.onebuilding.org></a>
                      <b>On Behalf Of </b>Integral Mechanical
                      Engineering Designs via Equest-users<br>
                      <b>Sent:</b> Saturday, March 23, 2019 2:34 PM<br>
                      <b>To:</b> David Eldridge <a
class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-rfc2396E"
                        href="mailto:DEldridge@grummanbutkus.com"
                        target="_blank" moz-do-not-send="true"><DEldridge@grummanbutkus.com></a>;
                      <a
class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated"
                        href="mailto:equest-users@lists.onebuilding.org"
                        target="_blank" moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                      <b>Subject:</b> Re: [Equest-users] Hourly space
                      temperature after cooling</p>
                  </div>
                </div>
                <p class="MsoNormal"> </p>
                <p class="MsoNormal"><span>Hi David,</span></p>
                <div>
                  <p class="MsoNormal"><span> </span></p>
                </div>
                <div>
                  <p class="MsoNormal"><span>Thanks for the answer. I
                      don´t think that explain the data because the
                      system is working most of the time during the
                      year, and a note in the SS-O report shows that the
                      temperature counts are made only for the hours
                      when the fans are on. The cooling schedule matches
                      with the  occupancy schedule.</span></p>
                  <p class="MsoNormal"><img
id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_4"
                      src="cid:169ba614cb3bdbb393"
                      moz-do-not-send="true" width="885" height="463"><span></span></p>
                  <p class="MsoNormal"><span>The set point is 75 °F and
                      the throttle range is 2 °R.</span></p>
                  <p class="MsoNormal"><img
id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_5"
                      src="cid:169ba614cb31f3c04f4"
                      moz-do-not-send="true" width="362" height="210"><span></span></p>
                  <p class="MsoNormal"><span>The BEPS report shows that
                      are 155 unmet hours, but the SS-O report gives a
                      value of at least 2505 (adding from 80-85 and
                      above 85).</span></p>
                </div>
                <div>
                  <p class="MsoNormal"><span> </span></p>
                </div>
                <div
                  id="gmail-m_6304813575628337139gmail-m_1866183690012848749signature">
                  <div
id="gmail-m_6304813575628337139gmail-m_1866183690012848749divtagdefaultwrapper">
                    <div>
                      <p class="MsoNormal"><span>Kind Regards,</span></p>
                    </div>
                    <div
                      id="gmail-m_6304813575628337139gmail-m_1866183690012848749signature">
                      <div
id="gmail-m_6304813575628337139gmail-m_1866183690012848749divtagdefaultwrapper">
                        <p><span>Paul Caicedo</span></p>
                        <p><span>Mechanical Engineering Consultant</span></p>
                        <p><u><span>                                   
                                                          </span></u><span></span></p>
                        <p><b><span>IntegralMECH</span></b><span></span></p>
                      </div>
                    </div>
                  </div>
                </div>
                <div>
                  <p class="MsoNormal"><span> </span></p>
                </div>
                <p class="MsoNormal"><img
id="gmail-m_6304813575628337139gmail-m_1866183690012848749Horizontal_x0020_Line_x0020_1"
                    src="cid:169ba614cb3201d7d05" moz-do-not-send="true"
                    width="694" height="2"></p>
                <div
                  id="gmail-m_6304813575628337139gmail-m_1866183690012848749divRplyFwdMsg">
                  <p class="MsoNormal"><b><span>From:</span></b><span>
                      David Eldridge <<a
                        href="mailto:DEldridge@grummanbutkus.com"
                        target="_blank" moz-do-not-send="true">DEldridge@grummanbutkus.com</a>><br>
                      <b>Sent:</b> March 22, 2019 9:29 AM<br>
                      <b>To:</b> Integral Mechanical Engineering Designs<br>
                      <b>Subject:</b> RE: Hourly space temperatura after
                      cooling</span> </p>
                  <div>
                    <p class="MsoNormal"> </p>
                  </div>
                </div>
                <div>
                  <div>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>That
                        SS-O report should be after cooling (it’s a
                        “system” report), but it may include some hours
                        when the control system is in setback – it’s not
                        only for occupied hours, would that explain your
                        data?</span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>There
                        is a separate module for report variables that
                        you can specify to document any number of
                        internal calculations, including one or more
                        space temperatures – it’s been a while since I
                        set one of those up but if you search this
                        community for “report variables” some
                        instructions should pop up.</span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>These
                        can then also be exported to excel, or printed
                        in the *.sim report.</span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>David </span><span></span></p>
                    <div>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b><span>David
                            S. Eldridge, Jr.</span><span>, P</span><span>.</span><span>E</span><span>.</span><span>,
                            LEED AP BD+C, BEMP, BEAP, HBDP</span></b><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>Associate</span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>Direct:
                          (847) 316-92</span><span>24</span><span> |
                          Mobile: (</span><span>773</span><span>) </span><span>490</span><span>-</span><span>5038</span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b><span>Grumman/Butkus
                            Associates</span></b><span> </span><span>|
                          820 Davis Street, Suite 300 | Evanston, IL
                          60201</span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>Energy
                          Efficiency Consultants and Sustainable Design
                          Engineers</span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                      <p
                        class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><u><span><a
                              href="http://grummanbutkus.com/"
                              target="_blank" moz-do-not-send="true"><span>grummanbutkus.com</span></a></span></u><span>
                          | <u><a href="http://grummanbutkus.com/blog"
                              target="_blank" moz-do-not-send="true"><span>Blog</span></a></u>
                          | <u><a
href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526"
                              target="_blank" moz-do-not-send="true"><span>Facebook</span></a></u>
                          | <u><a
                              href="https://twitter.com/grummanbutkus"
                              target="_blank" moz-do-not-send="true"><span>Twitter</span></a></u></span><span></span></p>
                    </div>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span><span></span></p>
                    <div>
                      <div>
                        <p
                          class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b>From:</b>
                          Equest-users [<a
                            href="mailto:equest-users-bounces@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                          <b>On Behalf Of </b>Integral Mechanical
                          Engineering Designs via Equest-users<br>
                          <b>Sent:</b> Friday, March 22, 2019 8:51 AM<br>
                          <b>To:</b> <a
                            href="mailto:equest-users@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                          <b>Subject:</b> [Equest-users] Hourly space
                          temperatura after cooling<span></span></p>
                      </div>
                    </div>
                    <p
                      class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> </span></p>
                    <div>
                      <p><span lang="EN-CA">Hi all,</span><span></span></p>
                      <p><span lang="EN-CA"> </span><span></span></p>
                      <p><span lang="EN-CA">If I open the BEPS Building
                          Energy Performance, there are 155 unmet hours.
                          I would like to get the temperature values
                          throughout the year after cooling, but the
                          only related option that I can see is the SS-O
                          Space Temperature Summary where the
                          temperatures above the set point are much more
                          than the unmet hours. It seems that is the
                          report of the space before cooling.</span><span></span></p>
                      <p><span lang="EN-CA"> </span><span></span></p>
                      <p><span lang="EN-CA">How could I get the space
                          temperature after cooling to have relation
                          with the unmet hours?</span><span></span></p>
                      <p><span lang="EN-CA"> </span><span></span></p>
                    </div>
                    <div
                      id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_signature">
                      <div
id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_divtagdefaultwrapper">
                        <div>
                          <p
                            class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span>Kind
                              Regards,</span><span></span></p>
                        </div>
                        <div
                          id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_signature">
                          <div
id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_divtagdefaultwrapper">
                            <p><span>Paul Caicedo</span><span></span></p>
                            <p><span>Mechanical Engineering Consultant</span><span></span></p>
                            <p><u><span>                               
                                                                  </span></u><span></span></p>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
                <p><b><span>IntegralMECH</span></b><span></span></p>
              </div>
              <br>
              <fieldset
class="gmail-m_6304813575628337139gmail-m_1866183690012848749mimeAttachmentHeader"></fieldset>
              <pre class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-quote-pre">_______________________________________________
Equest-users mailing list
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
            </blockquote>
          </div>
          _______________________________________________<br>
          Equest-users mailing list<br>
          <a
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
          To unsubscribe from this mailing list send  a blank message to
          <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
            target="_blank" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
        </blockquote>
      </div>
      <br>
      <div><br>
      </div>
      -- <br>
      <div dir="ltr" class="gmail-m_6304813575628337139gmail_signature">
        <div dir="ltr">
          <div>
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div>
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div>
                            <div dir="ltr">
                              <div>
                                <div dir="ltr"><span><b>The Energy
                                      Simulation Academy</b></span>
                                  <div><a href="http://simulate.energy/"
                                      target="_blank"
                                      moz-do-not-send="true"><img
                                        moz-do-not-send="true"
                                        width="200" height="131"></a></div>
                                  <div><a href="http://simulate.energy/"
                                      target="_blank"
                                      moz-do-not-send="true">Simulate.Energy</a></div>
                                  <div>Follow us on <a
href="https://www.linkedin.com/in/the-energy-simulation-academy-tesa-42584b16b/"
                                      target="_blank"
                                      moz-do-not-send="true">Linkedin</a> and <a
href="https://www.facebook.com/groups/245943612664667/?ref=bookmarks"
                                      target="_blank"
                                      moz-do-not-send="true">Facebook</a></div>
                                  <div><br>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
  </body>
</html>