    <p>Paul, others,</p>
    <p>Being an old DOE-2 user, I would recommend getting the hourly
      reports for zone temperature, setpoint temperature,  and cooling
      load, and then aggregating these by hour of day and month, i.e.,
      get 12 average hourly profiles by month, which would tell you
      what's going on. I don't know if there's an hourly report variable
      for unmet load, but it should be detectable as hours where the
      zone temperature exceeds the setpoint temperature.  I know how to 
      set up hourly reports in DOE-2, but  don't know how can be done in
      eQUEST.<br>
    </p>
    <p>Joe<br>
    </p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 3/25/2019 6:27 AM, Bishop, Bill via
      Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:90D829482BDEDB4CB264DE5060592B195B72FEF3@lightning.pathfinderengineers.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"Franklin Gothic Medium";
        panose-1:2 11 6 3 2 1 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
p.xmsonormal, li.xmsonormal, div.xmsonormal
        {mso-style-name:x_msonormal;
        margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1027" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Hi Paul,<o:p></o:p></p>
        <p class="MsoNormal">The <span
            style="font-size:12.0pt;color:black">75 °F input that you
            shared below for “Indoor Design Temperature” is the
            DESIGN-COOL-T which is used for sizing calculations (and is
            optional when using DOE-2.3). The hourly thermostat setpoint
            is part of the thermostat schedule so you need to look at
            the day schedules within the S1 Sys1 (PSZ) Cool Sch.<o:p></o:p></span></p>
        <p class="MsoNormal">Regards,<o:p></o:p></p>
        <p class="MsoNormal">~Bill<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <p class="MsoNormal"><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:black">William
                Bishop, PE, BEMP, BEAP, CEM, LEED AP<o:p></o:p></span></b></p>
          <p class="MsoNormal"><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">Senior
                Energy Engineer<o:p></o:p></span></b></p>
          <p class="MsoNormal"><b><span
style="font-size:3.0pt;font-family:"Arial",sans-serif;color:black"><o:p> </o:p></span></b></p>
          <p class="MsoNormal"><!--[if gte vml 1]><v:shapetype id="_x0000_t75" coordsize="21600,21600" o:spt="75" o:preferrelative="t" path="m@4@5l@4@11@9@11@9@5xe" filled="f" stroked="f">
<v:stroke joinstyle="miter" />
<v:formulas>
<v:f eqn="if lineDrawn pixelLineWidth 0" />
<v:f eqn="sum @0 1 0" />
<v:f eqn="sum 0 0 @1" />
<v:f eqn="prod @2 1 2" />
<v:f eqn="prod @3 21600 pixelWidth" />
<v:f eqn="prod @3 21600 pixelHeight" />
<v:f eqn="sum @0 0 1" />
<v:f eqn="prod @6 1 2" />
<v:f eqn="prod @7 21600 pixelWidth" />
<v:f eqn="sum @8 21600 0" />
<v:f eqn="prod @7 21600 pixelHeight" />
<v:f eqn="sum @10 21600 0" />
</v:formulas>
<v:path o:extrusionok="f" gradientshapeok="t" o:connecttype="rect" />
<o:lock v:ext="edit" aspectratio="t" />
</v:shapetype><v:shape id="Picture_x0020_4" o:spid="_x0000_s1026" type="#_x0000_t75" alt="Pathfinder-EA-logo-2" style='position:absolute;margin-left:0;margin-top:63.6pt;width:68.45pt;height:43.9pt;z-index:-251657216;visibility:visible;mso-wrap-style:square;mso-width-percent:0;mso-height-percent:0;mso-wrap-distance-left:9pt;mso-wrap-distance-top:0;mso-wrap-distance-right:9pt;mso-wrap-distance-bottom:0;mso-position-horizontal:left;mso-position-horizontal-relative:text;mso-position-vertical:absolute;mso-position-vertical-relative:text;mso-width-percent:0;mso-height-percent:0;mso-width-relative:page;mso-height-relative:page'>
<v:imagedata src="mailbox:///C:/Users/Joe%20Huang/AppData/Roaming/Thunderbird/Profiles/6tp56871.default/Mail/Local%20Folders/Inbox?number=114418361&header=quotebody&part=1.1.2&filename=image004.jpg" o:title="Pathfinder-EA-logo-2" />
<w:wrap type="through"/>
</v:shape><![endif]--><!--[if !vml]--><img
              style="width:.9479in;height:.6145in"
              src="cid:part1.9FA30851.973EFDC7@whiteboxtechnologies.com"
              alt="Pathfinder-EA-logo-2" v:shapes="Picture_x0020_4"
              class="" width="91" hspace="12" height="59" align="left"><!--[endif]--><b><i><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#002060">T:
                  (585) 698-1956</span></i></b><b><i><span
                  style="color:#002060">              </span>
              </i></b><span style="color:#1F497D">          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#1F497D">F:
              (585) 325-6005<o:p></o:p></span></p>
          <p class="MsoNormal"><a
              href="mailto:wbishop@pathfinder-ea.com"
              moz-do-not-send="true"><span
                style="font-size:9.0pt;font-family:"Arial",sans-serif">bbishop@pathfinder-ea.com</span></a><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">        </span><a
              href="http://www.pathfinder-ea.com/"
              moz-do-not-send="true"><span
                style="font-size:9.0pt;font-family:"Arial",sans-serif">www.pathfinder-ea.com</span></a><span
              style="color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#1F497D">134
              South Fitzhugh Street<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#1F497D">Rochester,
              NY 14608               <img
                style="width:.2708in;height:.2395in"
                id="Picture_x0020_1"
                src="cid:part4.2DA6AAF5.FA6AD030@whiteboxtechnologies.com"
                class="" width="26" height="23" border="0">       
            </span><i><span
style="font-size:7.0pt;font-family:"Verdana",sans-serif;color:#00B0F0">Ask
                me why Carbon Fee & Dividend may be right for you.</span></i><span
              style="color:#1F497D"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users
              <a class="moz-txt-link-rfc2396E" href="mailto:equest-users-bounces@lists.onebuilding.org"><equest-users-bounces@lists.onebuilding.org></a>
              <b>On Behalf Of </b>Integral Mechanical Engineering
              Designs via Equest-users<br>
              <b>Sent:</b> Saturday, March 23, 2019 2:34 PM<br>
              <b>To:</b> David Eldridge
              <a class="moz-txt-link-rfc2396E" href="mailto:DEldridge@grummanbutkus.com"><DEldridge@grummanbutkus.com></a>;
              <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] Hourly space
              temperature after cooling<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="font-size:12.0pt;color:black">Hi
            David,<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black"><o:p> </o:p></span></p>
        </div>
        <div>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black">Thanks for the
              answer. I don´t think that explain the data because the
              system is working most of the time during the year, and a
              note in the SS-O report shows that the temperature counts
              are made only for the hours when the fans are on. The
              cooling schedule matches with the  occupancy schedule.<o:p></o:p></span></p>
          <p class="MsoNormal"><img
              style="width:9.2187in;height:4.8229in"
              id="Picture_x0020_4"
              src="cid:part5.B4023ED4.1CCCB8DD@whiteboxtechnologies.com"
              class="" width="885" height="463" border="0"><span
              style="font-size:12.0pt;color:black"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black">The set point is 75
              °F and the throttle range is 2 °R.<o:p></o:p></span></p>
          <p class="MsoNormal"><img
              style="width:3.7708in;height:2.1875in"
              id="Picture_x0020_5"
              src="cid:part6.A55536AD.2DF3B2C0@whiteboxtechnologies.com"
              class="" width="362" height="210" border="0"><span
              style="font-size:12.0pt;color:black"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black">The BEPS report shows
              that are 155 unmet hours, but the SS-O report gives a
              value of at least 2505 (adding from 80-85 and above 85).<o:p></o:p></span></p>
        </div>
        <div>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black"><o:p> </o:p></span></p>
        </div>
        <div id="signature">
          <div id="divtagdefaultwrapper">
            <div>
              <p class="MsoNormal" style="background:white"><span
                  style="font-size:12.0pt;color:black">Kind Regards,<o:p></o:p></span></p>
            </div>
            <div id="signature">
              <div id="divtagdefaultwrapper">
                <p style="background:white"><span
                    style="font-size:12.0pt;color:black">Paul Caicedo<o:p></o:p></span></p>
                <p style="background:white"><span
                    style="font-size:12.0pt;color:black">Mechanical
                    Engineering Consultant<o:p></o:p></span></p>
                <p style="background:white"><u><span
                      style="font-size:12.0pt;color:black">             
                                                                        </span></u><span
                    style="font-size:12.0pt;color:black"><o:p></o:p></span></p>
                <p style="background:white"><b><span
                      style="font-size:12.0pt;color:black">IntegralMECH</span></b><span
                    style="font-size:12.0pt;color:black"><o:p></o:p></span></p>
              </div>
            </div>
          </div>
        </div>
        <div>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;color:black"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><img style="width:7.2291in;height:.0208in"
            id="Horizontal_x0020_Line_x0020_1"
            src="cid:part7.D22CCEFC.ECF572DB@whiteboxtechnologies.com"
            class="" width="694" height="2" border="0"><o:p></o:p></p>
        <div id="divRplyFwdMsg">
          <p class="MsoNormal"><b><span style="color:black">From:</span></b><span
              style="color:black"> David Eldridge <<a
                href="mailto:DEldridge@grummanbutkus.com"
                moz-do-not-send="true">DEldridge@grummanbutkus.com</a>><br>
              <b>Sent:</b> March 22, 2019 9:29 AM<br>
              <b>To:</b> Integral Mechanical Engineering Designs<br>
              <b>Subject:</b> RE: Hourly space temperatura after cooling</span>
            <o:p></o:p></p>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
        </div>
        <div>
          <div>
            <p class="xmsonormal"><span style="color:#1F497D">That SS-O
                report should be after cooling (it’s a “system” report),
                but it may include some hours when the control system is
                in setback – it’s not only for occupied hours, would
                that explain your data?</span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D">There is a
                separate module for report variables that you can
                specify to document any number of internal calculations,
                including one or more space temperatures – it’s been a
                while since I set one of those up but if you search this
                community for “report variables” some instructions
                should pop up.</span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D">These can
                then also be exported to excel, or printed in the *.sim
                report.</span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <p class="xmsonormal"><span style="color:#1F497D">David </span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <div>
              <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><b><span style="color:#1F497D">David
                    S. Eldridge, Jr.</span><span style="color:#244061">,
                    P</span><span style="color:#1F497D">.</span><span
                    style="color:#244061">E</span><span
                    style="color:#1F497D">.</span><span
                    style="color:#244061">, LEED AP BD+C, BEMP, BEAP,
                    HBDP</span></b><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span style="color:#1F497D">Associate</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span
                  style="font-size:4.0pt;color:#1F497D"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span style="color:#365F91">Direct:
                  (847) 316-92</span><span style="color:#1F497D">24</span><span
                  style="color:#365F91"> | Mobile: (</span><span
                  style="color:#1F497D">773</span><span
                  style="color:#365F91">)
                </span><span style="color:#1F497D">490</span><span
                  style="color:#365F91">-</span><span
                  style="color:#1F497D">5038</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span
                  style="font-size:10.0pt;color:#1F497D"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><b><span style="color:#244061">Grumman/Butkus
                    Associates</span></b><span style="color:gray">
                </span><span style="color:#365F91">| 820 Davis Street,
                  Suite 300 | Evanston, IL 60201</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span
                  style="font-size:9.0pt;color:gray">Energy Efficiency
                  Consultants and Sustainable Design Engineers</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p class="xmsonormal"><u><span
                    style="font-size:9.0pt;color:gray"><a
                      href="http://grummanbutkus.com/"
                      moz-do-not-send="true"><span style="color:gray">grummanbutkus.com</span></a></span></u><span
                  style="font-size:9.0pt;color:gray"> |
                  <u><a href="http://grummanbutkus.com/blog"
                      moz-do-not-send="true"><span style="color:gray">Blog</span></a></u>
                  |
                  <u><a
href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526"
                      moz-do-not-send="true"><span style="color:gray">Facebook</span></a></u>
                  |
                  <u><a href="https://twitter.com/grummanbutkus"
                      moz-do-not-send="true"><span style="color:gray">Twitter</span></a></u></span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
            </div>
            <p class="xmsonormal"><span style="color:#1F497D"> </span><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><o:p></o:p></span></p>
            <div>
              <div style="border:none;border-top:solid windowtext
                1.0pt;padding:3.0pt 0in 0in
                0in;border-color:currentColor currentColor;border-image:
                none">
                <p class="xmsonormal"><b>From:</b> Equest-users [<a
                    href="mailto:equest-users-bounces@lists.onebuilding.org"
                    moz-do-not-send="true">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                  <b>On Behalf Of </b>Integral Mechanical Engineering
                  Designs via Equest-users<br>
                  <b>Sent:</b> Friday, March 22, 2019 8:51 AM<br>
                  <b>To:</b> <a
                    href="mailto:equest-users@lists.onebuilding.org"
                    moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                  <b>Subject:</b> [Equest-users] Hourly space
                  temperatura after cooling<span
                    style="font-size:12.0pt;font-family:"Times New
                    Roman",serif"><o:p></o:p></span></p>
              </div>
            </div>
            <p class="xmsonormal"><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"> <o:p></o:p></span></p>
            <div>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA">Hi
                  all,</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA">If
                  I open the BEPS Building Energy Performance, there are
                  155 unmet hours. I would like to get the temperature
                  values throughout the year after cooling, but the only
                  related option that I can see is the SS-O Space
                  Temperature Summary where the temperatures above the
                  set point are much more than the unmet hours. It seems
                  that is the report of the space before cooling.</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA">How
                  could I get the space temperature after cooling to
                  have relation with the unmet hours?</span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
              <p><span style="font-size:12.0pt;color:black" lang="EN-CA"> </span><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><o:p></o:p></span></p>
            </div>
            <div id="x_signature">
              <div id="x_divtagdefaultwrapper">
                <div>
                  <p class="xmsonormal" style="background:white"><span
                      style="font-size:12.0pt;color:black">Kind Regards,</span><span
                      style="font-size:12.0pt;font-family:"Times
                      New Roman",serif"><o:p></o:p></span></p>
                </div>
                <div id="x_signature">
                  <div id="x_divtagdefaultwrapper">
                    <p style="background:white"><span
                        style="font-size:12.0pt;color:black">Paul
                        Caicedo</span><span
                        style="font-size:12.0pt;font-family:"Times
                        New Roman",serif"><o:p></o:p></span></p>
                    <p style="background:white"><span
                        style="font-size:12.0pt;color:black">Mechanical
                        Engineering Consultant</span><span
                        style="font-size:12.0pt;font-family:"Times
                        New Roman",serif"><o:p></o:p></span></p>
                    <p style="background:white"><u><span
                          style="font-size:12.0pt;color:black">         
                                                                       
                                  </span></u><span
                        style="font-size:12.0pt;font-family:"Times
                        New Roman",serif"><o:p></o:p></span></p>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <p style="background:white"><b><span
              style="font-size:12.0pt;color:black">IntegralMECH</span></b><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif"><o:p></o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>