<div dir="ltr">Thanks Joe!<br><br>Your participation prompts me to ask the question that is at the heart of this discussion - it looks like an attempt to "reverse engineer" a definition. We have all done it. FYI - and it's a massive but educational time pit. Does anyone [Joe] know the programmed definition for eQUEST, [probably from DOE2] on unmet hours?<br><i>i.e DOE2 will mark an Unmet hour if a zone is: Outside the throttling range? How many degrees outside range (.1, 1 etc)? Plus Occupied? Plus Coil capacities are exceeded? Plus Any other conditions?</i><br><br>Agreed about the hourly reports. The hourly one for eQUEST that I use is under thermal zone for the "amount of load that's unmet" for an hour. Include the zone temperature that hour and that should get you what you want (but possibly not what you need). There is probably an unmet hours flag to enable (0 or 1), but I might be thinking of the wrong software package? I try not to look at individual unmet hours for spaces - the space/zone is usually not the actual problem.<br><br>A few notables from the images sent:<br><ul><li>Fans are running over 7500 hours per year. I doubt the building is occupied that many hours.</li><li>Schedule seems to be a default schedule from the wizard? Defaults like this are often unoccupied on weekends and 12 hours per day.</li><li>That would be around 3000 occupied hours.</li><li>Similar default schedules allow 82 degrees for unoccupied hours --> Possibly >5500 hours requiring 85 to be outside the throttling range, and they are unoccupied</li></ul><br>Best Regards,<br><br>Bob<br><br><a href="http://Energy-models.com" target="_blank">Energy-models.com</a><br><a href="http://Simulate.Energy" target="_blank">Simulate.Energy</a></div><div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=aaW5mb0BlbmVyZ3ktbW9kZWxzLmNvbQ%3D%3D&type=zerocontent&guid=31e55d6b-c99e-46ff-8e24-96eb6ec2a044"><font color="#ffffff" size="1">ᐧ</font></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Mar 25, 2019 at 3:40 PM Joe Huang via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF">
    <p>Paul, others,</p>
    <p>Being an old DOE-2 user, I would recommend getting the hourly
      reports for zone temperature, setpoint temperature,  and cooling
      load, and then aggregating these by hour of day and month, i.e.,
      get 12 average hourly profiles by month, which would tell you
      what's going on. I don't know if there's an hourly report variable
      for unmet load, but it should be detectable as hours where the
      zone temperature exceeds the setpoint temperature.  I know how to 
      set up hourly reports in DOE-2, but  don't know how can be done in
      eQUEST.<br>
    </p>
    <p>Joe<br>
    </p>
    <pre class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-cite-prefix">On 3/25/2019 6:27 AM, Bishop, Bill via
      Equest-users wrote:<br>
    </div>
    <blockquote type="cite">
      
      
      
      
      <div class="gmail-m_6304813575628337139gmail-m_1866183690012848749WordSection1">
        <p class="MsoNormal">Hi Paul,<u></u><u></u></p>
        <p class="MsoNormal">The <span style="font-size:12pt;color:black">75 °F input that you
            shared below for “Indoor Design Temperature” is the
            DESIGN-COOL-T which is used for sizing calculations (and is
            optional when using DOE-2.3). The hourly thermostat setpoint
            is part of the thermostat schedule so you need to look at
            the day schedules within the S1 Sys1 (PSZ) Cool Sch.<u></u><u></u></span></p>
        <p class="MsoNormal">Regards,<u></u><u></u></p>
        <p class="MsoNormal">~Bill<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <div>
          <p class="MsoNormal"><b><span>William
                Bishop, PE, BEMP, BEAP, CEM, LEED AP<u></u><u></u></span></b></p>
          <p class="MsoNormal"><b><span style="font-size:9pt;font-family:Arial,sans-serif;color:black">Senior
                Energy Engineer<u></u><u></u></span></b></p>
          <p class="MsoNormal"><b><span style="font-size:3pt;font-family:Arial,sans-serif;color:black"><u></u> <u></u></span></b></p>
          <p class="MsoNormal"><img style="width: 0.9479in; height: 0.6145in;" src="cid:169ba614cb25b006a1" alt="Pathfinder-EA-logo-2" width="91" hspace="12" height="59" align="left"><b><i><span style="font-size:9pt;font-family:Arial,sans-serif;color:rgb(0,32,96)">T:
                  (585) 698-1956</span></i></b><b><i><span style="color:rgb(0,32,96)">              </span>
              </i></b><span style="color:rgb(31,73,125)">          </span><span style="font-size:9pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">F:
              (585) 325-6005<u></u><u></u></span></p>
          <p class="MsoNormal"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">bbishop@pathfinder-ea.com</span></a><span style="font-size:9pt;font-family:Arial,sans-serif;color:black">        </span><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">www.pathfinder-ea.com</span></a><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
          <p class="MsoNormal"><span style="font-size:9pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">134
              South Fitzhugh Street<u></u><u></u></span></p>
          <p class="MsoNormal"><span style="font-size:9pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Rochester,
              NY 14608               <img style="width: 0.2708in; height: 0.2395in;" id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_1" src="cid:169ba614cb2afa3b82" width="26" height="23" border="0">       
            </span><i><span style="font-size:7pt;font-family:Verdana,sans-serif;color:rgb(0,176,240)">Ask
                me why Carbon Fee & Dividend may be right for you.</span></i><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
        </div>
        <p class="MsoNormal"><u></u> <u></u></p>
        <div>
          <div style="border-right:none;border-bottom:none;border-left:none;border-top:1pt solid rgb(225,225,225);padding:3pt 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users
              <a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-rfc2396E" href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank"><equest-users-bounces@lists.onebuilding.org></a>
              <b>On Behalf Of </b>Integral Mechanical Engineering
              Designs via Equest-users<br>
              <b>Sent:</b> Saturday, March 23, 2019 2:34 PM<br>
              <b>To:</b> David Eldridge
              <a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-rfc2396E" href="mailto:DEldridge@grummanbutkus.com" target="_blank"><DEldridge@grummanbutkus.com></a>;
              <a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] Hourly space
              temperature after cooling<u></u><u></u></p>
          </div>
        </div>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal"><span style="font-size:12pt;color:black">Hi
            David,<u></u><u></u></span></p>
        <div>
          <p class="MsoNormal"><span style="font-size:12pt;color:black"><u></u> <u></u></span></p>
        </div>
        <div>
          <p class="MsoNormal"><span style="font-size:12pt;color:black">Thanks for the
              answer. I don´t think that explain the data because the
              system is working most of the time during the year, and a
              note in the SS-O report shows that the temperature counts
              are made only for the hours when the fans are on. The
              cooling schedule matches with the  occupancy schedule.<u></u><u></u></span></p>
          <p class="MsoNormal"><img style="width: 9.2187in; height: 4.8229in;" id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_4" src="cid:169ba614cb3bdbb393" width="885" height="463" border="0"><span style="font-size:12pt;color:black"><u></u><u></u></span></p>
          <p class="MsoNormal"><span style="font-size:12pt;color:black">The set point is 75
              °F and the throttle range is 2 °R.<u></u><u></u></span></p>
          <p class="MsoNormal"><img style="width: 3.7708in; height: 2.1875in;" id="gmail-m_6304813575628337139gmail-m_1866183690012848749Picture_x0020_5" src="cid:169ba614cb31f3c04f4" width="362" height="210" border="0"><span style="font-size:12pt;color:black"><u></u><u></u></span></p>
          <p class="MsoNormal"><span style="font-size:12pt;color:black">The BEPS report shows
              that are 155 unmet hours, but the SS-O report gives a
              value of at least 2505 (adding from 80-85 and above 85).<u></u><u></u></span></p>
        </div>
        <div>
          <p class="MsoNormal"><span style="font-size:12pt;color:black"><u></u> <u></u></span></p>
        </div>
        <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749signature">
          <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749divtagdefaultwrapper">
            <div>
              <p class="MsoNormal" style="background:white"><span style="font-size:12pt;color:black">Kind Regards,<u></u><u></u></span></p>
            </div>
            <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749signature">
              <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749divtagdefaultwrapper">
                <p style="background:white"><span style="font-size:12pt;color:black">Paul Caicedo<u></u><u></u></span></p>
                <p style="background:white"><span style="font-size:12pt;color:black">Mechanical
                    Engineering Consultant<u></u><u></u></span></p>
                <p style="background:white"><u><span style="font-size:12pt;color:black">             
                                                                        </span></u><span style="font-size:12pt;color:black"><u></u><u></u></span></p>
                <p style="background:white"><b><span style="font-size:12pt;color:black">IntegralMECH</span></b><span style="font-size:12pt;color:black"><u></u><u></u></span></p>
              </div>
            </div>
          </div>
        </div>
        <div>
          <p class="MsoNormal"><span style="font-size:12pt;color:black"><u></u> <u></u></span></p>
        </div>
        <p class="MsoNormal"><img style="width: 7.2291in; height: 0.0208in;" id="gmail-m_6304813575628337139gmail-m_1866183690012848749Horizontal_x0020_Line_x0020_1" src="cid:169ba614cb3201d7d05" width="694" height="2" border="0"><u></u><u></u></p>
        <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749divRplyFwdMsg">
          <p class="MsoNormal"><b><span style="color:black">From:</span></b><span style="color:black"> David Eldridge <<a href="mailto:DEldridge@grummanbutkus.com" target="_blank">DEldridge@grummanbutkus.com</a>><br>
              <b>Sent:</b> March 22, 2019 9:29 AM<br>
              <b>To:</b> Integral Mechanical Engineering Designs<br>
              <b>Subject:</b> RE: Hourly space temperatura after cooling</span>
            <u></u><u></u></p>
          <div>
            <p class="MsoNormal"> <u></u><u></u></p>
          </div>
        </div>
        <div>
          <div>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)">That SS-O
                report should be after cooling (it’s a “system” report),
                but it may include some hours when the control system is
                in setback – it’s not only for occupied hours, would
                that explain your data?</span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)">There is a
                separate module for report variables that you can
                specify to document any number of internal calculations,
                including one or more space temperatures – it’s been a
                while since I set one of those up but if you search this
                community for “report variables” some instructions
                should pop up.</span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)">These can
                then also be exported to excel, or printed in the *.sim
                report.</span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)">David </span><span><u></u><u></u></span></p>
            <div>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b><span style="color:rgb(31,73,125)">David
                    S. Eldridge, Jr.</span><span style="color:rgb(36,64,97)">,
                    P</span><span style="color:rgb(31,73,125)">.</span><span style="color:rgb(36,64,97)">E</span><span style="color:rgb(31,73,125)">.</span><span style="color:rgb(36,64,97)">, LEED AP BD+C, BEMP, BEAP,
                    HBDP</span></b><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)">Associate</span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="font-size:4pt;color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(54,95,145)">Direct:
                  (847) 316-92</span><span style="color:rgb(31,73,125)">24</span><span style="color:rgb(54,95,145)"> | Mobile: (</span><span style="color:rgb(31,73,125)">773</span><span style="color:rgb(54,95,145)">)
                </span><span style="color:rgb(31,73,125)">490</span><span style="color:rgb(54,95,145)">-</span><span style="color:rgb(31,73,125)">5038</span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="font-size:10pt;color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b><span style="color:rgb(36,64,97)">Grumman/Butkus
                    Associates</span></b><span style="color:gray">
                </span><span style="color:rgb(54,95,145)">| 820 Davis Street,
                  Suite 300 | Evanston, IL 60201</span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="font-size:9pt;color:gray">Energy Efficiency
                  Consultants and Sustainable Design Engineers</span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
              <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><u><span style="font-size:9pt;color:gray"><a href="http://grummanbutkus.com/" target="_blank"><span style="color:gray">grummanbutkus.com</span></a></span></u><span style="font-size:9pt;color:gray"> |
                  <u><a href="http://grummanbutkus.com/blog" target="_blank"><span style="color:gray">Blog</span></a></u>
                  |
                  <u><a href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526" target="_blank"><span style="color:gray">Facebook</span></a></u>
                  |
                  <u><a href="https://twitter.com/grummanbutkus" target="_blank"><span style="color:gray">Twitter</span></a></u></span><span><u></u><u></u></span></p>
            </div>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span style="color:rgb(31,73,125)"> </span><span><u></u><u></u></span></p>
            <div>
              <div style="border-right:none currentcolor;border-bottom:none currentcolor;border-left:none currentcolor;border-top:1pt solid currentcolor;padding:3pt 0in 0in">
                <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                  <b>On Behalf Of </b>Integral Mechanical Engineering
                  Designs via Equest-users<br>
                  <b>Sent:</b> Friday, March 22, 2019 8:51 AM<br>
                  <b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
                  <b>Subject:</b> [Equest-users] Hourly space
                  temperatura after cooling<span><u></u><u></u></span></p>
              </div>
            </div>
            <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal"><span> <u></u><u></u></span></p>
            <div>
              <p><span style="font-size:12pt;color:black" lang="EN-CA">Hi
                  all,</span><span><u></u><u></u></span></p>
              <p><span style="font-size:12pt;color:black" lang="EN-CA"> </span><span><u></u><u></u></span></p>
              <p><span style="font-size:12pt;color:black" lang="EN-CA">If
                  I open the BEPS Building Energy Performance, there are
                  155 unmet hours. I would like to get the temperature
                  values throughout the year after cooling, but the only
                  related option that I can see is the SS-O Space
                  Temperature Summary where the temperatures above the
                  set point are much more than the unmet hours. It seems
                  that is the report of the space before cooling.</span><span><u></u><u></u></span></p>
              <p><span style="font-size:12pt;color:black" lang="EN-CA"> </span><span><u></u><u></u></span></p>
              <p><span style="font-size:12pt;color:black" lang="EN-CA">How
                  could I get the space temperature after cooling to
                  have relation with the unmet hours?</span><span><u></u><u></u></span></p>
              <p><span style="font-size:12pt;color:black" lang="EN-CA"> </span><span><u></u><u></u></span></p>
            </div>
            <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_signature">
              <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_divtagdefaultwrapper">
                <div>
                  <p class="gmail-m_6304813575628337139gmail-m_1866183690012848749xmsonormal" style="background:white"><span style="font-size:12pt;color:black">Kind Regards,</span><span><u></u><u></u></span></p>
                </div>
                <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_signature">
                  <div id="gmail-m_6304813575628337139gmail-m_1866183690012848749x_divtagdefaultwrapper">
                    <p style="background:white"><span style="font-size:12pt;color:black">Paul
                        Caicedo</span><span><u></u><u></u></span></p>
                    <p style="background:white"><span style="font-size:12pt;color:black">Mechanical
                        Engineering Consultant</span><span><u></u><u></u></span></p>
                    <p style="background:white"><u><span style="font-size:12pt;color:black">         
                                                                       
                                  </span></u><span><u></u><u></u></span></p>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <p style="background:white"><b><span style="font-size:12pt;color:black">IntegralMECH</span></b><span><u></u><u></u></span></p>
      </div>
      <br>
      <fieldset class="gmail-m_6304813575628337139gmail-m_1866183690012848749mimeAttachmentHeader"></fieldset>
      <pre class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-quote-pre">_______________________________________________
Equest-users mailing list
<a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="gmail-m_6304813575628337139gmail-m_1866183690012848749moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </div>

_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr" class="gmail-m_6304813575628337139gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><font face="georgia, serif" style="color:rgb(136,136,136);font-size:12.8px"><span style="font-size:12.8px"><b>The Energy Simulation Academy</b></span></font><div style="color:rgb(136,136,136);font-size:12.8px;font-family:Arial,Helvetica,sans-serif"><a href="http://simulate.energy/" style="color:rgb(17,85,204)" target="_blank"><img src="https://docs.google.com/uc?export=download&id=1HlkgKdB26cSbEQN-U6d4hm8Zg-jrpCyg&revid=0B1vD4jOXrCvQVGdobk9laElydW5hYU0wUVphVUUyRlUyZFZZPQ" width="200" height="131"></a></div><div style="color:rgb(136,136,136);font-size:12.8px;font-family:Arial,Helvetica,sans-serif"><a href="http://simulate.energy/" style="color:rgb(17,85,204)" target="_blank">Simulate.Energy</a></div><div style="color:rgb(136,136,136);font-size:12.8px;font-family:Arial,Helvetica,sans-serif">Follow us on <a href="https://www.linkedin.com/in/the-energy-simulation-academy-tesa-42584b16b/" target="_blank">Linkedin</a> and <a href="https://www.facebook.com/groups/245943612664667/?ref=bookmarks" target="_blank">Facebook</a></div><div style="font-family:Arial,Helvetica,sans-serif"><br></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div>